Hardware versions: v9 and earlier
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
The controller is intended for fan coil, ceiling systems, and other applications. The controller is typically installed next to or inside the fan coil equipment. The controller can be equipped with optional covers to reduce access to the screw terminals and wires.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
For information on wiring, including connection diagrams, rating of and location of fuses (circuit breakers), and cable specifications, see the SpaceLogic and EasyLogic - Hardware Reference Guide.
Product |
Part number |
RP-C-16A-F-230V
|
SXWRCF16A10002
|
Optional covers
|
SXWRPCCOV10001
|
DIN-rail end clip, 25 pieces |
SXWDINEND10001 |
AC input | |
Nominal voltage
|
230 VAC
|
Maximum power consumption
|
65 VA
|
Power consumption without load
|
5 VA
|
Overvoltage category
|
III
|
Pollution degree
|
2
|
AC output | |
Type
|
Isolated Class 2 output
|
Nominal voltage
|
24 VAC
|
Power rating
|
19 VA
|
Port types | |
USB device port
|
Mini-B
|
USB host port
|
Type-A, 5 VDC, 0.5 A
|
Ethernet port 1 and 2
|
10/100BASE-TX RJ45
|
Sensor bus
|
24 VDC, 2 W, RS-485 (RJ45)
|
Room bus
|
24 VDC, 3 W, RS-485 (RJ45)
|
Wireless connectivity | |
Bluetooth
®
Low Energy (Bluetooth
®
5)
|
2.402 to 2.480 GHz, max. 10 dBm output power, 100 m (328 ft) line-of-sight range
|
Antenna
|
Integrated antenna
|
Approved external antenna (optional)
|
Manufacturer: Linx Technologies, Model: ANT-2.4-WRT-MON-SMA, Gain: 0.8 dBi, Type: Monopole, Impedance: 50 ohm, Connector: SMA
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
See section Installation Orientation Restrictions.
|
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94-5VB
|
IP networking | |
IP address assignment methods
|
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
|
Ub – Universal I/O | |
Input rating
|
24 VDC
|
Voltage output rating
|
0 to 10 VDC
|
Channels
|
8
|
DO – Relay outputs | |
Relay contact rating
|
Pilot Duty (C300)
|
Min. current: 100 mA (5 VDC)
|
|
Resistive: 250 VAC
|
|
4 A (cos phi = 1)
|
|
Inductive: 250 VAC
|
|
4 A (cos phi = 0.4)
|
|
Channels
|
3
|
DO – High power relay outputs | |
Relay contact rating
|
Pilot Duty (B300)
|
Normally Open, resistive: 250 VAC
|
|
/ 24 VDC
|
|
Normally Closed, inductive: 250 VAC
|
|
/ 24 VDC
|
|
Channels
|
1
|
DO – Solid-state relay outputs | |
Output rating
|
30 VAC
|
Max. 4 A total load
|
|
Channels
|
4
|
A eu.bac approved controller application must operate in the controller to maintain compliance with the eu.bac certification. Approved controller applications can be downloaded from the Schneider Electric BMS Applications website, bms-applications.schneider-electric.com.