Hardware Installation

Hardware Installation


Products: RP-C-EXT-KNX
Functionalities: Hardware
Product version: 3.3, 2022, 2023, 2024, 7.0, 7.1
2/11/2026

SpaceLogic™ RP-C-EXT-KNX

arrow1_rotationSafety Information arrow1_rotationTechnical Literature arrow1_rotationDimensions arrow1_rotationInstalling the Device arrow1_rotationConnecting the Device to the RP-C RS-485 Port arrow1_rotationPart Numbers arrow1_rotationSpecifications

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installing the Device

 
action_zoom_plus_stroke

Connecting the Device to the RP-C RS-485 Port

 
action_zoom_plus_stroke

Terminal (Label)

Description

RJ45 Pin

1 (–)

Ground

5

2 (–)

Ground

Not connected

3 (+)

+24 VDC

4, 7

4 (–)

Ground

8

5 (A)

Modbus/RS485+ (A)

3

6 (B)

Modbus/RS485– (B)

6

Part Numbers

Product

Part number

RP-C-EXT-KNX
SXWREKNX10001

Specifications

DC input
Nominal voltage
24 VDC
 
action_zoom_plus_stroke
  
Powered by the RP-C
Maximum power consumption
<0.24 W from the KNX bus
  
<0.24 W from the RP-C
Connectors
Power supply and Modbus (RS-485)
3-position pluggable screw terminal block for power supply from the RP-C
  
3-position pluggable screw terminal block for Modbus communication with the RP-C
  
Wire cross-sectional area: 0.34 to 2.5 mm 2 (22 to 14 AWG)
KNX bus
4-conductor KNX connectors with PUSH WIRE® connection, 2-pole, dark gray/red
Operation environment
Ambient temperature, operating
-5 °C to +45 °C (23 °F to +113 °F)
Humidity
5 to 93 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
 