Part numbers: SXWASP3XX10001 and SXWASPL3X10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
Product |
Part number |
SpaceLogic AS-P-3
|
SXWASP3XX10001
|
SpaceLogic AS-P-L-3
|
SXWASPL3X10001
|
AS-P-L-3 differs from AS-P-3 in that it supports LonWorks. Instead of a third RS-485 port, AS-P-L-3 has a LON port.
Product |
Part number |
S-Cable, 1.5 m, angle |
SXWSCABLE10002 |
S-Cable, 0.75 m, angle |
SXWSCABLE10003 |
The AS-P-3 server is delivered without software. Install the software on the AS-P-3 server using Device Administrator.
This product contains code that is covered by the GNU General Public License (GPL). The relevant code is available on the Schneider Electric extranet, ecoxpert.se.com
The PVC is a three-digit code printed on the device's product label. The PVC along with the serial number helps to verify the owner of the device.
AC input | |
Type
|
Isolated Class 2 input
|
Nominal voltage
|
24 VAC
![]() |
Recommended transformer rating
|
60 VA or higher
|
DC input | |
Nominal voltage
|
24 to 30 VDC
![]() |
Power consumption
|
40 W
|
DC output | |
Output voltage
|
24 VDC ± 1 V
|
Maximum output power
|
20 W
|
Port types | |
USB device port
|
USB 3.0, type-C
|
USB host port 1 and 2
|
USB 3.0 or USB 2.0, type-A
|
USB 3.0: 5 VDC, 0.9 A from port 1 or 2
|
|
USB 2.0: 5 VDC, 0.5 A from port 1 and 2
|
|
Ethernet port 1
|
10/100/1000BASE-TX (RJ45), IEEE 802.3 compliant
|
Ethernet port 2 and 3
|
10/100BASE-TX (RJ45), IEEE 802.3 compliant
|
RS-485 port Com A, Com B, and Com C
|
2-wire ports, bias 5.0 VDC
|
Com C is only available on AS-P-3
|
|
LON port
|
TP/FT-10, 2-wire port
|
LON is only available on AS-P-L-3
|
|
Operation environment | |
Ambient temperature, operating
|
0 to 55 °C (32 to 131 °F) on AS-P-3
|
0 to 50 °C (32 to 122 °F) on AS-P-L-3
|
|
Indoor use only
|
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94 V-0
|
IP networking | |
IP address assignment methods
|
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
|