The PS-24V is mounted on the Terminal Base model TB-PS-W1. The TB-PS-W1 appears similar to the TB-AS-W1 terminal base as seen in the figures in the section that follows. For more information, see AS-P and AS-P-NLS Installation .
They differ in the printed circuit board function provided in each.
There may be multiple PS-24V modules on an I/O bus, but there must be one located in the first, leftmost position on the bus (directly to the left of the Smoke Control Server). The connector extending from the right side of the first TB-PS-W1 base is the beginning of the I/O bus. The TB-ASP-W1 terminal base (holding the AS-P-SMK or AS-P-NLS-SMK) the TB-ASP-W1 base (holding the Automation Server AS-SMK), is located adjacent and to the right of the first PS-24V. The TB-ASP-W1 base slides to the left on the DIN rail to receive and mate with the connector extending from the TB-PS-W1 base.
The PS-24V receives input power in the form of 24 VAC +/-20% (60VA max) and delivers a 24 VDC +/-1V (30W) to the terminal base backplane. In smoke control applications, the 24-30 VDC power input capability is not used. The terminal base is typically wired before plugging in electronic module (the PS-24V). Only terminals 1, 2 and 4 are used in the power supply terminal base for power input. The following diagram shows the terminations.
You connect a PS-24V power supply module as follows:
Connect a 24 VAC source (from one of the transformers listed in this guide) to terminals 1 and 2 on the terminal base using 18 AWG (or larger) wire
For more information, see Transformers .
Connect terminal 4 to the Earth or Signal ground rail in the enclosure using 16 AWG (or larger) wire
Use the power budget table to determine how many and what type of Central IO modules you can power from this PS-24V module. You must also use the table to determine where you must install another PS-24V module to power additional Central IO modules.
For more information, see Power Rating .
You must connect the additional PS-24V modules to 24 VAC input power as shown.
The specifications for the PS-24V are as follows:
|
Power Input |
|
|
AC Input Voltage |
24VAC Class 2 |
|
AC Input Range |
+/- 20% 50/50Hz |
|
Maximum Current |
2.5 A rms |
|
Transformer Size |
60VA or larger |
|
Power Output |
|
|
DC Output |
24VDC +/- 1VDC |
|
Maximum Power |
30W |
|
Environment |
|
|
Op. Temperature |
0 to 50 o C 32 to 122 o F |
|
Humidity |
95% Max. nonCondensing |
|
Mechanical |
|
|
Housing Rating |
IP20 |
|
Plastic Rating |
UL94-5VB |
The PS-24V Status LED indicates the condition of the device as follows:
|
LED Patterns |
Condition of the PS-24V |
|
Green, constant |
Output voltage and load OK |
|
Red/green, flashing |
Output slightly overloaded |
|
Red, constant |
Output overloaded |
|
No light |
No input power |
The Main Power LED is illuminated when the module receives 24 VAC power.
The LEDs provided on the PS-24V, the Smoke Control Servers and all of the Central IO modules are intended to support diagnostic and service functions for the modules. For more information, see Module and MP Controller Status LEDs .