Part numbers: SXWRCF12AM10001, SXWRCF12BM10001, and SXWRCF16AM10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Configure a unique MS/TP address for the device during installation. Use position 1 to 7 on the Address DIP switch. Position 1 to 7 represent the binary values 1, 2, 4, 8, 16, 32, and 64. For example, to configure MS/TP address 6, set DIP switches 2 and 3 to ON and switches 1, 4, 5, 6, and 7 to OFF. For more information, see the SpaceLogic and EasyLogic - Hardware Reference Guide.
Recommended screw tightening torque for removable screw terminal block: 0.56 to 0.79 Nm (5 to 7 lbf.in)
Recommended screw tightening torque for fixed screw terminal blocks: 0.56 to 0.79 Nm (5 to 7 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Reference Guide.
Product |
Part number |
RP-C-12A-M-24V
|
SXWRCF12AM10001
|
RP-C-12B-M-24V
|
SXWRCF12BM10001
|
RP-C-16A-M-24V
|
SXWRCF16AM10001
|
Optional covers
|
SXWRPCCOV10001
|
DIN-rail end clip, 25 pieces |
SXWDINEND10001 |
AC input | |
Nominal voltage
|
24 VAC
|
Power consumption
|
14 VA
|
DC input | |
Nominal voltage
|
24 to 30 VDC
|
Power consumption
|
8 W
|
Port types | |
RS-485 port Com A
|
24 VDC, 3 W, RS-485 (RJ45)
|
RS-485 port
|
RS-485 (3-pole screw terminal block)
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F) at normal operation
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94-5VB
|
Ub – Universal I/O | |
Input rating
|
24 VDC
|
Voltage output rating
|
0 to 10 VDC
|
Channels
|
RP-C-12A-M: 8; -12B-M: 8; -16A-M: 8
|
DO – Relay outputs | |
Relay contact rating
|
Pilot Duty (C300)
|
Min. current: 100 mA (5 VDC)
|
|
Resistive: 250 VAC
|
|
4 A (cos phi = 1)
|
|
Inductive: 250 VAC
|
|
4 A (cos phi = 0.4)
|
|
Channels
|
RP-C-12A-M: 0; -12B-M: 3; -16A-M: 3
|
DO – High power relay outputs | |
Relay contact rating
|
Pilot Duty (B300)
|
Normally Open, resistive: 250 VAC
|
|
/ 24 VDC
|
|
Normally Closed, inductive: 250 VAC
|
|
/ 24 VDC
|
|
Channels
|
RP-C-12A-M: 0; -12B-M: 1; -16A-M: 1
|
DO – Solid-state relay outputs | |
Output rating
|
30 VAC
|
Max. 4 A total load
|
|
Channels
|
RP-C-12A-M: 4; -12B-M: 0; -16A-M: 4
|