earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: RP-C
Functionalities: Hardware
Product version: 3.0, 3.1
7/27/2020

RP-C-16A Model

Regulatory Compliance and Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

The technical literature and declarations of conformity can be accessed on the Schneider Electric Exchange website, ecobuilding.schneider-electric.com. Contact your local Schneider Electric sales office for hard copy of documentation or for additional information.

Technical Literature

  • SmartX Controller - Hardware Reference Guide, 04-XX001-XX-en

Recommended Installation Location

The controller is intended for fan coil, ceiling systems, and other applications. The controller is typically installed next to or inside the fan coil equipment. The controller can be equipped with optional covers to reduce access to the screw terminals and wires.

Dimensions

 
action_zoom_plus_stroke

Installation Orientation Restrictions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail

Notice

CONTROLLER DAMAGE

Use the DIN rail end clip when you install the controller on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Flat Surface

 
action_zoom_plus_stroke

Installing and Removing the Optional Covers

 
action_zoom_plus_stroke

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • Turn off all power connected to this controller before working on the device.

  • Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs/outputs.

Failure to follow these instructions will result in death or serious injury.

Warning Warning

HAZARD OF ELECTRIC SHOCK

  • Do not use shielded Ethernet cables when connecting RP-C controllers.

  • Do not connect signal ground (RET terminals, USB shield, or antenna shield) between RP-C controllers without connecting at least one of the RET terminals to protective earth ground.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Notice

CONTROLLER DAMAGE

Before powering up the controller, ensure that the input power voltage level meets the specifications of the controller.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Wiring

For information on wiring, including connection diagrams, rating of and location of fuses (circuit breakers), and cable specifications, see the SmartX Controller - Hardware Reference Guide.

Part Numbers

Product

Part number

RP-C-16A-F-230V
SXWRCF16A10002
Optional covers
SXWRPCCOV10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Specifications

AC input
Nominal voltage
230 VAC
 
action_zoom_plus_stroke
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 VA
Overvoltage category
III
Pollution degree
2
AC output
Type
Isolated output
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Power rating
19 VA
Port types
USB device port
Mini-B
USB host port
Type-A, 5 VDC, 0.5 A
Ethernet port 1 and 2
10/100BASE-TX RJ45
Sensor bus
24 VDC, 2 W, RS-485 (RJ45)
Room bus
24 VDC, 3 W, RS-485 (RJ45)
Wireless connectivity
Bluetooth ® Low Energy (Bluetooth ® 5)
2.402 to 2.480 GHz, max. 10 dBm output power, 100 m (328 ft) line-of-sight range
Antenna
Integrated antenna
Approved external antenna (optional)
Manufacturer: Linx Technologies, Model: ANT-2.4-WRT-MON-SMA, Gain: 0.8 dBi, Type: Monopole, Impedance: 50 ohm, Connector: SMA
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
  
See section Installation Orientation Restrictions.
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
IP networking
IP address assignment methods
Static, DHCP, Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
Regulatory compliance
EMC, safety, and environment
RCM, CE - RED 2014/53/EU, WEEE 2012/19/EU, RoHS 2011/65/EU and 2015/863/EU, China RoHS SJ/T 11364-2014, eu.bac certified product (Licence No. 219832)
Ub – Universal I/O
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Channels
8
DO – Relay outputs
Relay contact rating
Pilot Duty (C300)
  
Min. current: 100 mA (5 VDC)
  
Resistive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 1)
  
Inductive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 0.4)
Channels
3
DO – High power relay outputs
Relay contact rating
Pilot Duty (B300)
  
Normally Open, resistive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 12 A (cos phi = 1)
  
Normally Closed, inductive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 3 A (cos phi = 0.4)
Channels
1
DO – Solid-state relay outputs
Output rating
30 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 2 A
  
Max. 4 A total load
Channels
4

eu.bac Approved Controller Applications

A eu.bac approved controller application must operate in the controller to maintain compliance with the eu.bac certification. Approved controller applications can be downloaded from the Schneider Electric BMS Applications website, bms-applications.schneider-electric.com.

 
action_zoom_plus_stroke