earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: Twisted Pair Adapter
Functionalities: Hardware
Product version: 1.8, 1.9, 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024, 7.0, 7.1
12/18/2025

Wiring the Screw Terminals on a Twisted Pair Adapter for Connection to a Twisted Pair Cable Network

You wire the screw terminals on a Twisted Pair Adapter to connect the adapter to a twisted pair cable network. Always use the recommended wires (or wires with larger cross-sectional area).

Show More
action_close

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the Twisted Pair Adapter.

The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

Table: Wire Sizes and Lengths for the Twisted Pair Adapter

Terminals

Minimum Cross-sectional Area

Maximum Cable Length

Power input terminals (1, 2)

0.2 mm² (24 AWG) a

According to local wiring rules

Functional earth ground terminals (3, 4)

0.2 mm² (24 AWG) a b

According to local wiring rules

Twisted pair cable network (NET) terminals (5, 6)

0.52 mm² (20 AWG)

1200 m (3900 ft)
  1. Use wires rated for at least 90 °C (194 °F).
  2. The functional earth ground conductor must have a cross-sectional area at least equal to that of the power supply conductor.

Show More
action_close

The Twisted Pair Adapter is equipped with the following connectors:

  • 4-position removable screw terminal block (Power input)

  • 2-position removable screw terminal block (NET)

  • RJ45 port labelled Ethernet 10/100

 
action_zoom_plus_stroke Screw terminals and port
Figure: Screw terminals and port
Screw terminals

The screw terminal blocks are used as follows:

  • 4-position, rear terminal block: Power input

  • 2-position, front terminal block: Twisted pair cable network (NET) connection

The screw terminal are wired and connected to an external power supply and a twisted pair cable network as described in the following table.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

Table: Screw Terminals

Terminal number

Designation

Usage

Power input

1

L / +

Line (L) lead at 24 VAC, 50/60 Hz or positive (+) lead at 24-30 VDC.

2

N / –

Neutral (N) lead at 24 VAC, 50/60 Hz or negative (–) lead at 24-30 VDC.

Terminals 2, 3, and 4 are internally connected.

3

 
action_zoom_plus_stroke

Functional earth ground.

Terminals 2, 3, and 4 are internally connected.

4

 
action_zoom_plus_stroke

Functional earth ground.

Terminals 2, 3, and 4 are internally connected.

Twisted pair cable network (NET)

5

NET

Twisted pair cable network connection.

Polarity insensitive.

6

NET

Twisted pair cable network connection.

Polarity insensitive.

RJ45 port

The RJ45 port is a standard Ethernet 10/100BASE-TX interface that supports data rates of 10 or 100 Mbit/s. It complies with the IEEE 802.3 Ethernet standard and is used to connect the device to a SpaceLogic BACnet/IP controller or automation server. Actual data throughput may vary depending on factors such as the type and length of the transmission medium, network topology, and the number of nodes.

To wire the screw terminals on a Twisted Pair Adapter for connection to a twisted pair cable network
  1. Loosen the screws of the terminals for network connection. For more information, see Twisted Pair Adapter Screw Terminals and Port .

  2. Strip approximately 7 mm (0.3 inch) of the insulation from the end of each wire.

  3. Insert the end of the wire fully into its intended terminals. Ensure that no bare wire strands extend from the terminal.

  4. Tighten the screw using a small flat-blade screwdriver. Ensure that the screw is fully tightened. Use the following recommended screw tightening torque: 0.56 Nm (5 lbf.in).

  5. Repeat steps 2 to 5 until all screw terminals for the network connection on the adapter are correctly wired. For more information, see Twisted Pair Adapter Screw Terminals and Port .

    Note:

    Terminals 5 and 6 are polarity insensitive.

     
    action_zoom_plus_stroke
  6. Use appropriate cable strain relief methods, to help prevent any load applied to the cable from being transferred to conductor terminations.

  • Twisted Pair Adapter
  • Twisted Pair Adapter Screw Terminals and Port
  • Wiring
  • Wire Sizes and Lengths for the Twisted Pair Adapter