earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: AS-P-3
Functionalities: Hardware
Product version: 7.0, 7.1
10/23/2026

SpaceLogicâ„¢ AS-P-3 and AS-P-L-3

arrow1_rotation Safety Information arrow1_rotation Technical Literature arrow1_rotation Dimensions arrow1_rotation Installing the Device on a DIN Rail in a Cabinet arrow1_rotation Connecting the Next Device on the I/O Bus arrow1_rotation I/O Bus Addressing, Power Limits, and Cables arrow1_rotation Connections arrow1_rotation Wiring arrow1_rotation Part Numbers arrow1_rotation Spare Parts arrow1_rotation Accessories arrow1_rotation AS-P-3 Software arrow1_rotation Software License Notice arrow1_rotation Product Verification Code (PVC) arrow1_rotation Specifications arrow1_rotation Addendum - California Proposition 65 Warning Statement for California Residents

Part numbers: SXWASP3XX10001 and SXWASPL3X10001

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail in a Cabinet

Notice

REDUCED DEVICE LIFE SPAN

Install the device on a horizontal DIN rail to provide sufficient cooling air flow through the device.

Failure to follow these instructions can result in reduced life span of the device.

 
action_zoom_plus_stroke

Connecting the Next Device on the I/O Bus

 
action_zoom_plus_stroke

I/O Bus Addressing, Power Limits, and Cables

 
action_zoom_plus_stroke

Connections

Notice

EQUIPMENT DAMAGE

  • Do not connect 230 VAC or 110 VAC to any terminal.

  • Install only a wired terminal block that matches the markings of the terminals on the device.

  • Use only terminal blocks delivered with the device or ordered from Schneider Electric using the part number SXWASPCON10002.

Failure to follow these instructions can result in equipment damage.

Notice

DECREASED RS-485 NETWORK PERFORMANCE

Consider the RS-485 bus termination and biasing. For more information, see the Hardware Installation System Guide.

Failure to follow these instructions can result in decreased performance and reliability of the RS-485 network.

 
action_zoom_plus_stroke
 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

SpaceLogic AS-P-3
SXWASP3XX10001
SpaceLogic AS-P-L-3
SXWASPL3X10001
  • AS-P-L-3 differs from AS-P-3 in that it supports LonWorks. Instead of a third RS-485 port, AS-P-L-3 has a LON port.

Spare Parts

Product

Part number

AS-P-3-CON (Connector kit)
SXWASPCON10002

Accessories

Product

Part number

S-Cable, 1.5 m, angle

SXWSCABLE10002

S-Cable, 0.75 m, angle

SXWSCABLE10003

AS-P-3 Software

The AS-P-3 server is delivered without software. Install the software on the AS-P-3 server using Device Administrator.

Software License Notice

This product contains code that is covered by the GNU General Public License (GPL). The relevant code is available on the Schneider Electric extranet

Product Verification Code (PVC)

The PVC is a three-digit code printed on the device's product label. The PVC along with the serial number helps to verify the owner of the device.

Specifications

AC input
Type
Isolated Class 2 input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Recommended transformer rating
60 VA or higher
DC input
Nominal voltage
24 to 30 VDC
 
action_zoom_plus_stroke
Power consumption
40 W
DC output
Output voltage
24 VDC ± 1 V
Maximum output power
20 W
Port types
USB device port
USB 3.0, type-C
USB host port 1 and 2
USB 3.0 or USB 2.0, type-A
  
USB 3.0: 5 VDC, 0.9 A from port 1 or 2
  
USB 2.0: 5 VDC, 0.5 A from port 1 and 2
Ethernet port 1
10/100/1000BASE-TX (RJ45), IEEE 802.3 compliant
Ethernet port 2 and 3
10/100BASE-TX (RJ45), IEEE 802.3 compliant
RS-485 port Com A, Com B, and Com C
2-wire ports, bias 5.0 VDC
  
Com C is only available on AS-P-3
LON port
TP/FT-10, 2-wire port
  
LON is only available on AS-P-L-3
Operation environment
Ambient temperature, operating
0 to 55 °C (32 to 131 °F) on AS-P-3
  
0 to 50 °C (32 to 122 °F) on AS-P-L-3
  
Indoor use only
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov
 
action_zoom_plus_stroke
  • Hardware Overview