Concept

Concept


Products: AD v3, AO-8, AO-V-8, AS-B, CRS-HH-REL-10, DI-16, DO-FA-12, DO-FC-8, IP-IO , MP-C, MP-V, AS-P, Operator Display, PS-24V, RP-C, RP-C-EXT-0-10V-4, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-2-LV-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-BL-SMI-2-LV-PD, RP-C-EXT-BL-SMI-4-HV-PD, RP-C-EXT-DALI, RP-C-EXT-DALI-M-PD, RP-C-EXT-KNX, RP-C-EXT-MS-BLE, RP-C-EXT-REL-4, RP-C-RC-BLE, RP-IO , RP-V, RTD-DI-16, SpaceLogic Sensors, UI-16, UI-8/AO-4, UI-8/AO-4 v2, UI-8/AO-V-4, UI-8/AO-V-4 v2, UI-8/DO-FC-4, UI-8/DO-FC-4 v2, Wireless Adapter - Advanced
Functionalities: Hardware
Product version: 2023, 2024
6/24/2026

Hardware Overview

arrow1_rotationTerminal Bases arrow1_rotationPS-24V Power Supplies arrow1_rotation AS-P Servers arrow1_rotationCentral IO Modules arrow1_rotationCentral IO Modules v2 arrow1_rotation AS-B Servers arrow1_rotationMP-C Controllers arrow1_rotationMP-V Controllers arrow1_rotationIP-IO Modules arrow1_rotationRP-C Controllers arrow1_rotationRP-V Controllers arrow1_rotationRP-IO Modules arrow1_rotationRP Controller Expansion Modules arrow1_rotationRP Controller Expansion Zigbee Modules arrow1_rotationRemote Control arrow1_rotationKNX Modbus Gateway arrow1_rotationSpaceLogic Sensor Devices arrow1_rotationSpaceLogic Bluetooth Adapter arrow1_rotationWireless Adapter - Advanced arrow1_rotationAD v3 arrow1_rotationOperator Display arrow1_rotationWiring

The Schneider Electric EasyLogic and SpaceLogic hardware devices for the EcoStruxure BMS include terminal bases, PS-24V power supplies, Central IO modules, automation servers such as AS-P and AS-B servers, MP-C, MP-V, RP-C, and RP-V controllers, IP-IO and RP-IO I/O modules, RP controller expansion modules, remote control, KNX Modbus gateway, Bluetooth adapter, Wireless Adapter - Advanced, SpaceLogic Sensor devices, Advanced Display devices, and Operator Display devices.

Terminal Bases

The terminal bases are used for SpaceLogic devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SpaceLogic device installed to the right (next terminal base in the chain).

For more information, see Terminal Bases .

PS-24V Power Supplies

PS-24V is the power supply for the AS-P servers and Central IO modules. The PS-24V power supply requires an input voltage of either 24 VAC +/–20 % or 24–30 VDC.

For more information, see PS-24V Power Supplies .

AS-P Servers

The AS-P server offers enhanced processor performance, increased memory size, dual Ethernet ports, and high-speed USB interfaces. The AS-P server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The AS-P controls and supervises equipment, typically HVAC equipment. AS-P servers use Central IO module with connected field devices, such as sensors and actuators, to do that.

For more information, see AS-P Servers .

Central IO Modules

By adding a variety of Central IO and power supply modules, you can use the AS-P server to tailor the Intelligent Building Management System to your unique requirements.

For more information, see Central IO Modules .

Central IO Modules v2

The second-generation (v2) Central IO modules feature several enhancements over the first-generation models, including faster processor performance and higher-resolution A/D converters for universal inputs. Additionally, the v2 module design has been updated to better align with the DIN 43880 standard by removing the previously high shoulder height. By adding a variety of Central IO and power supply modules, you can use the AS-P server to tailor the Intelligent Building Management System to your unique requirements.

For more information, see Central IO Modules v2 .

AS-B Servers

An AS-B server is a powerful automation server that features both onboard I/O and built-in power supply. Like the other automation servers, the AS-B server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The automation server controls and supervises equipment, typically HVAC equipment. The AS-B server uses its onboard I/O with connected field devices, such as sensors and actuators, to do that.

For more information, see AS-B Servers .

MP-C Controllers

The MP-C controller is a multi-purpose, fully programmable, IP based field controller. The MP-C models offer a flexible mix of I/O point types that suits a wide range of HVAC applications. The MP-C can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server.

For more information, see MP-C Controllers .

MP-V Controllers

The MP-V controller is a multi-purpose, fully programmable, IP based field controller dedicated for VAV applications. MP-V integrates a controller, a damper actuator, and an air flow sensor in a single unit for ease of installation. The MP-V can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server. MP-V can also be reconfigured through the EcoStruxure Building Operation software to use BACnet MS/TP, instead of BACnet/IP.

For more information, see MP-V Controllers .

IP-IO Modules

The IP-IO module provides I/O expansion to your HVAC application over BACnet/IP and can share their I/O resources across applications running in automation servers, BACnet/IP controllers, or third-party systems. The IP-IO module can be installed near facilities in the field, away from the automation server or the BACnet/IP controller.

