Input modules support a single electrical type, such as digital or universal inputs. The available input modules include the following:
DI-16
UI-16
RTD-DI-16
The DI-16 Central IO module is a digital input, 16-channel I/O module. You can use the DI-16 Central IO module for sensing of multiple dry digital inputs in applications such as equipment status or alarm point monitoring.
The maximum counter frequency is 25 Hz on all sixteen inputs. This input type is useful in metering applications.
The following input types are supported:
Digital input
Dry contact, Open Collector, or Open Drain
Per maggior informazioni, consulta DI-16 Central IO Module .
The UI-16 Central IO module is a 16-channel universal input I/O module with status indicators for each of the inputs. You can use this module for any mix of temperature, pressure, flow, status points, and similar inputs in a control system with a 0-10 V input range and a 12-bit A/D conversion. You can also make adjustments for various sensor types using the available pull-up resistors.
The following input types are supported:
Dry contact closing
Voltage 0–10 V
Current 0–20 mA
Thermistor – 10k Type I (Continuum), 10k Type II (I/NET), 10k Type III (Satchwell), 10k Linearized (Satchwell D?T), 10k Type IV (FD), and 10k Type V (FD w/ 11k shunt)
Thermistor – 1.8k (Xenta)
Thermistor – 1k (Balco)
Thermistor – 20k (Honeywell)
Thermistor – 2.2k (Johnson Controls)
Supervised
Per maggior informazioni, consulta UI-16 Central IO Module .
A Resistance Temperature Detector (RTD) is a sensing element that uses the change in the resistance of a metal, such as platinum or nickel, to measure temperature ranges from -50 °C to 150 °C (-58 to +302 °F). Due to their accuracy and repeatability, RTDs are used in scientific and industrial applications to measure temperature for kilns, gas turbine exhaust, diesel engines, and other industrial processes as well as for room temperature measurement.
The RTD-DI-16 Central IO module is a 16-channel I/O module with 1 return per 2 inputs. It supports the following input types:
RTD temperature including:
Pt100
Pt1000
Ni1000
LG-Ni1000
JCI-Ni1000
RTD resistive including:
100 ohm
1,000 ohm
Resistive including 0 to 15 kohm
Digital
Counter
The RTD connection type is either a 2-wire or 3-wire configuration with a 3-wire RTD using 2 inputs. Per maggior informazioni, consulta RTD-DI-16 Central IO Module .