earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: MP-V
Functionalities: Hardware
Product version: 2023, 2024, 7.0, 7.1
7/8/2025

SpaceLogic™ MP-V-BAA

Part numbers: SXWMPV7AX10A02 and SXWMPV9AX10A02

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Installation Orientations

 
action_zoom_plus_stroke

Determining the Shaft Rotation Direction that Opens the Damper

 
action_zoom_plus_stroke

Determining the Damper Shaft Length and Diameter

 
action_zoom_plus_stroke

Moving the Damper Shaft Mounting Screws to the Alternative Positions for Short Shafts Only

 
action_zoom_plus_stroke

Installing the MP-V over the Damper Shaft

 
action_zoom_plus_stroke

Securing the MP-V to the Damper Shaft and the VAV Box

 
action_zoom_plus_stroke

Adjusting the Position of the CW Travel Adjustment Screw (Open CW Stop)

Notice

VAV DAMPER NOT PROPERLY CONTROLLED

Ensure that the VAV controller damper actuator can rotate freely between the fully open and fully closed positions.

Failure to follow these instructions can result in the VAV damper not being properly controlled by the controller.

 
action_zoom_plus_stroke

Connecting the Air Flow Sensor

Notice

AIR FLOW SENSOR DAMAGE

Create a tubing dip that extends below the elevation of the barbed fittings to help prevent moisture from entering the VAV controller. This applies to all controller orientations.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Connections

Notice

CONTROLLER DAMAGE OR VAV DAMPER NOT PROPERLY CONTROLLED

  • Before powering up the controller, ensure that the input power polarity is correct, the voltage level meets the specifications of the controller, and the terminal blocks are plugged into the correct connector headers on the controller.

  • Ensure that the controller is properly installed and secured before the application of 24 VAC power and the damper position calibration that starts automatically with it.

Failure to follow these instructions can result in equipment damage or the VAV damper not being properly controlled by the controller.

 
action_zoom_plus_stroke
 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

MP-V-7A-BAA
SXWMPV7AX10A02
MP-V-9A-BAA
SXWMPV9AX10A02

Spare terminal blocks for all MP-V models

SXWMPVCON10001

Adapter for damper shaft diameter 9.5 mm (3/8 inch)

AM-135

Specifications

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Power consumption
MP-V-7A: 21 VA
  
MP-V-9A: 22 VA
Port types
USB ports
Device (Mini-B), Host (Type-A)
Ethernet port 1 and 2
10/100BASE-TX (RJ45), IEEE 802.3 compliant
RS-485 port Com A
24 VDC, 2 W, RS-485 (RJ45)
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043 (Approved for plenum installations)
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
UI – Universal inputs
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Channels
MP-V-7A: 3; -9A: 4
DO – Triac outputs
Triac rating
Max. 30 VAC
 
action_zoom_plus_stroke
, 0.5 A
Channels
MP-V-7A: 3; -9A: 3
AO – Analog outputs
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Current output rating
0 to 20 mA, 650 ohm (max.)
Channels
MP-V-7A: 1; -9A: 2

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke
  • MP-V Device Installation
  • I/O Wiring
  • Communication Port Wiring
  • MP-V Controllers
  • Hardware Overview