Hardware Installation Hardware Installation 12/3/2022
Products: IP-IO
Functionalities: Hardware
Product version: 3.3, 2022

SpaceLogic™ IP-IO

Part numbers: SXWIPIOAA10001, SXWIPIOBA10001, and SXWIPIOCA10001

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

Installation Orientation Restrictions

Installing the Device on a DIN Rail

Notice

EQUIPMENT DAMAGE

Use the DIN rail end clip when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

Installing the Device on a Flat Surface

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • Disconnect all line voltage connected to the IP-IO module and its relay outputs before working on the device.

  • More than one disconnect switch may be required to de-energize this equipment before servicing.

  • Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the IP-IO module universal inputs/outputs.

Failure to follow these instructions will result in death or serious injury.

Notice

EQUIPMENT DAMAGE

Before powering up the IP-IO module, ensure that the input power polarity is correct, the voltage level meets the specifications of the module, and the terminal blocks are plugged into the correct connector headers on the module.

Failure to follow these instructions can result in equipment damage.

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

Part Numbers

Product

Part number

IP-IO-DI10
SXWIPIOAA10001
IP-IO-UIO10
SXWIPIOBA10001
IP-IO-UIO5DOFA4
SXWIPIOCA10001
MP-C DISPLAY
(MP-C override display module)
SXWMPCDSP10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Specifications
AC input
Nominal voltage
24 VAC 50/60 Hz
Power consumption
17 VA
DC input
Nominal voltage
24 to 30 VDC
Power consumption
9 W
Port types
USB device port
Mini-B
USB host port
Type-A
Ethernet port 1 and 2
10/100BASE-TX RJ45
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
  
See section Installation Orientation Restrictions.
  
MP-C Display temperature range: -30 to +60 °C (-22 to +140 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
DI – Digital inputs
Input rating
24 VDC , 2.4 mA
Channels
IP-IO-DI10: 10; IP-IO-UIO10: 0; IP-IO-UIO5DOFA4: 0
Ub – Universal I/O
Input rating
24 VDC , 2.4 mA
Voltage output rating
0 to 10 VDC , 5 kohm (min.)
Channels
IP-IO-DI10: 0; IP-IO-UIO10: 10; IP-IO-UIO5DOFA4: 5
DO – Relay outputs
Relay contact rating
250 VAC / 30 VDC , 2 A
  
Pilot Duty (C300)
Channels
IP-IO-DI10: 0; IP-IO-UIO10: 0; IP-IO-UIO5DOFA4: 3
DO – High power relay outputs
Relay contact rating
250 VAC / 24 VDC , 12 A
  
Pilot Duty (B300)
Channels
IP-IO-DI10: 0; IP-IO-UIO10: 0; IP-IO-UIO5DOFA4: 1