Prodotti: AS-P Smoke Control, Automation Server Smoke Control
Funzionalità: Smoke Control
Versione del prodotto: 1.8
26/09/2016

Transformers

The following transformers are approved for the SmartStruxure Solution Smoke Control System.

EMSC-541

The specifications for EMSC-541 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 50 VA

  • Frequency- 50/60 Hz

  • Circuit protection: Fused (non-replaceable) Primary Has a self-contained enclosure

  • Class 2

EMSC-542

The specifications for EMSC-542 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 100 VA

  • Frequency- 50/60 Hz

  • Circuit protection: Fused (non-replaceable) Primary Has a self-contained enclosure

  • Class 2

EMSC-543

The specifications for EMSC-543 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 240 VA

  • Frequency- 60 Hz

  • Circuit protection- Fused (non-replaceable) Primary

  • Must be installed in a UL Listed Enclosure

EMSC-583

The specifications for EMSC-583 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 75 VA

  • Frequency- 50/60 Hz

  • Class 2

  • Must be installed in a UL Listed Enclosure

EMSC-616

The specifications for EMSC-616 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 75 VA

  • Frequency- 50/60 Hz

  • Circuit protection: Foot Mount Single Hub UL-Listed with Circuit Breaker

  • Class 2

  • Must be installed in a UL Listed Enclosure

EMSC-618

The specifications for the EMSC-618 are as follows:

  • Input- 120 V

  • Output- 24 V

  • Power- 96 VA

  • Frequency- 50/60 Hz

  • Circuit protection: Foot Mount Single Hub UL-Listed with Circuit Breaker

  • Class 2

  • Must be installed in a UL Listed Enclosure

LE10500
024-024-040-TF

The specifications for LE10500 024-024-040-TF are as follows:

  • Input- 24 VAC

  • Output- 24 VAC

  • Power- 40 VA

  • Frequency- 50/60 Hz

  • Circuit protection: Internally Protected

  • Class 2

  • Has a self-contained enclosure

01-2100-040-TF

The specification for 01-2100-323 are as follows:

  • Input- 120 VAC

  • Output- 24 Volts

  • Power- 40 VA

  • Frequency- 60 Hz

  • Must be installed in a UL Listed Enclosure

  • Class 2

  • Smoke Control Enclosures and Requirements
  • SmartStruxure Solution Hardware Overview
  • Smoke Control System Restrictions