For more information, see IP-IO Modules .

RP-C Controllers

The RP-C controller is a room-purpose, fully programmable, IP based field controller. The RP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. The RP-C can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server. The BACnet/IP enabled RP-C controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP. The RP-C features a wireless chip that allows a mobile device running the Commission mobile application to connect directly to the controller.

For more information, see RP-C Controllers .

RP-V Controllers

The RP-V controller is a room-purpose, fully programmable, IP based field controller dedicated for VAV cooling and Heating applications. RP-V integrates a controller, a damper actuator, and an air flow sensor in a single compact unit for ease of installation. The controller can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or an Enterprise Server as the parent server. The BACnet/IP enabled RP-V controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP. The RP-V features a wireless chip that allows a mobile device running the Commission mobile application to connect directly to the controller. 

For more information, see RP-V Controllers .

RP-IO Modules

The RP-IO module provides I/O expansion to your HVAC application over BACnet MS/TP. The I/O module can share its I/O resources across applications running in automation servers, RP and MP controllers, or third-party systems. With the support of local alarms and local trend logs, the I/O module avoids unnecessary traffic over the network while being able to log important information locally. The I/O module can be installed near facilities in the field, away from the automation server or the RP or MP controller.

For more information, see RP-IO Modules .

RP Controller Expansion Modules

The RP controller expansion modules provide a range of devices that can be combined to form a connected room solution. The RP controller expansion modules are connected to the RP controller room bus and provide the RP controllers with I/O expansion and sensors that enable lighting and blind control.

For more information, see RP Controller Expansion Modules .

RP Controller Expansion Zigbee Modules

The RP controller expansion Zigbee modules provide devices that can be used to form a connected room solution. The RP controller expansion Zigbee modules are connected to the RP-C room controllers through the Zigbee TM wireless protocol and provide the controllers with I/O expansion that enable lighting control.

For more information, see RP Controller Expansion Zigbee Modules .

Remote Control

The RP-C-RC-BLE remote control connects wirelessly to the RP controller expansion sensor modules, such as the Multi-sensor and Insight-Sensor, and enables the occupants of modern office buildings to control the comfort level of their space.

For more information, see RP-C-RC-BLE .

KNX Modbus Gateway

The KNX Modbus gateway RP-C-EXT-KNX connects to the RP-C controllers and provides an interface between the controller and KNX devices such as push-buttons, sensors, and control units for lights, blinds, and room temperature.

For more information, see KNX Modbus Gateway RP-C-EXT-KNX .

SpaceLogic Sensor Devices

SpaceLogic Sensors are a family of living space sensors designed for BACnet/IP controllers using the EcoStruxure Building Operation user interface. These sensors use an RJ-45 sensor bus that provides communication and power from the BACnet/IP controller.

For more information, see SpaceLogic Sensors .

SpaceLogic Bluetooth Adapter

The SpaceLogic Bluetooth Adapter is plugged into a SpaceLogic Sensor to provide a wireless Bluetooth connection to the BACnet/IP controller (Sensor Bus compliant controller) for commissioning, maintenance, and troubleshooting of the controller and the sensor.

For more information, see SpaceLogic Bluetooth Adapter .

Wireless Adapter - Advanced

Wireless Adapter - Advanced is a USB-based wireless adapter that enables Zigbee TM wireless connectivity with an RP controller or automation server, extending the controller's or server's point count and bringing flexibility in retrofit applications.

For more information, see Wireless Adapter - Advanced .

AD v3

Advanced Display v3 (AD v3) is the successor to AD v2. AD v3 provides an industrial grade Human Machine Interface (HMI), with battery-free power supply, for local access to the EcoStruxure BMS servers.

For more information, see AD v3 .

Operator Display

SpaceLogic™ Operator Display is a touch-screen Human Machine Interface (HMI) for SpaceLogic controllers and servers, designed for local monitoring of building controllers in small and medium-sized buildings, as well as in large buildings with comprehensive building management systems. Operator Display is specifically designed for equipment rooms and it simplifies operations, service, and troubleshooting for System Integrators and Service Engineers, as well as for non-technical users (notably Facility Managers and Janitors).

For more information, see Operator Display .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, RP and MP controllers, IP-IO and RP-IO modules, RP controller expansion modules, Operator Display, and Twisted Pair Adapter.

For more information, see Wiring .

  • EcoStruxure Building Management Overview
  • Terminal Bases
  • PS-24V Power Supplies
  • AS-P Servers
  • Central IO Modules
  • Central IO Modules v2
  • AS-B Servers
  • MP-C Controllers
  • MP-V Controllers
  • IP-IO Modules
  • RP-C Controllers
  • RP-V Controllers
  • RP-IO Modules
  • RP Controller Expansion Modules
  • RP Controller Expansion Zigbee Modules
  • RP-C-RC-BLE
  • KNX Modbus Gateway RP-C-EXT-KNX
  • ETS Database for the KNX Modbus Gateway
  • SpaceLogic Sensors
  • SpaceLogic Bluetooth Adapter
  • Wireless Adapter - Advanced
  • AD v3
  • Operator Display
  • Wiring