The RP-C-12C model has 12 I/O points and the controller is equipped with 24 fixed screw terminals.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
The 24 screw terminals are used as follows:
Three screw terminals for the power input
Two screw terminals for the return (RET) terminals 4 and 5
Six screw terminals for the four solid-state relay (SSR) outputs
Four screw terminals for the three relay outputs
Three screw terminals for the high power relay output
Six screw terminals for the four universal inputs/outputs of type Ub
Terminal number | Designation | Usage |
Power input | ||
1 | 24 VAC, 50/60 Hz, 23 VA Positive lead (+) when operating the device from 24-30 VDC, 14 W | |
2 | Earth ground lead of 24 VAC transformer connects to terminal 2. Terminals 2 and 3 are internally connected. Negative (–) lead when operating the device from 24-30 VDC, 14 W | |
3 | RET | Terminal 3 is provided for convenience to connect to protective earth ground (optional). Terminals 2 and 3 are internally connected. |
Return terminals | ||
4 | RET | Internally connected to all earth ground and RET terminals |
5 | RET | Internally connected to all earth ground and RET terminals |
Solid-state relay (SSR) outputs | ||
6 | DO1 | SSR output |
7 | COM1 | Common connection for DO1 and DO2 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
8 | DO2 | SSR output |
9 | DO3 | SSR output |
10 | COM2 | Common connection for DO3 and DO4 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
11 | DO4 | SSR output |
Relay outputs | ||
12 | COM3 | Common connection for DO1, DO2, and DO3 |
13 | DO1 | Relay output, type Form A |
14 | DO2 | Relay output, type Form A |
15 | DO3 | Relay output, type Form A |
High power relay outputs | ||
16 | NC | Normally Closed terminal. High power relay output, type Form C. |
17 | DO4 | Common terminal. High power relay output, type Form C. |
18 | NO | Normally Open terminal. High power relay output, type Form C. |
Universal inputs/outputs | ||
19 | Ub1 | Universal input/output, type Ub |
20 | RET | Internally connected to all earth ground and RET terminals |
21 | Ub2 | Universal input/output, type Ub |
22 | Ub3 | Universal input/output, type Ub |
23 | RET | Internally connected to all earth ground and RET terminals |
24 | Ub4 | Universal input/output, type Ub |