earth_america
user_standard Anmelden
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Konzept

Konzept


Produkte: AS-C, AS-B, AS-P
Funktionen: Hardware
Produktversion: 1.8, 1.9
10.06.2016

Expanded Unit Load with Network of Isolated Devices Only (Viconics VT/VZ7xxx Devices)

If the network is comprised exclusively of devices with isolated RS-485 interfaces with the only exception being the SmartStruxure server device, it is recommended that the maximum unit load limit can be stretched higher. It is recommended that a maximum load extension should be 16UL (that is, 50% overload) giving a total expanded unit load limit of 48UL. Using a maximum network load of 48UL and subtracting the 24UL for the bias network and SmartStruxure server device leaves 24UL available for the sensors/controllers. With the example device load of 0.62UL each, it is suggested that the isolated bus arrangement could support the full collection of up to 38 sensors.

The extra unit load accommodation is unique to the isolated interface configuration. The configuration is operating with a single non-isolated node (the SmartStruxure server device) which acts as the single point reference for the CMV of the network pair as imposed by the bias arrangement. If this configuration of isolated device nodes is intermixed with any other products that are not isolated, the configuration rules on the network node count must fall back to the limits produced with the standard 32UL maximum total unit load.

If the standard specified unit load limit of 32 is applied, the node count calculation is as follows:

  • Subtracting 24UL from the starting budget of 32 gives a node budget of 8UL.

  • Each of the Viconics sensors presents a RS-485 network load of 0.62UL.

  • The calculated VT7xxx node count that consumes the remainder of the budget is: 8UL / 0.62UL = 12.9 nodes

Hinweis

The recommended limits on RS-485 bus node counts discussed here pertain to hardware bias and unit load considerations only. The recommended maximum node count may be further limited based on product and system version.

  • RS-485 Communications
  • Viconics VT/VZ/SE 7xxx Series Devices