earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: MP-C
Functionalities: Hardware
Product version: 2023, 2024, 7.0
7/8/2025

SpaceLogic™ MP-C-BAA

Part numbers: SXWMPC15A10A01, SXWMPC18A10A01, SXWMPC18B10A01, SXWMPC24A10A01, and SXWMPC36A10A01

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installation Orientation Restrictions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail

Notice

CONTROLLER DAMAGE

Use the DIN rail end clip when you install the controller on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Wall

 
action_zoom_plus_stroke

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • Disconnect all line voltage connected to the controller and its relay outputs before working on the device.

  • More than one disconnect switch may be required to de-energize this equipment before servicing.

  • Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs/outputs.

Failure to follow these instructions will result in death or serious injury.

Notice

CONTROLLER DAMAGE

Before powering up MP-C, ensure that the input power polarity is correct, the voltage level meets the specifications of the controller, and the terminal blocks are plugged into the correct connector headers on the controller.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

MP-C-15A-BAA
SXWMPC15A10A01
MP-C-18A-BAA
SXWMPC18A10A01
MP-C-18B-BAA
SXWMPC18B10A01
MP-C-24A-BAA
SXWMPC24A10A01
MP-C-36A-BAA
SXWMPC36A10A01
MP-C-BAA DISPLAY
(MP-C override display module)
SXWMPCDSP10A01

Spare terminal blocks for all MP-C models

SXWMPCCON10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Specifications

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Power consumption
MP-C-15A, -18A, -18B: 22 VA
  
MP-C-24A: 28 VA
  
MP-C-36A: 33 VA
DC input
Nominal voltage
24 to 30 VDC
 
action_zoom_plus_stroke
Power consumption
MP-C-15A, -18A, -18B: 12 W
  
MP-C-24A: 15 W
  
MP-C-36A: 18 W
Port types
USB device port
Mini-B
USB host port
Type-A
Ethernet port 1 and 2
10/100BASE-TX (RJ45), IEEE 802.3 compliant
RS-485 port Com A
24 VDC, 2 W, RS-485 (RJ45)
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
  
See section Installation Orientation Restrictions.
  
MP-C Display temperature range: -30 to +60 °C (-22 to +140 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
Ub – Universal I/O
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Channels
MP-C-15A: 8; -18A: 10; -18B: 10;
  
-24A: 16; -36A: 20
Uc – Universal I/O
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Current output rating
0 to 20 mA, 650 ohm (max.)
Channels
MP-C-15A: 0; -18A: 0; -18B: 0;
  
-24A: 4; -36A: 8
DO – Relay outputs
Relay contact rating
250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 2 A
  
Pilot Duty (C300)
Channels
MP-C-15A: 0; -18A: 3; -18B: 0;
  
-24A: 4; -36A: 8
DO – High power relay outputs
Relay contact rating
250 VAC
 
action_zoom_plus_stroke
/ 24 VDC
 
action_zoom_plus_stroke
, 12 A
  
Pilot Duty (B300)
Channels
MP-C-15A: 1; -18A: 1; -18B: 0;
  
-24A: 0; -36A: 0
DO – Triac outputs
Triac rating
Max. 30 VAC
 
action_zoom_plus_stroke
, 0.5 A
Channels
MP-C-15A: 6; -18A: 4; -18B: 8;
  
-24A: 0; -36A: 0

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke
  • MP-C Device Installation
  • I/O Wiring
  • Communication Port Wiring
  • MP-C Controllers
  • Hardware Overview