0
Concept

Concept


Produits : AS-B, AS-P
Fonctionnalités : Matériel
Version produit : 3.3, 2022, 2023, 2024
07/10/2024

Generic RS-485 Network Device Configuration 5

This configuration is recommended if the following conditions apply to the RS-485 network and the devices to be connected to the automation server's RS-485 port:

  • Not all RS-485 network devices have failsafe receivers.

  • Not all RS-485 network devices have isolated RS-485 interfaces.

  • The maximum data rate required is greater than 19,200 bps.

  • The maximum network cable length required depends on the size of the cable:

    • 150 m (500 ft) or less with 24 AWG (0.20 mm²)

    • 240 m (800 ft) or less with 22 AWG (0.33 mm²)

The third condition indicates that network termination is needed. The first condition indicates the termination will cause a need for strong bias.

A strong external resistor bias (low resistance pull-up and pull-down) is required to create a minimum +200 mV level (plus noise margin) across the data+ and data- conductors for the full length of the bus when the network is idle (in between all packets). The low resistance bias is needed to overcome the voltage drop created by the wire resistance and current pulled by the termination resistors. This is referenced as failsafe bias and is required because the transceiver is of the earlier type with no integrated failsafe receiver function.

With the first and third conditions defined, there are two bias configuration options to choose from. The choice relates to simplicity of the arrangement and the maximum cable length needed (the fourth condition). This configuration uses single end-point biasing. Dual end-point biasing is required to support cable lengths up to 1200 m (4000 ft). Pour plus d'informations, voir Generic RS-485 Network Device Configuration 7 .

This configuration uses the bias supply output from the automation server to generate bias on the bus from the single location where the automation server is located (typically at the head end of the bus). AS-P servers and AS-B servers provide a 5 V bias voltage supply, which supports 120 ohm termination resistors at the two ends of the bus.

Connect a 510 ohm bias resistor from the TX/RX+ terminal to the Bias+ terminal on the automatin server (see the figure below). Connect another 510 ohm bias resistor from the TX/RX- terminal to the RET terminal on the automation server.

Connect a 120 ohm termination resistor across the + and - data lines at the head end of the bus (typically at the automation server). Connect another termination resistor across the + and - data lines on the last node at the far end of the bus.

Connect the shield drain wire to earth ground terminal rail in the panel with the automation server. This is the only ground connection of the shield for the complete cable segment. Connect the RET terminal on the automation server to the ground rail in the panel using a 12 AWG (3.31 mm²) to 18 AWG (0.82 mm²) wire.

If the network has a mix of isolated and non-isolated devices, the shield terminal or communications ground terminal of the isolated devices should be connected to the shield. Refer to the device specific instructions.

The shield drain wires are connected together at each device, allowing the shield to continue on past the devices for the full length of the bus.

The example diagram below shows the alternate RS-485 terminal block connections for the different automation server models.

The example diagram below shows the RS-485 Com B connections on the AS-P and AS-B servers. The guidelines are the same for Com A. When failsafe bias resistors are required on the Com A network, the pull-up voltage is obtained from the Bias+ terminal.

 
action_zoom_plus_stroke Generic RS-485 network device configuration 5 – terminated bus, single end-point 510 ohm bias, non-isolated interfaces
Figure : Generic RS-485 network device configuration 5 – terminated bus, single end-point 510 ohm bias, non-isolated interfaces

The addition of termination resistors to a network requiring failsafe bias resistors creates a continuous current flow through the network in the idle condition. The result is a voltage divider network where the termination resistors create a voltage drop in the bias resistors and network wire. The bus biasing from the single point presents cable length limitations based on wire size as seen in the following table. This table indicates the wire lengths where the starting (head end) bias voltage created by the 510 ohm resistors has dropped to the minimum bias voltage level due to the wire resistance.

Table : Recommended Maximum Cable Lengths and Associated Wire Sizes

Maximum Length

Wire Size

150 m (500 ft)

24 AWG (0.20 mm²)

240 m (800 ft)

22 AWG (0.33 mm²)

The recommended node count for the configuration shown in the figure above is determined using the following process.

The unit load rating of the individual network devices along with the remaining available unit load budget will determine the recommended maximum number of nodes you should install on this copper segment. The total unit load budget specified in the RS-485 standard for all components connected to a bus segment (communicating devices and bias resistors) is 32UL.

We must determine the UL node budget available after subtracting the load imposed by the bias resistors and the automation server. The single end-point bias configuration presents a unit load of 23.5UL (12,000 / 510 = 23.5). The automation server adds 0.5UL.

For a bus with non-isolated interfaces, the remaining node budget is: 32 - 23.5 - 0.5 = 8UL

We must divide our node budget by the device load value to determine node count. For the network device load, select the higher unit load value between answers Q5 and Q6b. Pour plus d'informations, voir Worksheet for Configuration of RS-485 Bus with Generic RS-485 Devices . Divide the node budget value by the device UL value (Q5 or Q6b, whichever is greater). The result is the maximum recommended node count in regards to bus loading.

Example: If the answer to Q5 was 0.25 and the answer to Q6b was 0.32, use the value 0.32.

For a network with any non-isolated devices, the maximum node count is: 8 / 0.32 = 25 nodes