earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
硬件安装

硬件安装


产品: RP-C
功能: 硬件
产品版本: 2023, 2024, 7.0
2025/1/17

EasyLogic™ RP-C

Part numbers: SXWRCF12AM10001, SXWRCF12BM10001, and SXWRCF16AM10001

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installation Orientations

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail

通知

CONTROLLER DAMAGE

Use the DIN rail end clip when you install the controller on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Flat Surface

 
action_zoom_plus_stroke

Installing and Removing the Optional Covers

 
action_zoom_plus_stroke

Connections and DIP Switch

危险 危险

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • On RP-C-12B-M-24V and RP-C-16A-M-24V, disconnect all line voltage connected to the relay outputs before working on the device.

    More than one disconnect switch may be required to de-energize this equipment before servicing.

  • Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs/outputs.

Failure to follow these instructions will result in death or serious injury.

通知

CONTROLLER DAMAGE

Before powering up RP-C, ensure that the input power polarity is correct and that the voltage level meets the specifications of the controller.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke
 
action_zoom_plus_stroke

Configuring a Unique MS/TP Address

Configure a unique MS/TP address for the device during installation. Use position 1 to 7 on the Address DIP switch. Position 1 to 7 represent the binary values 1, 2, 4, 8, 16, 32, and 64. For example, to configure MS/TP address 6, set DIP switches 2 and 3 to ON and switches 1, 4, 5, 6, and 7 to OFF. For more information, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

Wiring

Recommended screw tightening torque for removable screw terminal block: 0.56 to 0.79 Nm (5 to 7 lbf.in)

Recommended screw tightening torque for fixed screw terminal blocks: 0.56 to 0.79 Nm (5 to 7 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

Part Numbers

Product

Part number

RP-C-12A-M-24V
SXWRCF12AM10001
RP-C-12B-M-24V
SXWRCF12BM10001
RP-C-16A-M-24V
SXWRCF16AM10001
Optional covers
SXWRPCCOV10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

规格

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Power consumption
14 VA
DC input
Nominal voltage
24 to 30 VDC
 
action_zoom_plus_stroke
Power consumption
8 W
Port types
RS-485 port Com A
24 VDC, 3 W, RS-485 (RJ45)
RS-485 port
RS-485 (3-pole screw terminal block)
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
Ub – Universal I/O
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 2.4 kohm (min.)
Channels
RP-C-12A-M: 8; -12B-M: 8; -16A-M: 8
DO – Relay outputs
Relay contact rating
Pilot Duty (C300)
  
Min. current: 100 mA (5 VDC)
  
Resistive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 1)
  
Inductive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 0.4)
Channels
RP-C-12A-M: 0; -12B-M: 3; -16A-M: 3
DO – High power relay outputs
Relay contact rating
Pilot Duty (B300)
  
Normally Open, resistive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 12 A (cos phi = 1)
  
Normally Closed, inductive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 3 A (cos phi = 0.4)
Channels
RP-C-12A-M: 0; -12B-M: 1; -16A-M: 1
DO – Solid-state relay outputs
Output rating
30 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 2 A
  
Max. 4 A total load
Channels
RP-C-12A-M: 4; -12B-M: 0; -16A-M: 4

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke