SpaceLogic™ CRS-HH-REL-10 relay module connects to the SpaceLogic RP-C Pro room controllers and enables the control of lights and blinds.
It supports high-voltage (120/240 VAC) blind motors. Other types of blind motors are supported by means of external relays. For more information, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
It is part of the EcoStruxure™ Connected Room Solutions for Hotels and can be combined with other modules from this product range.
It is designed for hotel guest room applications.
It is not recommended to be used with the SpaceLogic RP-C Advanced room controllers for hotel applications.
Le module relais présente les caractéristiques suivantes :
Alimentation et communications via le bus "Room Bus"
10 sorties relais pour le contrôle de l’éclairage et des stores
12 entrées digitales pour connecter des interrupteurs pour les luminaires ou autres contacts. Les entrées numériques répondent aux spécifications SELV (ultra-basse tension de sécurité).
Relais hautes performances, avec une capacité de courant d'appel élevée, bien adaptés aux applications d'éclairage LED
LED d'état de fonctionnement
Commutateur rotatif pour configuration d'adresse
Cette solution transforme facilement les hôtels. Son architecture étendue est conçue pour une large gamme de composants modulaires, notamment les interfaces de contrôle de la température, de l'éclairage et des stores, ainsi que les panneaux de chevet, les capteurs, et les thermostats. Profitez des dernières fonctionnalités sans fil avec l'application mobile Commission pour la mise en service et les protocoles ouverts pour communiquer avec les appareils IoT standard du marché.
For information on the maximum number of RP controller expansion modules that can be connected to the RP-C Pro controller room bus, and which restrictions apply to certain types of devices, see the Architectural Guidelines - EcoStruxure Building Management and the Connected Room Solutions for Hotels Supplementary Document Architecture Guidelines, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.
Maximum total length of the room bus is 72 m (236 ft).
Produit |
Référence |
CRS-HH-REL-10 Includes pluggable screw terminal blocks (10 x 2-pole, 2 x 9-pole connectors) for the I/O, delivered in a plastic bag with the device. |
SXWHHREL10001
|
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
|
SXWDINEND10001
|
Electrical | |
DC input supply voltage
|
24 VDC
|
Powered by the RP-C through the room bus (RJ45)
|
|
Maximum power consumption
|
0.3 W
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
![]() |
|
Weight
|
0.476 kg (1.050 lb)
|
Installation
|
DIN rail or flat surface
|
Terminal blocks
|
Relay outputs: 10 x 2-pin screw terminal block
|
Digital inputs: 2 x 9-pin screw terminal block
|
|
Compatibility | |
EcoStruxure BMS server communication
|
|
EcoStruxure Building Operation
|
version 3.3.1 and later
|
Agency compliances | |
Emission
|
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
|
Immunity
|
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
|
Safety standards
|
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
|
Fire performance in air-handling spaces
a
|
UL 2043
|
a) Le module relais CRS-HH-REL-10 est approuvé pour les environnements de plénum. | |
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
Sorties relais | |
Outputs
|
10, DO1 to DO10
|
Relay output rating
|
24 to 277 VAC, 50/60 Hz, 30 VDC:
|
Resistive and incandescent: 10 A
|
|
Standard magnetic ballast: 5 A
|
|
LED driver: 5 A
|
|
1/2 HP, 240 VAC, 50/60 Hz
|
|
1/4 HP, 120 VAC, 50/60 Hz
|
|
Courant de charge maximum
|
Maximum 50 A total load for the 10 outputs
|
Courant d'appel maximum
|
Maximum 165 A inrush current (<20 ms) per output
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
12, DI1 to DI12
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
Follow proper installation wiring diagrams and instructions. For more information on wiring, see the installation instructions in the SpaceLogic CRS-HH-REL-10 Expansion Module Installation Sheet, the SpaceLogic and EasyLogic - Hardware Installation System Guide, and the RP-C room bus restrictions specified for the Connected Room Solutions for Hotels in the Architecture Guidelines - Hotel Application, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.