earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: PS-24V
Functionalities: Hardware
Product version: 1.8, 1.9, 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024
12/14/2023

SpaceLogic™ PS-24V-BAA

Part number: SXWPS24VX10A01

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installing the Module

Warning Warning

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Install only the module type that is indicated on the label on the terminal base backplane.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

 
action_zoom_plus_stroke

Labeling the Module

 
action_zoom_plus_stroke

Electronics Module and Terminal Base

Device

Part number

PS-24V-BAA Power Supply
SXWPS24VX10A01
TB-PS-W1-BAA Terminal Base
SXWTBPSW110A01

Specifications

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Recommended transformer rating
≥60 VA
DC input
Nominal voltage
24 VDC
 
action_zoom_plus_stroke
Power consumption
max. 40 W
DC output
Output voltage
24 V ±1 V
Output power
max. 30 W
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
Electrical
I/O bus power
24 VDC
 
action_zoom_plus_stroke
max. 30 W per I/O bus power supply, Class 2
Maximum addresses per I/O bus
32

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke