A SmartX AS-B server is a powerful SmartX server that features both onboard I/O and built-in power supply. Like the other SmartX servers, the SmartX AS-B server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The SmartX server controls and supervises equipment, typically HVAC equipment. The SmartX AS-B server uses its onboard I/O with connected field devices, such as sensors and actuators, to do that.
The SmartX AS-B server is installed on DIN rails in cabinets.
The SmartX AS-B server comes in four models with different I/O point count and I/O mix.
Model |
I/O Points |
AS-B-24 |
24 |
AS-B-24H |
24 |
AS-B-36 |
36 |
AS-B-36H |
36 |
SmartX AS-B servers with “H” in the product name are equipped with a display for output override.
SmartX AS-B servers with 36 I/O points have the same small footprint as SmartX AS-B servers with 24 I/O points.
The SmartX AS-B server offers a mix of I/O point types that match a wide variety of HVAC applications. Most of the I/O points are universal inputs/outputs, which are highly flexible and can be configured as either inputs or outputs.
For more information, see SmartX AS-B Server Onboard I/O .
The output override function allows you to manually override outputs. This function can be used for testing, commissioning, and maintenance of equipment.
For more information, see Output Override Function .
The device has a built-in power supply designed to accommodate 24 VAC or 24 VDC input power. The main AC/DC input (L/+ and N/-) is galvanically isolated from the electronics. This removes the risk of damage due to earth currents and permits the input power to be wired without concern for polarity matching.
A SmartX AS-B server has two types of memory:
256 MB DDR2 SDRAM (for program execution)
4 GB eMMC memory (for storage)
If a power outage occurs, all important variables are automatically saved to the eMMC memory before complete shutdown. When power returns, this data retention function helps ensure that AS-B can continue to run with the correct set of values.
The SmartX AS-B server natively communicates with two of the most popular communication protocols:
BACnet: The SmartX AS-B server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to MP Series controllers, b3 BACnet devices, and BACnet devices.
Modbus: The SmartX AS-B server natively integrates Modbus RS-485 master and slave configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.
A SmartX AS-B server has the following communication ports:
2 Ethernet 10/100 megabit ports
1 RS-485 port
1 USB host port
1 USB device port
For more information, see SmartX AS-B Server Communication Ports .
SmartX AS-B servers use pluggable terminal blocks, which are easy to install and remove from the device. The terminal blocks are delivered with the device.
For more information, see SmartX AS-B Server Screw Terminals .
There are five LEDs on the front panel of the SmartX AS-B server.
For more information, see SmartX AS-B Server LEDs .
There are four different types of reset for the SmartX servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the SmartX server can be reset using the reset button or a command from WorkStation.
For more information, see SmartX Server Reset Functions .
The SmartX AS-B servers are designed for installing on DIN rails in a cabinet.
For more information, see SmartX AS-B Server Device Installation .
The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, and SmartX IP Controller devices.
For more information, see Wiring .
Before you engineer a SmartX AS-B server, install the SmartX AS-B server software on the server using Device Administrator. The software is not pre-loaded on the SmartX AS-B servers.
For more information, see Installing SmartX AS-P or SmartX AS-B Software .
Backup and Restore helps assure that SmartX server data can be restored to a replacement SmartX server in the event of detected failure, or to the same SmartX server in the event of data loss. As a precaution, you back up your SmartX servers regularly so that you can use the most current backup to restore the SmartX server data to a replacement SmartX server. You also configure the new SmartX server to match the name and the network settings of the replaced SmartX server so the system can identify this SmartX server when online.
For more information, see SmartX Server Replacement Using Restore .
AC input | |
Nominal voltage
|
24 VAC
|
Operating voltage range
|
+/- 20 %
|
Frequency
|
50/60 Hz
|
Maximum current
|
0.5 A rms
|
Recommended transformer rating
|
≥15 VA
|
DC input | |
Nominal voltage
|
24 to 30 VDC
|
Operating voltage range
|
21 to 33 VDC
|
Maximum power consumption
|
10 W
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Maximum humidity
|
95 % RH non-condensing
|
Material | |
Plastic flame rating
|
UL94-5VB
|
Enclosure
|
PC/ABS
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
![]() |
|
Weight, including terminal blocks
|
0.504 kg (1.111 lb)
a
|
a) The weight includes the display and keys, which are 0.022 kg (0.049 lb). | |
Weight, excluding terminal blocks
|
0.420 kg (0.926 lb)
a
|
a) The weight includes the display and keys, which are 0.022 kg (0.049 lb). | |
Real-time clock | |
Accuracy in runtime mode
|
NTP server
|
Accuracy in backup mode, at 25 °C (77 °F)
|
+/-52 seconds per month
|
Backup time, at 25 °C (77 °F)
|
10 days
|
Communication ports | |
Ethernet
|
Dual 10/100BASE-TX (RJ45)
|
USB
|
1 USB 2.0 device port (mini-B)
|
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
|
|
RS-485
|
2-wire port, bias 5.0 VDC
|
Communications | |
BACnet
|
BACnet/IP and MS/TP, port configurable, default 47808
|
BTL B-BC (BACnet Building Controller)
a
|
|
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page. | |
Modbus
|
Modbus TCP, client and server
|
Serial, RS-485, client and server
|
|
TCP
|
Binary, port fixed, 4444
|
HTTP
|
Non-binary, port configurable, default 80
|
HTTPS
|
Encrypted supporting TLS 1.2, 1.1, and 1.0, port configurable default 443
|
SMTP
|
Email sending, port configurable, default 25
|
SMTPS
|
Email sending, port configurable, default 587
|
SNMP
|
version 3
|
Network supervision using poll and trap
|
|
Application alarm distribution using trap
|
|
CPU | |
Frequency
|
333 MHz
|
Type
|
SPEAr320S, ARM926 core
|
DDR2 SDRAM
|
256 MB
|
eMMC memory
|
4 GB
|
Memory backup
|
Yes, battery-free, no maintenance
|
The SmartX AS-B servers internal configuration with regards to the signal ground is shown in the following figure.
The earth ground terminal (