earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: RP-C-EXT-REL-4
Functionalities: Hardware
Product version: 3.3, 2022, 2023, 2024, 7.0, 7.1
2/11/2026

SpaceLogic™ RP-C-EXT-REL-4

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installation Orientation Restrictions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail

Notice

EXPANSION MODULE DAMAGE

Use the DIN rail end clip when you install the RP controller expansion module on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Flat Surface

 
action_zoom_plus_stroke

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Turn off all power connected to this equipment before working on the equipment.

Failure to follow these instructions will result in death or serious injury.

Notice

EXPANSION MODULE DAMAGE

Before powering up the RP controller expansion module, ensure that the input power voltage level meets the specifications of the device.

Failure to follow these instructions can result in equipment damage.

Notice

CONNECTOR OR CABLE ASSEMBLY DAMAGE

Anchor the excess cabling to alleviate all stresses on connectors and cable assemblies.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Wiring

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

RP-C-EXT-REL-4
SXWREREL410001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Mounting plate - RP controller expansion modules, 5 pieces

SXWREMPK510001

Required External Connectors

Table: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Tightening torque, screws

Nm (lbf.in)

Marking

Color of coding

/housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female

5.6–11

(0.22–0.43)

0.3–0.5

(2.7–4.4)

L, PE, N

Black

/Black

100

Relay outputs

SXWRPCCONWWREL

91.932.4053.1

Male

5.6–11

(0.22–0.43)

0.3–0.5

(2.7–4.4)

N, PE, L

Black

/Black

100

Digital inputs

SXWRPCCONWDI

91.921.2353.0

Female

3.4–5.5

(0.14–0.21)

0.3–0.5

(2.7–4.4)

1, 2

1: DI1..4

2: RET

Light blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

Specifications

AC input
Nominal voltage
100 to 277 VAC
 
action_zoom_plus_stroke
50/60 Hz
Maximum current consumption
10 A
Overvoltage category
III
DC input
Room bus power consumption
0.3 W (24 VDC)
Port types
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043 (Approved for plenum installations)
Relay outputs
Outputs
4, Relay 1 to Relay 4 (L, PE, N terminals)
Power distribution
100 to 277 VAC (same voltage as power supply)
  
Maximum 5 A load per output
  
Maximum 10 A total load for the 4 outputs
  
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
DI – Digital inputs
Input rating
5 VDC
 
action_zoom_plus_stroke
, 2.2 mA, SELV
Inputs
4

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke
  • RP Controller Expansion Module Device Installation
  • I/O Wiring
  • Communication Port Wiring
  • RP-C-EXT-REL-4
  • Hardware Overview