Hardware Installation

Hardware Installation


Products: AS-P
Functionalities: Hardware, Vista Transition
Product version: 2.0, 2.1, 3.0, 3.1, 3.2
6/6/2019

Xenta to AS-P Adapter

Regulatory Compliance and Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

The technical literature and declarations of conformity can be accessed on the Schneider Electric Exchange website, ecobuilding.schneider-electric.com. Contact your local Schneider Electric sales office for hard copy of documentation or for additional information.

Technical Literature

  • SmartX Controller - Hardware Reference Guide, 04-XX001-XX-en

Dimensions

 
action_zoom_plus_stroke

Installing the Adapter

 
action_zoom_plus_stroke

Installing the SmartX AS-P Server on the Adapter

 
action_zoom_plus_stroke

Connecting the Cables

 
action_zoom_plus_stroke

Part Numbers

Device

Part number

Xenta to AS-P Adapter

SXWASPXEN10001

SmartX Controller – AS-P

SXWASPXXX10001

TAC Xenta 400 Terminal Part

007309020

Specifications

Xenta to AS-P Adapter
AC input
Operating voltage range
24 VAC ± 20 %
 
action_zoom_plus_stroke
, 50/60 Hz
Recommended transformer rating
≥16 VA
DC input
Operating voltage range
19.2-40 VDC
 
action_zoom_plus_stroke
Power consumption
max. 15 W
DC output
Output voltage
24 VDC ± 1 V
Output power
10 W
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
Regulatory compliance
EMC, safety, and environment
FCC CFR 47 Part 15 Class B, ICES-003 Class B, RCM, CE - EMCD 2014/30/EU, WEEE 2012/19/EU, RoHS 2011/65/EU and 2015/863/EU, China RoHS SJ/T 11364-2014, UL 916 Listed products for the United States and Canada, Open Class Energy Management Equipment (UL file E80146.)

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke