earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: AS-B, AS-P
Functionalities: Hardware
Product version: 3.2, 3.3, 2022, 2023, 2024
10/15/2020

MS/TP Data and Shield Connections

The cable shield drain wire is connected to each MNB device to provide a ground reference to the isolated RS-485 interface in each of the MNB devices. This shield connection on each MNB device is not a local ground connection. The shield drain wire from the MS/TP bus cable must only connect to the specific terminal designated to receive the shield for the MS/TP bus. The terminal label/text reference varies a little in the device documentation between the MNB devices. In all cases, it will be a third screw terminal in a set of three on a terminal block identified for MS/TP communications.

The sequence of MSTP+, MSTP-, and Shield terminals are different from that presented in the generic MNB configuration diagrams. For more information, see MNB Configurations . Be sure to observe the signal name instructions for each of the specific products in their respective installation guides.

Table: Terminal Numbers and References for Different MNB BACnet Devices

MNB Device

Terminal Block Reference

MSTP+ Terminal Number

MSTP- Terminal Number

Shield Terminal Number

Shield Label Reference

MNB-70

TB1

3

2

1

SHLD

MNB-V1 / MNB-V2

TB1

3

2

1

SHLD

MNB-300

P102

1

2

3

SLD

MNB-1000

P103

1

2

3

SLD

Important:

There are two shield connection terminals on the MNB-1000 device. Both are referenced as SLD in the product data. The terminal block identified as P102 (BACnet Network Communications) is the connection serving the MS/TP bus and only the SLD terminal on this terminal block should be used to connect the shield from the MS/TP cable. The other SLD terminal is adjacent on terminal block TB101 and is used only for separate I/O RS-485 Bus. This is also an isolated ground reference connection, but it is a different isolated ground from the MS/TP bus.

  • MNB BACnet Devices
  • MNB Configurations