You wire the terminal blocks installed on the IP-IO module to connect I/O devices and power.

Show More
action_close

The IP-IO module device can be installed on a DIN rail or other flat surface inside a cabinet.

A DIN rail is a common and convenient technique for installing the IP-IO module along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the IP-IO module rail and adjacent rails or other panel-mounted devices.

The IP-IO module is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke IP-IO module installed on a horizontal DIN rail
Figure: IP-IO module installed on a horizontal DIN rail

The IP-IO module can also be installed vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. Installing the IP-IO module face down from a ceiling or face up on a horizontal surface is not supported.

 
action_zoom_plus_stroke Restrictions regarding the installation orientation
Figure: Restrictions regarding the installation orientation
Notice

Loss of data

Install the IP-IO module horizontally in rooftop applications, -40 to +60 °C (-40 to +140 °F), to ensure that the device stays within the thermal specifications. Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Failure to follow these instructions can result in loss of data.

Install the IP-IO modules in a cabinet with ample space between the DIN rails and the IP-IO modules for sufficient ventilation.

 
action_zoom_plus_stroke IP-IO modules installed on horizontal DIN rails in a cabinet
Figure: IP-IO modules installed on horizontal DIN rails in a cabinet

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

Notice

Loss of data

Equipment damage

Use an end clip (part number SXWDINEND10001) when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

Failure to follow these instructions can result in loss of data.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
Figure: End clip for DIN 35 fixed across the DIN rail

The IP-IO module is delivered with terminal blocks installed on the device.

The terminal blocks are removable. You can replace an IP-IO module in seconds because no terminal wiring is affected. The only exception is the high power relay output on the IP-IO-UIO5DOFA4 model, which uses a two-position fixed terminal block due to current requirements.

All IP-IO module models can be equipped with MP-C Display (part number SXWMPCDSP10001), which is an add-on module that enables manual override control of analog and digital outputs. The module consists of an LCD display and keys. The module is designed for permanent installation.

 
action_zoom_plus_stroke MP-C Display installed on an IP-IO module
Figure: MP-C Display installed on an IP-IO module
Notice

Loss of data

Do not try to remove the MP-C Display module as it may damage the enclosure and the module. Once installed, the MP-C Display module cannot be removed.

Failure to follow these instructions can result in loss of data.

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

De‑energize all hazardous voltage sources connected to the relay outputs before wiring. More than one disconnect switch may be required to fully de‑energize the equipment.

Failure to follow these instructions will result in death or serious injury.

Caution Caution

RISK OF ELECTRIC SHOCK

Disconnect the 24 VAC/DC power supply and other electrically powered equipment before wiring.

Failure to follow these instructions can result in injury or equipment damage.

Notice Notice

EQUIPMENT DAMAGE

Always use the recommended cables (or wires with larger cross-sectional area). For more information, see Wiring .

Failure to follow these instructions can result in equipment damage.

To wire a terminal block on an IP-IO module
  1. De-energize all hazardous voltage sources connected to the relay outputs of the IP-IO module.

    This only applies to the IP-IO-UIO5DOFA4 model, which has relay outputs.

  2. Disconnect the 24 VAC/DC power supply and other electrically powered equipment that is connected to the IP-IO module.

  3. Ensure that the correct terminal block is used and that it is properly installed on the IP-IO module. For more information, see Installing a Terminal Block on an IP-IO Module .

  4. Loosen the screws of the terminal block.

  5. Strip approximately 7 mm (0.3 inch) of the insulation from the end of each wire.

  6. Insert the stripped end of each wire fully into its intended terminal. Ensure that no bare wire strands extend from the terminal.

  7. Tighten the screws using a small flat-blade screwdriver. Ensure that the screws are fully tightened. Use the following recommended screw tightening torque: 0.56 Nm (5 lbf.in).

  • IP-IO Module Device Installation
  • IP-IO Module Screw Terminals
  • IP-IO-DI10 Screw Terminals
  • IP-IO-UIO10 Screw Terminals
  • IP-IO-UIO5DOFA4 Screw Terminals
  • Wiring
  • Installing a Terminal Block on an IP-IO Module
  • Removing a Terminal Block from an IP-IO Module
  • Powering Up an IP-IO Module