Part number: SXWTBPSW110A01
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
Device |
Part number |
TB-PS-W1-BAA Terminal Base
|
SXWTBPSW110A01
|
PS-24V-BAA Power Supply
|
SXWPS24VX10A01
|
Device |
Part number |
S-Cable, 1.5 m, angle |
SXWSCABLE10002 |
S-Cable, 0.75 m, angle |
SXWSCABLE10003 |
AC input | |
Nominal voltage
|
24 VAC
![]() |
Recommended transformer rating
|
≥60 VA
|
DC input | |
Nominal voltage
|
24 VDC
![]() |
Power consumption
|
max. 40 W
|
DC output | |
Output voltage
|
24 V ±1 V
|
Output power
|
max. 30 W
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94-5VB
|
Electrical | |
I/O bus power
|
24 VDC
![]() |
Maximum addresses per I/O bus
|
32
|