Specifications

Specifications


Products: Operator Display
Functionalities: Hardware
Product version: 3.3, 2022, 2023, 2024, 7.0
7/7/2025

SpaceLogic Operator Display

arrow1_rotationIntroduction arrow1_rotationFeatures arrow1_rotationSpecifications
 
action_zoom_plus_stroke HMIST6400SL
Figure: HMIST6400SL

Introduction

SpaceLogic™ Operator Display is a touch-screen Human Machine Interface (HMI) for SpaceLogic controllers and servers, designed for local monitoring of building controllers in small and medium-sized buildings, as well as in large buildings with comprehensive building management systems. Operator Display is specifically designed for equipment rooms and it simplifies operations, service, and troubleshooting for System Integrators and Service Engineers, as well as for non-technical users (notably Facility Managers and Janitors).

Features

The simplified user interface and the intuitive touch-screen navigation make it easy to operate and maintain the system. Operator Display communicates quickly over BACnet/IP open protocol with a direct connection to SpaceLogic MP or RP controllers, IP-IO modules, AS-B or AS-P servers. Only one Operator Display is required per cabinet in the equipment room, so there is no need for more displays when a controller is added. The operator can view and acknowledge alarms, edit schedules, and adjust setpoint temperatures. Authorized operators can also view and override inputs, outputs, and other virtual points.

Fully integrated HMI solution

Operator Display offers a fully integrated HMI solution that provides benefits such as ease of use and installation.

Protective frame and ease of installation

Operator Display has an IP 65 rated frame that helps protect against dust and moisture. It is quick and easy to install.

It is important to note that this product is designed for indoor use only.

Touch-screen display

Operator Display features a large 7-inch, color touch-screen display.

Preinstalled software

Operator Display is delivered with the purpose-built application preloaded on the device so it is ready-to-use and commissioned quickly without the need for any programming or external tools.

Communication and power

Operator Display is powered by an external 24 VDC power supply (not included) through the DC power supply connector, and it communicates over BACnet/IP open protocol.

Table: Part Number

Product

Part number

Operator Display 7-inch bundle
(Includes HMI device, installation gasket, installation fasteners, screws, DC power supply connector, and installation sheet)
HMIST6400SL

Table: Spare Parts (Not Included)

Product

Part number

Installation gasket
(Provides dust and moisture resistance when this product is installed into a solid panel (1 piece))
HMIZS53W1
Installation fastener
(2 pieces/set)
HMIZSFIXTF1
Power supply connector for small panels
(10 pieces/set)
XBTZ3004

Table: Other Required Parts (Not Included)

Product

Part number

24 VDC power supply
(Typical examples)
ABLM1A24004, ABLM1A24006, ABLM1A24012, ABLM1A24025

Micro USB 2.0 OTG cable

USB stick (FAT formatted)

Specifications

System capacity
Maximum number of controllers or servers per display
Up to 7
DC input
Nominal voltage
24 VDC
Operating voltage range
+/- 20 %
Inrush current
30 A or less
Maximum power consumption
9 W
Immunity to microbreaks
5 ms
Environment
Physical environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +60 °C (-4 to +140 °F)
Humidity
10 to 90 % RH non-condensing
Pollution degree
2
Operating altitude
800 to 1,114 hPa (2,000 m (6,561 ft) or lower)
Mechanical environment
Vibration resistance
IEC/BS/EN 61131-2 compliant
  
5 to 9 Hz Single amplitude 3.5 mm (0.14 in)
  
9 to 150 Hz Fixed acceleration: 9.8 m/s 2
  
X, Y, Z directions for 10 cycles (approximately 100 minutes)
Shock resistance
IEC/BS/EN 61131-2 compliant: 147 m/s 2 , X, Y, Z directions for 3 times
Electrical environment
Electrical fast transient/burst
IEC/BS/EN 61000-4-4, 2 kV: Power port (display unit), 1 kV: Signal ports
Electrostatic discharge immunity
IEC/BS/EN 61000-4-2 Level 3, Contact discharge method: 6 kV, Air discharge method: 8 kV
Material
Enclosure
Polycarbonate (PC)
Front
Aluminum
Display
Polyethylene Terephthalate (PET)
Ingress protection rating
IP 65 (front of product that is exposed, on panel-mounted installation)
NEMA rating
NEMA 4 (front, indoor use)
  
NEMA 13 (front, in enclosure)
Plastic flame rating
UL94 V-0
Mechanical
Dimensions (W x H x D)
208 x 153 x 45 mm (8.19 x 6.02 x 1.77 in.)
See drawing below:
 
action_zoom_plus_stroke
Weight
0.8 kg (1.8 lb)
Installation
Mounted to the panel using 4 screws (included), conforming to UL 61010-1, CSA C22.2 No 61010-1, UL 61010-2-201, CSA C22.2 No 61010-2-201 (1.6 to 5 mm (0.1 to 0.2 in) thick panel), BS/EN 61131-2, and BS/EN 61000-6-2
Software compatibility
Customized alarm message support
EcoStruxure Building Operation software
version 3.3.1 and later
Agency compliances
Emission
BS/EN 61326-1, Class A; FCC Part 15, Sub-part B, Class A
  
BS/EN 61000-6-4
Immunity
BS/EN 61000-6-2
Safety standards
BS/EN 61131-2
  
UL 61010-1
  
CSA C22.2 No 61010-1
  
UL 61010-2-201
  
CSA C22.2 No 61010-2-201
Real-time clock
Power
Battery (CR2032)
Accuracy
+/- 20 ppm
Battery lifetime
5 years at room temperature a
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45) a
USB
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
  
1 USB 2.0 device port (micro-B)
RS-232C
1 COM1 (D-Sub, 9-pin, female) - Inactive
RS-485
1 COM2 (RJ45, female) - Inactive
Hardware
CPU type
ARM Cortex-A8 single-core
Frequency
800 MHz
Device memory (NAND Flash)
1 GB (including 180 MB for user data)
Backup memory (MRAM)
512 KB
Status indicator
LED (green, orange, and red)
  
Buzzer (not used)
Display
Display resolution
800 x 480 pixels (WVGA)
Display aspect ratio
16:10
Display size
7 inches (178 mm)
Display type
TFT LCD, touchscreen
  
Single touch analog resistive panel
Color
16 million colors
Display languages
Czech, Danish, English, Finnish, French, German, Italian, Norwegian, Polish, Portuguese, Russian, Slovak, Spanish, Swedish
Brightness control
400 cd/m 2
  
16 levels
LED lifetime a
50,000 hours
  • SpaceLogic MP-C Pro
  • SpaceLogic MP-V
  • SpaceLogic RP-C Advanced
  • SpaceLogic RP-V Advanced
  • SpaceLogic IP-IO
  • SpaceLogic AS-B
  • SpaceLogic AS-P