earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: AS-C, AS-B, AS-P
功能: 硬件
产品版本: 1.8, 1.9
2016/6/10

VT/VZ7xxx Configuration 2: Dual End-point Bias (External Supply Source)

Dual end-point bias applies a separate 5 V DC supply at each end of the network to generate the RS-485 bias. Instead of a single pair of 510 ohm resistors, the dual end scheme uses a pair of 1000 ohm resistors at each end. The dual end-point is the best technique for avoiding the drop in the bias voltage over extended cable lengths as you move away from the bias connection location. By applying bias at the two termination points, the arrangement maintains an equal bias across the complete length of the cable.

When using AS-P or AS-B, and the server is positioned near one end of the network cable, you can use the 5 V available on the Bias+ terminal to provide the network bias at the head end of the cable. You use a separate 5 V DC power supply to provide the network bias at the far end of the cable. For Automation Server, you use external 5 V DC power supplies to provide the network bias both at the head end of the cable and at the far end of the cable. The recommended power supplies are discussed separately. 有关更多信息,请参阅 Power Supply Selection for VT/VZ7xxx Configuration 2 .

Connect a 1000 ohm bias resistor from the TX/RX+ terminal (see the figure below) to the 5 V bias supply (connect the resistor to the Bias+ terminal on AS-P or AS-B, or to the positive terminal on the external 5 V DC power supply). Connect another 1000 ohm bias resistor from the TX/RX- terminal to the 5 V bias supply (connect the resistor to the RET terminal on AS-P or AS-B, or to the negative terminal on the external 5 V DC power supply). Connect an external 5 V DC power supply to the MS/TP bus pair through two 1000 ohm bias resistors at the far end of the cable.

Connect a 120 ohm termination resistor across the + and - data lines at the head end of the bus (typically at the SmartStruxure server device). Connect another 120 ohm termination resistor across the + and - data lines on the last node at the far end of the bus.

Connect the shield drain wire to earth ground terminal rail in the control panel with the SmartStruxure server device. This is the only ground connection of the shield for the complete cable segment. Connect the RET/Shield terminal on the SmartStruxure server device to the ground rail in the panel using a 12 AWG (3.31 mm²) to 18 AWG (0.82 mm²) wire.

The shield drain wires are connected together at each device, allowing the shield to continue on past the devices for the full length of the bus.

Use only twisted pair bus cable specified for use with RS-485 (for example, Belden 9841 or equivalent). 有关更多信息,请参阅 Cable Selection .

The example diagram below shows the alternate RS-485 terminal block connections for the different SmartStruxure server device models.

The example diagram below shows the RS-485 Com B connections on Automation Server and AS-P. The guidelines are the same for Com A.

 
action_zoom_plus_stroke VT/VZ7xxx configuration 2 – dual end-point bias (external supply source)
图: VT/VZ7xxx configuration 2 – dual end-point bias (external supply source)

The recommended maximum cable length is 1200 m (4000 ft), if using a 24 AWG (0.20 mm²) or larger cable.

The maximum sensor/node count is 38 (using only the VT/VT7xxx devices). The node count reduces if mixed network with non-isolated devices (such as b3 BACnet devices). Node count discussions and other limiting factors are described separately. 有关更多信息,请参阅 Expanded Unit Load with Network of Isolated Devices Only (Viconics VT/VZ7xxx Devices) .

The recommended location for the bias is at the two extreme ends of the network cable, but the bias voltage remains effective with a 60 m (200 ft) tolerance on the cable length from the end. This configuration supports the preferred termination resistor values of 120 ohm with one positioned at each end of the cable. The unit load imposed by the dual end-point bias is 24UL (12,000 / (1,000 / 2)).

  • Viconics VT/VZ/SE 7xxx Series Devices
  • VT/VZ7xxx Configurations
  • Cable Selection
  • Expanded Unit Load with Network of Isolated Devices Only (Viconics VT/VZ7xxx Devices)
  • Power Supply Selection for VT/VZ7xxx Configuration 2