SpaceLogicâ„¢ CRS-HH-REL-10

arrow1_rotation Safety Information arrow1_rotation Technical Literature arrow1_rotation Dimensions arrow1_rotation Installation Orientation Restrictions arrow1_rotation Installing the Device on a DIN Rail arrow1_rotation Installing the Device on a Flat Surface arrow1_rotation Connections arrow1_rotation Wiring arrow1_rotation Part Numbers arrow1_rotation Specifications arrow1_rotation Addendum - California Proposition 65 Warning Statement for California Residents

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installation Orientation Restrictions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail

Notice

EXPANSION MODULE DAMAGE

Use the DIN rail end clip when you install the RP controller expansion module on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Flat Surface

 
action_zoom_plus_stroke

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • Turn off all power connected to this equipment before working on the equipment.

  • More than one disconnect switch may be required to de-energize this equipment before servicing.

Failure to follow these instructions will result in death or serious injury.

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Do not connect high and low voltage next to each other for relay outputs.

Failure to follow these instructions will result in death or serious injury.

To prevent from connecting high and low voltage next to each other, it is recommended not to mix high and low voltage connections on the same side of the device. Connect the high voltage equipment on the upper (DO1-DO6) or lower (DO7-DO10) side and connect low voltage equipment on the opposite side.

 
action_zoom_plus_stroke
Notice

BLINDS/AWNINGS DAMAGE

Before connecting the AC mains voltage to the blinds/awnings connected to the relay outputs, ensure that the CRS-HH-REL-10 relay module is powered up by the RP-C room bus (24 VDC).

Failure to follow these instructions can result in equipment damage.

Notice

CONNECTOR OR CABLE ASSEMBLY DAMAGE

Anchor the excess cabling to alleviate all stresses on connectors and cable assemblies.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torques:

  • 2-pole connector: 0.5 Nm (4.4 lbf.in)

  • 9-pole connector: 0.2 Nm (1.7 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

CRS-HH-REL-10

Includes pluggable screw terminal blocks (10 x 2-pole, 2 x 9-pole connectors) for the I/O, delivered in a plastic bag with the device.

SXWHHREL10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Specifications

DC input
DC input supply voltage
24 VDC
  
Powered by the RP-C through the room bus (RJ45)
Maximum power consumption
0.3 W
Port types
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043 (Approved for plenum installations)
Relay outputs
Outputs
10, DO1 to DO10
Relay output rating
24 to 277 VAC
 
action_zoom_plus_stroke
, 50/60 Hz / 30 VDC
 
action_zoom_plus_stroke
,
  
Resistive and incandescent: 10 A
  
Standard magnetic ballast: 5 A
  
LED driver: 5 A
  
1/2 HP, 240 VAC, 50/60 Hz
  
1/4 HP, 120 VAC, 50/60 Hz
Maximum load current
Maximum 50 A total load for the 10 outputs
Maximum inrush current
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
Digital inputs
Inputs
12, DI1 to DI12
Input rating
5 VDC
 
action_zoom_plus_stroke
, 2.2 mA, SELV

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov
 
action_zoom_plus_stroke
  • RP Series Expansion Module Device Installation
  • I/O Module Wiring
  • SmartStruxure Server Device Wiring
  • CRS-HH-REL-10
  • Hardware Overview