Log on to rate and give feedback    1 2 3 4 5 Log on to rate
0
Concept Concept 9/12/2021
Products: RP-C, RP-C-EXT-REL-4
Functionalities: Hardware
Product version: 3.3

RP-C-EXT-REL-4

The RP-C-EXT-REL-4 relay module connects to the RP-C room controllers and enables power supply and control of lights.

The relay module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

RP-C-EXT-REL-4 – Relay module

RP-C-EXT-REL-4 – Relay module

Relay Outputs

The RP-C-EXT-REL-4 relay module has four Relay outputs, which are designed for power supply and control of lights.

For more information, see Relay Outputs on RP-C-EXT-REL-4 .

RP Controller Expansion Module Digital Inputs

The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.

  • The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.

For more information, see RP Controller Expansion Module Digital Inputs .

RP Controller Expansion Module Energy Metering

RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.

For more information, see RP Controller Expansion Module Energy Metering .

RP Controller Expansion Module and Multi-sensor Memory

RP controller expansion modules and multi-sensor have two types of memory, flash memory and RAM.

For more information, see RP Controller Expansion Module and Multi-sensor Memory .

RP Controller Expansion Module and Multi-sensor Communication Ports

The RP controller expansion modules and multi-sensors have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules and multi-sensors on the room bus through a daisy-chain configuration.

For more information, see RP-C Room Bus .

RP Controller Expansion Module and Multi-sensor Address Switch

Each RP controller expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus.

For more information, see RP-C Room Bus .

RP-C Room Bus

The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

For more information, see RP-C Room Bus .

RP Controller Expansion Module Pluggable Connectors

The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.

  • The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.

For more information, see RP Controller Expansion Module Pluggable Connectors .

RP Controller Expansion Module LEDs

There is one or more LEDs on the front panel of the RP controller expansion modules.

For more information, see RP Controller Expansion Module LEDs .

RP Controller Expansion Module Set Button

All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.

For more information, see RP Controller Expansion Module Set Button .

RP Controller Expansion Module Device Installation

The RP controller expansion module can be installed on a DIN rail or flat surface.

For more information, see RP Controller Expansion Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, and RP controller expansion modules, and Operator Display.

For more information, see Wiring .

RP Controller Expansion Module and Multi-sensor Maintenance Modes

The RP controller expansion modules and multi-sensors support different modes that can be used for maintenance purposes.

For more information, see RP Controller Expansion Module and Multi-sensor Maintenance Modes .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Tip:

SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors are supported by the RP controller.

For more information, see BACnet/IP Device Firmware Management .

RP Controller Expansion Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion modules.

For more information, see RP Controller Expansion Modules Regulatory Compliance and Approvals .

Specifications
Electrical
Nominal voltage
100 to 277 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum current consumption
10 A
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
Weight
0.378 kg (0.833 lb)
Installation
DIN rail or flat surface
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Relay outputs: 4 x 3-pin Wieland GST15i3 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Relay status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Energy consumption measurement
The energy consumption is measured in Wh, shared by the four outputs.
Voltage range
230 to 277 VAC +/-10 %
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
20 to 100 W: 5%
  
100 to 3000 W: 1%
Relay outputs
Relay outputs for lights powered by 100 to 277 VAC.
Outputs
4, Relay 1 to Relay 4
Output terminals
N, PE, and L
Power distribution
100 to 277 VAC (same voltage as power supply)
  
Maximum 5 A load per output
  
Maximum 10 A total load for the 4 outputs
  
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Internal Configuration

The RP-C-EXT-REL-4 internal configuration with regards to the signal ground is shown in the following figure.

RP-C-EXT-REL-4 internal configuration

RP-C-EXT-REL-4 internal configuration

Community Content

Product version

Language