earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos AO-8, AO-V-8, DI-16, DO-FA-12, DO-FC-8, AS-P, PS-24 V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Funcionalidades: Hardware
Versión del producto: 3.2
16/08/2022

SmartX AS-P Servers

arrow1_rotationElectronics Modules arrow1_rotationTerminal Bases arrow1_rotationMemory arrow1_rotationSupported Building Standards arrow1_rotationSmartX AS-P Server Communication Ports arrow1_rotationSmartX AS-P Server Screw Terminals arrow1_rotationSmartX AS-P Server LEDs arrow1_rotationReset Functions arrow1_rotationCommunication Port Wiring arrow1_rotationSmartX AS-P Server Software arrow1_rotationSmartX Server Replacement Using Restore arrow1_rotationEspecificaciones arrow1_rotationInternal Configuration

The SmartX AS-P server offers enhanced processor performance, increased memory size, dual Ethernet ports, and high-speed USB interfaces. The SmartX AS-P server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The SmartX server controls and supervises equipment, typically HVAC equipment. SmartX AS-P servers use I/O modules with connected field devices, such as sensors and actuators, to do that.

SmartX AS-P servers are based on the patented two-piece design. Each SmartX AS-P server consists of an electronics module and a terminal base.

The SmartX AS-P server is installed with the I/O modules on DIN rails in cabinets. The SmartX AS-P server electronics module uses a W1 enclosure. Power is supplied through the terminal base backplane.

 
action_zoom_plus_stroke SmartX AS-P server
Figura: SmartX AS-P server

Electronics Modules

The electronics module is the main component of SmartX devices that are based on the patented two-piece design. The electronics module is installed on a terminal base, which constitutes the second component of the device.

Para obtener más información, consulte Electronics Modules .

Terminal Bases

The terminal bases are used for SmartX devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SmartX device installed to the right (next terminal base in the chain).

Para obtener más información, consulte Terminal Bases .

Memory

A SmartX AS-P server has two types of memory:

  • 512 MB DDR3 SDRAM (for program execution)

  • 4 GB eMMC memory (for storage)

If a power outage occurs, all important variables are automatically saved to the eMMC memory before complete shutdown. When power returns, this data retention function helps ensure that the SmartX AS-P server can continue to run with the correct set of values.

Supported Building Standards

The SmartX AS-P server natively communicates with three of the most popular communication protocols:

  • BACnet: The SmartX AS-P server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to MP Series controllers, b3 BACnet devices, and BACnet devices.

  • LonWorks: The SmartX AS-P server has a built-in FTT-10 port, which enables access to Xenta devices and LonWorks devices.

  • Modbus: The SmartX AS-P server natively integrates Modbus RS-485 master and slave configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.

Aviso

The SmartX AS-P server model AS-P-NL does not support LonWorks.

SmartX AS-P Server Communication Ports

A SmartX AS-P server has the following communication ports:

  • 2 Ethernet 10/100 megabit ports

  • 2 RS-485 ports

  • 2 LonWorks (TP/FT and RS-485) ports (not available on AS-P-NL model)

  • 1 USB host port

  • 1 USB device port

  • 1 backplane I/O bus port

Para obtener más información, consulte SmartX AS-P Server Communication Ports .

SmartX AS-P Server Screw Terminals

There are pluggable screw terminals at the top of a SmartX AS-P server.

Para obtener más información, consulte SmartX AS-P Server Screw Terminals .

SmartX AS-P Server LEDs

There are several LEDs on the front panel of a SmartX AS-P server.

Para obtener más información, consulte SmartX AS-P Server LEDs .

Reset Functions

There are four different types of reset for the SmartX servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the SmartX server can be reset using the reset button or a command from WorkStation.

Para obtener más información, consulte SmartX Server Reset Functions .

Communication Port Wiring

The wiring recommendations for the communication ports on the SmartX servers and SmartX IP Controller devices apply to wires and cables used for RS-485 communications, LonWorks communications, USB connections, Ethernet connections, and Sensor Bus connections. Always use the recommended cables and wires.

Para obtener más información, consulte Communication Port Wiring .

SmartX AS-P Server Software

Before you engineer a SmartX AS-P server, install the SmartX AS-P server software on the server using Device Administrator. The software is not pre-loaded on the SmartX AS-P servers.

Para obtener más información, consulte Installing SmartX AS-P or SmartX AS-B Software .

SmartX Server Replacement Using Restore

Backup and Restore helps assure that SmartX server data can be restored to a replacement SmartX server in the event of detected failure, or to the same SmartX server in the event of data loss. As a precaution, you back up your SmartX servers regularly so that you can use the most current backup to restore the SmartX server data to a replacement SmartX server. You also configure the new SmartX server to match the name and the network settings of the replaced SmartX server so the system can identify this SmartX server when online.

Para obtener más información, consulte SmartX Server Replacement Using Restore .

Especificaciones

Electrical
DC input supply power
10 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.321 kg (0.71 lb)
Weight excluding terminal base
0.245 kg (0.54 lb)
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
Dual 2-wire ports, bias 5.0 VDC
LonWorks a
TP/FT-10
a) SmartX Controller – AS-P-NL (SXWASPXXX10002) does not support LonWorks.
Communications
BACnet
BACnet/IP and MS/TP, port configurable, default 47808
  
BTL B-BC (BACnet Building Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
Modbus
Modbus TCP, client and server
  
Serial, RS-485, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.2, 1.1, and 1.0, port configurable default 443
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
LNS
LNS version
OpenLNS
  
Installed on WorkStation PC
LonMark
Resource files version
14.00
CPU
Frequency
500 MHz
Type
SPEAr1380, ARM Cortex-A9 dual-core
DDR3 SDRAM
512 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance

Internal Configuration

All serial communication ports of the SmartX AS-P server module refer to signal ground as shown in the figure below.

 
action_zoom_plus_stroke SmartX AS-P server internal configuration
Figura: SmartX AS-P server internal configuration
Aviso

The SmartX AS-P server model AS-P-NL does not have LonWorks (LON) communication ports.

The I/O bus in the terminal base provides the SmartX AS-P server module with power and an address.

The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the I/O module and the SmartX server.

  • Hardware Overview
  • Electronics Modules
  • Terminal Bases
  • SmartX AS-P Server Communication Ports
  • SmartX AS-P Server Screw Terminals
  • SmartX AS-P Server LEDs
  • SmartX Server Reset Functions
  • Communication Port Wiring
  • Installing SmartX AS-P or SmartX AS-B Software
  • SmartX Server Replacement Using Restore