earth_america
user_standard Zaloguj się
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Pojęcie

Pojęcie


Produkty: AO-8, AO-V-8, AS-P Smoke Control, Automation Server Smoke Control, DI-16, DO-FA-12, DO-FC-8, PS-24V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Funkcje: Smoke Control
Wersja produktu: 2022
2025-01-09

Power Rating

Using the power rating for each of the modules (listed in the following table), accumulate the power consumed by the Smoke Control Server and Central IO modules. The PS-24V can supply up to 30W (~1.25A at 24 VDC). The 24 VDC from the PS-24V is delivered to all modules connecting on the bus on the right side of the PS-24V up to the next power supply module. You must add another PS-24V on the I/O bus to keep the load on the previous power supply at 30W or below.

Tabela: Power Budget Table

Device

Power (W)

AS-P or AS-P-NLS

10.0

Automation Server

7.0

AO-8

4.9

AO-8-H

4.9

AO-V-8

0.7

AO-V-8-H

0.7

DI-16

1.6

DO-FA-12

1.8

DO-FA-12-H

1.8

DO-FC-8

2.2

DO-FC-8-H

2.2

RTD-DI-16

1.6

UI-16

1.8

UI-8/DO-FC-4

1.9

UI-8/DO-FC-4-H

1.9

UI-8/AO-4

3.2

UI-8/AO-4-H

3.2

UI-8/AO-V-4

1.0

UI-8/AO-V-4-H

1.0

  • EcoStruxure BMS Module Installation
  • Terminal Base Installation
  • Terminal Base Wiring
  • Electronics Module Installation
  • PS-24V Power Supply Module
  • Automation Server Installation
  • AS-P and AS-P-NLS Installation
  • RS-485 Field Bus Cable Routing
  • Module and MP Controller Status LEDs
  • Central IO Module Installation