earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: AO-8, AO-V-8, DI-16, DO-FA-12, DO-FC-8, AS-P, PS-24V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Functionalities: Hardware
Product version: 2022
10/7/2024

AS-P Servers

arrow1_rotationElectronics Modules arrow1_rotationTerminal Bases arrow1_rotationAS-P Server and Terminal Base Models arrow1_rotationMemory arrow1_rotationSupported Building Standards arrow1_rotation AS-P Server Communication Ports arrow1_rotationAS-P Server Screw Terminals arrow1_rotationAS-P Server LEDs arrow1_rotationReset Functions arrow1_rotationCommunication Port Wiring arrow1_rotationAS-P Server Software arrow1_rotationAutomation Server Replacement Using Restore arrow1_rotationSpecifications arrow1_rotationInternal Configuration

The AS-P server offers enhanced processor performance, increased memory size, dual Ethernet ports, and high-speed USB interfaces. The AS-P server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The AS-P controls and supervises equipment, typically HVAC equipment. AS-P servers use Central IO module with connected field devices, such as sensors and actuators, to do that.

AS-P servers are based on the patented two-piece design. Each AS-P server consists of an electronics module and a terminal base.

The AS-P server is installed with the Central IO modules on DIN rails in cabinets. The AS-P server electronics module uses a W1 enclosure. Power is supplied through the terminal base backplane.

 
action_zoom_plus_stroke  AS-P server
Figure: AS-P server

Electronics Modules

The electronics module is the main component of SpaceLogic devices that are based on the patented two-piece design. The electronics module is installed on a terminal base, which constitutes the second component of the device.

For more information, see Electronics Modules .

Terminal Bases

The terminal bases are used for SpaceLogic devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SpaceLogic device installed to the right (next terminal base in the chain).

For more information, see Terminal Bases .

AS-P Server and Terminal Base Models

The AS-P server comes in four models that offer support for different functions.

Model

LonWorks

Secure Boot

AS-P

Yes

No

AS-P-NL

No

No

AS-P-S a

Yes

Yes

AS-P-NLS

No

Yes

  1. The AS-P-S model is available in a Buy American Act (BAA) compliant variant named AS-P-SBA. For more information, see the SpaceLogic AS-P Specification Sheet. The BAA compliant variant does not differ in terms of hardware and functionality.

The AS-P-S and AS-P-NLS models are hardware only. An AS-P software package needs to be purchased separately. For more information, see the SpaceLogic AS-P Specification Sheet.

The following terminal base model is used with the AS-P server models (electronics modules).

Model

TB-ASP-W1 a

  1. The terminal base model is available in a variant named TB-ASP-W1-BAA, which is included in a Buy American Act (BAA) compliant bundle along with the AS-P-SBA server. For more information, see the SpaceLogic AS-P Specification Sheet. TB-ASP-W1-BAA does not differ from TB-ASP-W1 in terms of hardware and functionality.

Memory

An AS-P server has two types of memory:

  • 512 MB DDR3 SDRAM (for program execution)

  • 4 GB eMMC memory (for storage)

If a power outage occurs, all important variables are automatically saved to the eMMC memory before complete shutdown. When power returns, this data retention function helps ensure that the AS-P server can continue to run with the correct set of values.

Supported Building Standards

The AS-P server natively communicates with three of the most popular communication protocols:

  • BACnet: The AS-P server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to MP and RP controllers, b3 BACnet devices, and BACnet devices. The AS-P server also supports BACnet/SC applications as a BACnet/SC node or BACnet/SC router, which allows the AS-P server to be in BACnet/SC networks and support applications that connect BACnet/IP or MS/TP networks with BACnet/SC networks.

  • LonWorks: The AS-P server has a built-in FTT-10 port, which enables access to Xenta devices and LonWorks devices.

  • Modbus: The AS-P server natively integrates Modbus RS-485 client and server configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.

Note:

The AS-P server models AS-P-NL and AS-P-NLS do not support LonWorks.

AS-P Server Communication Ports

An AS-P server has the following communication ports:

  • 2 Ethernet 10/100 megabit ports

  • 2 RS-485 ports

  • 2 LonWorks (TP/FT and RS-485) ports (not available on the AS-P-NL and AS-P-NLS models)

  • 1 USB host port

  • 1 USB device port

  • 1 backplane I/O bus port

For more information, see AS-P Server Communication Ports .

AS-P Server Screw Terminals

There are pluggable screw terminals at the top of an AS-P server.

For more information, see AS-P Server Screw Terminals .

AS-P Server LEDs

There are several LEDs on the front panel of an AS-P server.

For more information, see AS-P Server LEDs .

Reset Functions

There are four different types of reset for the automation servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the automation server can be reset using the reset button or a command from WorkStation.

For more information, see Automation Server Reset Functions .

Communication Port Wiring

The wiring recommendations for the communication ports on the automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display devices apply to wires and cables used for RS-485 communications, LonWorks communications, USB connections, Ethernet connections, sensor bus connections, room bus connections, and RP controller Modbus network connections. Always use the recommended cables and wires.

For more information, see Communication Port Wiring .

AS-P Server Software

Before you engineer an AS-P server, install the AS-P server software on the server using Device Administrator. The software is not pre-loaded on the AS-P servers.

For more information, see Installing AS-P or AS-B Software .

Automation Server Replacement Using Restore

Backup and Restore helps assure that automation server data can be restored to a replacement automation server in the event of detected failure, or to the same automation server in the event of data loss. As a precaution, you back up your automation servers regularly so that you can use the most current backup to restore the automation server data to a replacement automation server. You also configure the new automation server to match the name and the network settings of the replaced automation server so the system can identify this automation server when online.

For more information, see Automation Server Replacement Using Restore .

Specifications

Electrical
DC input supply power
10 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.321 kg (0.71 lb)
Weight excluding terminal base
0.245 kg (0.54 lb)
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
Dual 2-wire ports, bias 5.0 VDC
LonWorks a
TP/FT-10
Communications
BACnet
BACnet/IP and MS/TP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BTL B-BC (BACnet Building Controller) a
Modbus a
Modbus TCP, client and server
  
Serial, RS-485, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
LNS
LNS version
OpenLNS
  
Installed on WorkStation PC
LonMark
Resource files version
14.00
CPU
Frequency
500 MHz
Type
SPEAr1380, ARM Cortex-A9 dual-core
DDR3 SDRAM
512 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance

Internal Configuration

All serial communication ports of the AS-P server module refer to signal ground as shown in the figure below.

 
action_zoom_plus_stroke  AS-P server internal configuration
Figure: AS-P server internal configuration
Note:

The AS-P server models AS-P-NL and AS-P-NLS do not have LonWorks (LON) communication ports.

The I/O bus in the terminal base provides the AS-P server module with power and an address.

The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the Central IO module and the automation server.

  • Hardware Overview
  • Electronics Modules
  • Terminal Bases
  • AS-P
  • AS-P Server Communication Ports
  • AS-P Server Screw Terminals
  • AS-P Server LEDs
  • Automation Server Reset Functions
  • Communication Port Wiring
  • Installing AS-P or AS-B Software
  • Automation Server Replacement Using Restore