Part number: SXWRCF16C10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
The controller is intended for fan coil, ceiling systems, and other applications. The controller is typically installed next to or inside the fan coil equipment.
For information on wiring, including connection diagrams, rating of and location of fuses (circuit breakers), and cable specifications, see the SpaceLogic and EasyLogic - Hardware Reference Guide.
Product |
Part number |
RP-C-16C-F-230V
|
SXWRCF16C10001
|
DIN-rail end clip, 25 pieces |
SXWDINEND10001 |
Mounting plate - RP-C Pro Plus, 5 pieces |
SXWRCMPK510001
|
RS-485 power adapter
|
SXWNISORS485P10001
|
Use |
Part number |
Reference |
Connector type |
Suitable for cable diameters mm (inches) |
Tightening torque, screws Nm (lbf.in) |
Marking |
Color of coding /housing |
Minimum order quantity |
Power supply input |
SXWRPCCONWWPOW |
91.931.4053.1 |
Female, 3-pole |
5.6–11 (0.22–0.43) |
0.3–0.5 (2.7–4.4) |
L, PE, N |
Black /Black |
100 |
External input, 24 VAC / VDC |
SXWRPCCONPOWIP |
91.921.3053.0 |
Female, 2-pole |
6–7.7 (0.24–0.30) |
0.3–0.5 (2.7–4.4) |
L, N |
White /White |
100 |
SSR outputs (DO), 24 VAC / VDC |
SXWRPCCONDCOP |
91.922.3053.0 |
Male, 2-pole |
6–7.7 (0.24–0.30) |
0.3–0.5 (2.7–4.4) |
L, N |
White /White |
100 |
Universal I/O (Ub) |
SXWRPCCONWWLIGHT2 |
91.922.3353.0 |
Male, 2-pole |
6–7.7 (0.24–0.30) |
0.3–0.5 (2.7–4.4) |
2, 1 |
Light blue /White |
100 |
Configurable SSR outputs (DO) or Universal I/O (Ub) |
SXWRPCCONUIO |
91.942.4650.0 |
Male, 4-pole |
6.5–12 (0.26–0.47) |
0.3–0.5 (2.7–4.4) |
1, 2, 3, 4/N |
Turquoise blue /White |
100 |
The external connectors need to be ordered separately. The connectors can be ordered in quantities of 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.
AC input | |
Nominal voltage
|
230 VAC
|
Maximum power consumption
|
65 VA
|
Power consumption without load
|
5 VA
|
Overvoltage category
|
III
|
Pollution degree
|
2
|
24 VAC/VDC input (EXT Input) for external power supply to SSR outputs | |
Nominal voltage
|
24 VAC
|
Maximum current consumption
|
8 A
|
Port types | |
USB host port
|
Type-A, 5 VDC, 0.5 A
|
Ethernet port 1 and 2
|
10/100BASE-TX (RJ45), IEEE 802.3 compliant
|
RS-485 port Com A, B, and C
|
24 VDC, 3 W, RS-485 (RJ45)
|
Wireless connectivity | |
Bluetooth
®
Low Energy (Bluetooth
®
5)
|
2.402 to 2.480 GHz, max. 10 dBm output power, 100 m (328 ft) line-of-sight range
|
Antenna
|
Integrated antenna
|
Approved external antenna (optional)
|
Manufacturer: Linx Technologies, Model: ANT-2.4-WRT-MON-SMA, Gain: 0.8 dBi, Type: Monopole, Impedance: 50 ohm, Connector: SMA
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94 V-0
|
IP networking | |
IP address assignment methods
|
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
|
Ub – Universal I/O | |
Input rating
|
24 VDC
|
Voltage output rating
|
0 to 10 VDC
|
Channels
|
4, Ub9 to Ub12
|
Channels, configurable DO or Ub
|
8, Ub1 to Ub8
|
DO – SSR outputs | |
Output rating
|
24 VAC
|
Max. 2 A load per DO group A, B, C and D
|
|
Max. 8 A total load for 12 SSR outputs
|
|
Channels
|
4, DO9 to DO12
|
Channels, configurable DO or Ub
|
8, DO1 to DO8
|