Products: AO-8, AO-V-8, DI-16, DO-FA-12, DO-FC-8, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-4 v2, UI-8/AO-V-4, UI-8/AO-V-4 v2, UI-8/DO-FC-4, UI-8/DO-FC-4 v2
Functionalities: Hardware
Product version: 1.8, 1.9, 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024, 7.0, 7.1
2/11/2026

SpaceLogic™ TB-IO-W1-2

Part number: SXWTBIOW110002

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Overview

 
action_zoom_plus_stroke

Installing the Terminal Base

Notice

REDUCED LIFE SPAN OF ELECTRONICS MODULE

Always install the terminal base on a horizontal DIN rail to provide sufficient cooling air flow through the electronics module.

Failure to follow these instructions can result in reduced life span of the electronics module.

 
action_zoom_plus_stroke

Connecting the Next Terminal Base

Warning Warning

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Ensure that the module type and the terminal base type match.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

 
action_zoom_plus_stroke

Terminal Base and Applicable Electronics Modules (-H indicates Override Switch)

Device

Part number

SpaceLogic TB-IO-W1-2 Terminal Base
SXWTBIOW110002

SpaceLogic DI-16

SXWDI16XX10001

SpaceLogic UI-16

SXWUI16XX10001

SpaceLogic RTD-DI-16

SXWRTD16X10001

SpaceLogic DO-FA-12

SXWDOA12X10001

SpaceLogic DO-FA-12-H

SXWDOA12H10001

SpaceLogic DO-FC-8

SXWDOC8XX10001

SpaceLogic DO-FC-8-H

SXWDOC8HX10001

SpaceLogic AO-8

SXWAO8XXX10001

SpaceLogic AO-8-H

SXWAO8HXX10001

SpaceLogic AO-V-8

SXWAOV8XX10001

SpaceLogic AO-V-8-H

SXWAOV8HX10001

SpaceLogic UI-8/DO-FC-4-2
SXWUI8D4X10002
SpaceLogic UI-8/DO-FC-4-H-2
SXWUI8D4H10002
SpaceLogic UI-8/AO-4-2
SXWUI8A4X10002

SpaceLogic UI-8/AO-4-H-2
SXWUI8A4H10002
SpaceLogic UI-8/AO-V-4-2
SXWUI8V4X10002
SpaceLogic UI-8/AO-V-4-H-2

SXWUI8V4H10002

TB-IO-W1-2 can also be used with UI-8/DO-FC-4(-H), UI-8/AO-4(-H), and UI-8/AO-V-4(-H).

I/O Bus Addressing, Power Limits, and Cables

 
action_zoom_plus_stroke

S-Cables

Device

Part number

S-Cable, 1.5 m, angle

SXWSCABLE10002

S-Cable, 0.75 m, angle

SXWSCABLE10003

Connections for I/O Modules

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

 
action_zoom_plus_stroke

Wiring

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

Specifications

Operation environment
Ambient temperature, operating
0 to 60 °C (32 to 140 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
Electrical
I/O bus power
24 VDC
 
action_zoom_plus_stroke
, Class 2
  
Max. 20 W per I/O bus powered by AS-P-3
  
Max. 30 W per I/O bus powered by PS-24V
Maximum addresses per I/O bus
32
DI-16 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.6 W
Input rating
24 V, 2.4 mA
Channels
16 input
UI-16 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.8 W
Input rating
24 V, 2.4 mA
Channels
16 input
RTD-DI-16 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.6 W
Input rating
24 V, 2.4 mA
Channels
16 input
DO-FA-12(-H) Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.8 W
Relay contact rating
250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 2 A
  
Pilot Duty (Power Factor 0.35)
Channels
12 output
DO-FC-8(-H) Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 2.2 W
Relay contact rating
250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 3 A
  
Pilot Duty (Power Factor 0.35)
Channels
8 output
AO-8(-H) Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 4.9 W
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Current output rating
0 to 20 mA, 650 ohm (max.)
Channels
8 output
AO-V-8(-H) Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 0.7 W
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Channels
8 output
UI-8/DO-FC-4(-H)-2 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.9 W
Relay contact rating
250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 3 A
  
Pilot Duty (Power Factor 0.35)
Input rating
24 V, 2.4 mA
Channels
4 output/8 input
UI-8/AO-4(-H)-2 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 3.2 W
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Current output rating
0 to 20 mA, 650 ohm (max.)
Input rating
24 V, 2.4 mA
Channels
4 output/8 input
UI-8/AO-V-4(-H)-2 Module
DC input power
24 VDC
 
action_zoom_plus_stroke
, 1.0 W
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 5 kohm (min.)
Input rating
24 V, 2.4 mA
Channels
4 output/8 input

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke
  • Device Installation
  • I/O Wiring
  • Terminal Bases
  • Hardware Overview