earth_america
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Концепт

Концепт


Продукты: AS-B, AS-P
Функции: Аппаратное обеспечение
Версия продукта: 3.3, 2022, 2023, 2024, 7.0
23.07.2021

Configuration Selection for Generic RS-485 Network Devices

Use the answers from the worksheet together with these flowcharts to determine the recommended RS-485 bus configuration for your generic RS-485 devices.

Более подробную информацию см. Worksheet for Configuration of RS-485 Bus with Generic RS-485 Devices .

Flowcharts

Use Flowchart 1 below as a starting point for the selection of a recommended configuration.

 
action_zoom_plus_stroke Flowchart 1
Рисунок: Flowchart 1
 
action_zoom_plus_stroke Flowchart 2 – no failsafe receivers and the data rate is 19,200 bps or less
Рисунок: Flowchart 2 – no failsafe receivers and the data rate is 19,200 bps or less
 
action_zoom_plus_stroke Flowchart 3 – no failsafe receivers and the data rate is greater than 19,200 bps
Рисунок: Flowchart 3 – no failsafe receivers and the data rate is greater than 19,200 bps

Generic RS-485 Network Device Configuration 1

This configuration is recommended if the following conditions apply to the RS-485 network devices to be connected to the automation server's RS-485 port:

  • All RS-485 network devices have failsafe receivers.

  • Not all RS-485 network devices have isolated RS-485 interfaces.

Более подробную информацию см. Generic RS-485 Network Device Configuration 1 .

Generic RS-485 Network Device Configuration 2

This configuration is recommended if the following conditions apply to the RS-485 network devices to be connected to the automation server's RS-485 port:

  • All RS-485 network devices have failsafe receivers.

  • All RS-485 network devices have isolated RS-485 interfaces.

Более подробную информацию см. Generic RS-485 Network Device Configuration 2 .

Generic RS-485 Network Device Configuration 3

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • Not all RS-485 network devices have isolated RS-485 interfaces.

  • The maximum data rate required is 19,200 bps or lower.

  • The maximum network cable length required is 150 m (500 ft) or less.

Более подробную информацию см. Generic RS-485 Network Device Configuration 3 .

Generic RS-485 Network Device Configuration 4

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • All RS-485 network devices have isolated RS-485 interfaces.

  • The maximum data rate required is 19,200 bps or lower.

  • The maximum network cable length required is 150 m (500 ft) or less.

Более подробную информацию см. Generic RS-485 Network Device Configuration 4 .

Generic RS-485 Network Device Configuration 5

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • Not all RS-485 network devices have isolated RS-485 interfaces.

  • The maximum data rate required is greater than 19,200 bps.

  • The maximum network cable length required depends on the size of the cable:

    • 150 m (500 ft) or less with 24 AWG (0.20 mm²)

    • 240 m (800 ft) or less with 22 AWG (0.33 mm²)

Более подробную информацию см. Generic RS-485 Network Device Configuration 5 .

Generic RS-485 Network Device Configuration 6

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • All RS-485 network devices have isolated RS-485 interfaces.

  • The maximum data rate required is greater than 19,200 bps.

  • The maximum network cable length required depends on the size of the cable:

    • 150 m (500 ft) or less with 24 AWG (0.20 mm²)

    • 240 m (800 ft) or less with 22 AWG (0.33 mm²)

Более подробную информацию см. Generic RS-485 Network Device Configuration 6 .

Generic RS-485 Network Device Configuration 7

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • Not all RS-485 network devices have isolated RS-485 interfaces.

  • The maximum network cable length required depends on the size of the cable:

    • greater than 150 m (500 ft) with 24 AWG (0.20 mm²)

    • greater than 240 m (800 ft) with 22 AWG (0.33 mm²)

Более подробную информацию см. Generic RS-485 Network Device Configuration 7 .

Generic RS-485 Network Device Configuration 8

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • All RS-485 network devices have isolated RS-485 interfaces.

  • The maximum network cable length required depends on the size of the cable:

    • greater than 150 m (500 ft) with 24 AWG (0.20 mm²)

    • greater than 240 m (800 ft) with 22 AWG (0.33 mm²)

Более подробную информацию см. Generic RS-485 Network Device Configuration 8 .

Power Supply Selection for Generic RS-485 Network Device Configuration 7 and 8

The power required from the 5 V DC supply for the bias circuit is extremely small (approximately 5 mA) so just about any small isolated 5 V DC supply will have more than necessary power rating. A low noise power supply with an output isolated from local ground is recommended to minimize the injection of differential noise onto the bus.

Более подробную информацию см. Power Supply Selection for Generic RS-485 Network Device Configuration 7 and 8 .

  • Generic RS-485 Network Devices
  • Worksheet for Configuration of RS-485 Bus with Generic RS-485 Devices
  • Generic RS-485 Network Device Configuration 1
  • Generic RS-485 Network Device Configuration 2
  • Generic RS-485 Network Device Configuration 3
  • Generic RS-485 Network Device Configuration 4
  • Generic RS-485 Network Device Configuration 5
  • Generic RS-485 Network Device Configuration 6
  • Generic RS-485 Network Device Configuration 7
  • Generic RS-485 Network Device Configuration 8
  • Power Supply Selection for Generic RS-485 Network Device Configuration 7 and 8