earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
硬件安装

硬件安装


产品: PS-24V
功能: 硬件
产品版本: 1.8, 1.9, 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024
2024/9/13

SpaceLogic™ TB-PS-W1-BAA

arrow1_rotationSafety Information arrow1_rotationTechnical Literature arrow1_rotationDimensions arrow1_rotationOverview arrow1_rotationInstalling the Terminal Base arrow1_rotationConnecting the Next Terminal Base arrow1_rotationI/O Bus Addressing, Power Limits, and Cables arrow1_rotationConnections arrow1_rotationWiring arrow1_rotationTerminal Base and Electronics Module arrow1_rotationS-Cables arrow1_rotation规格 arrow1_rotationAddendum - California Proposition 65 Warning Statement for California Residents

Part number: SXWTBPSW110A01

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Overview

 
action_zoom_plus_stroke

Installing the Terminal Base

通知

REDUCED LIFE SPAN OF ELECTRONICS MODULE

Always install the terminal base on a horizontal DIN rail to provide sufficient cooling air flow through the electronics module.

Failure to follow these instructions can result in reduced life span of the electronics module.

 
action_zoom_plus_stroke

Connecting the Next Terminal Base

警告 警告

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Ensure that the module type and the terminal base type match.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

 
action_zoom_plus_stroke

I/O Bus Addressing, Power Limits, and Cables

 
action_zoom_plus_stroke

Connections

 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

Terminal Base and Electronics Module

Device

Part number

TB-PS-W1-BAA Terminal Base
SXWTBPSW110A01
PS-24V-BAA Power Supply
SXWPS24VX10A01

S-Cables

Device

Part number

S-Cable, 1.5 m, angle

SXWSCABLE10002

S-Cable, 0.75 m, angle

SXWSCABLE10003

规格

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Recommended transformer rating
≥60 VA
DC input
Nominal voltage
24 VDC
 
action_zoom_plus_stroke
Power consumption
max. 40 W
DC output
Output voltage
24 V ±1 V
Output power
max. 30 W
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
Electrical
I/O bus power
24 VDC
 
action_zoom_plus_stroke
max. 30 W per I/O bus power supply, Class 2
Maximum addresses per I/O bus
32

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke