SpaceLogic™ CRS-HH-REL-10 relay module connects to the SpaceLogic RP-C Pro room controllers and enables the control of lights and blinds.
It supports high-voltage (120/240 VAC) blind motors. Other types of blind motors are supported by means of external relays. For more information, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
It is part of the EcoStruxure™ Connected Room Solutions for Hotels and can be combined with other modules from this product range.
It is designed for hotel guest room applications.
It is not recommended to be used with the SpaceLogic RP-C Advanced room controllers for hotel applications.
继电器模块具有下述特点:
通过房间总线供电和通信
10 个继电器输出,用于控制酒店客房的灯光和百叶窗
12 个数字输入提供了更大的灵活性,用于有墙装开关面板干接点输入或传感器的不同应用。数字输入为 SELV(安全的弱电信号)
高性能继电器,具有高浪涌电流能力,非常适合 LED 照明应用
显示设备的状态 LED
用于地址配置的旋转开关
该解决方案可轻松给酒店带来改变。其广泛的体系结构设计用于广泛的模块化组件,包括温度、光和百叶窗控制界面,以及床头面板、传感器、恒温器,以及广泛的 HMI(如机械开关和 Modbus 玻璃触摸面板)。通过用于调试的 Commission 移动应用程序和与行业标准物联网设备接口的开放协议,获取最新的无线功能。
For information on the maximum number of RP controller expansion modules that can be connected to the RP-C Pro controller room bus, and which restrictions apply to certain types of devices, see the Architectural Guidelines - EcoStruxure Building Management and the Connected Room Solutions for Hotels Supplementary Document Architecture Guidelines, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.
Maximum total length of the room bus is 72 m (236 ft).
产品 |
物料号 |
CRS-HH-REL-10 Includes pluggable screw terminal blocks (10 x 2-pole, 2 x 9-pole connectors) for the I/O, delivered in a plastic bag with the device. |
SXWHHREL10001
|
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
|
SXWDINEND10001
|
Electrical | |
DC input supply voltage
|
24 VDC
|
Powered by the RP-C through the room bus (RJ45)
|
|
Maximum power consumption
|
0.3 W
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
![]() |
|
Weight
|
0.476 kg (1.050 lb)
|
Installation
|
DIN rail or flat surface
|
Terminal blocks
|
Relay outputs: 10 x 2-pin screw terminal block
|
Digital inputs: 2 x 9-pin screw terminal block
|
|
Compatibility | |
EcoStruxure BMS server communication
|
|
EcoStruxure Building Operation
|
version 3.3.1 and later
|
Agency compliances | |
Emission
|
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
|
Immunity
|
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
|
Safety standards
|
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
|
Fire performance in air-handling spaces
a
|
UL 2043
|
a) CRS-HH-REL-10 继电器模块批准用于增压应用。 | |
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
继电器输出 | |
Outputs
|
10, DO1 to DO10
|
Relay output rating
|
24 to 277 VAC, 50/60 Hz, 30 VDC:
|
Resistive and incandescent: 10 A
|
|
Standard magnetic ballast: 5 A
|
|
LED driver: 5 A
|
|
1/2 HP, 240 VAC, 50/60 Hz
|
|
1/4 HP, 120 VAC, 50/60 Hz
|
|
最大负载电流
|
Maximum 50 A total load for the 10 outputs
|
最大涌入电流
|
Maximum 165 A inrush current (<20 ms) per output
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
12, DI1 to DI12
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
Follow proper installation wiring diagrams and instructions. For more information on wiring, see the installation instructions in the SpaceLogic CRS-HH-REL-10 Expansion Module Installation Sheet, the SpaceLogic and EasyLogic - Hardware Installation System Guide, and the RP-C room bus restrictions specified for the Connected Room Solutions for Hotels in the Architecture Guidelines - Hotel Application, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.