The Twisted Pair Adapter is equipped with the following connectors:
4-position removable screw terminal block (Power input)
2-position removable screw terminal block (NET)
RJ45 port labelled Ethernet 10/100
The screw terminal blocks are used as follows:
4-position, rear terminal block: Power input
2-position, front terminal block: Twisted pair cable network (NET) connection
The screw terminal are wired and connected to an external power supply and a twisted pair cable network as described in the following table.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
|
Terminal number |
Designation |
Usage |
|
Power input |
|
|
|
1 |
L / + |
Line (L) lead at 24 VAC, 50/60 Hz or positive (+) lead at 24-30 VDC. |
|
2 |
N / – |
Neutral (N) lead at 24 VAC, 50/60 Hz or negative (–) lead at 24-30 VDC. Terminals 2, 3, and 4 are internally connected. |
|
3 |
|
Functional earth ground. Terminals 2, 3, and 4 are internally connected. |
|
4 |
|
Functional earth ground. Terminals 2, 3, and 4 are internally connected. |
|
Twisted pair cable network (NET) |
|
|
|
5 |
NET |
Twisted pair cable network connection. Polarity insensitive. |
|
6 |
NET |
Twisted pair cable network connection. Polarity insensitive. |
The RJ45 port is a standard Ethernet 10/100BASE-TX interface that supports data rates of 10 or 100 Mbit/s. It complies with the IEEE 802.3 Ethernet standard and is used to connect the device to a SpaceLogic BACnet/IP controller or automation server. Actual data throughput may vary depending on factors such as the type and length of the transmission medium, network topology, and the number of nodes.