SmartX IP Controller – MP-C is a multi-purpose, fully programmable, IP based field controller. The MP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. MP-C can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with a SmartX AS-P or AS-B server or an Enterprise Server as the parent server. The MP-C models support an optional display that provides insight and control of the inputs and outputs.
The MP-C has the following features:
IP enabled with dual-port Ethernet switch
Versatile onboard I/O point mix
Highly available
Sensor bus for living space sensors
Mobile commissioning application
Full EcoStruxure Building Operation software support, providing efficient engineering tools
For information on the reduced features, functions, and specifications of the Smoke Control (SMK) models approved for use in UL 864 systems, see the EcoStruxure Building Management - Smoke Control System Design Guide, 04-16014-XX-en.
The MP Series controllers are based on open protocols that simplify interoperability, IP configuration, and device management:
IP addressing
BACnet/IP communications
DHCP for easy network configuration
The MP Series controllers have a dual-port Ethernet switch, which enables flexible network topologies:
Star
Daisy chain
Rapid Spanning Tree Protocol (RSTP) ring
In a star topology, the controller and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple controllers together to reduce installation time and cost. Use an RSTP ring topology when you want a non-operational controller to be detected and recovered quickly and efficiently.
MP-C comes in five models with different I/O point count and a versatile mix of I/O point types that match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.
I/O Point Types |
MP-C-15A |
MP-C-18A |
MP-C-18B |
MP-C-24A |
MP-C-36A |
Universal I/O Type Ub |
8 |
10 |
10 |
16 |
20 |
Universal I/O Type Uc |
- |
- |
- |
4 |
8 |
Triac outputs |
6 |
4 |
8 |
- |
- |
Relay outputs Form A |
- |
3 |
- |
4 |
8 |
High power relay outputs Form A |
1 |
1 |
- |
- |
- |
Configurations |
Universal I/O Type Ub |
Universal I/O Type Uc |
Triac Outputs |
Relay Outputs Form A |
High Power Relay Outputs Form A |
Digital inputs |
yes |
yes |
- |
- |
- |
Counter inputs |
yes |
yes |
- |
- |
- |
Supervised inputs |
yes |
yes |
- |
- |
- |
Voltage inputs (0 to 10 VDC) |
yes |
yes |
- |
- |
- |
Current inputs (0 to 20 mA) |
yes |
yes |
- |
- |
- |
Temperature inputs |
yes |
yes |
- |
- |
- |
Resistive inputs |
yes |
yes |
- |
- |
- |
2-wire RTD temperature inputs |
yes |
yes |
- |
- |
- |
Voltage outputs (0 to 10 VDC) |
yes |
yes |
- |
- |
- |
Current outputs (0 to 20 mA) |
- |
yes |
- |
- |
- |
Digital outputs |
- |
- |
yes |
yes |
yes |
Digital pulsed outputs |
- |
- |
yes |
yes |
yes |
PWM outputs |
- |
- |
yes |
yes |
yes |
Tristate outputs |
- |
- |
yes |
yes |
- |
Tristate pulsed outputs |
- |
- |
yes |
yes |
- |
The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.
As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.
For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.
The universal inputs/outputs can also be used as voltage outputs or current outputs (Uc only), without the need for external bias resistors. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.
The triac outputs can be used in many applications to switch 24 VAC on or off for external loads such as actuators, relays, or indicators. The triac outputs are isolated from the controller. Triacs are silent and are not adversely affected by relay contact wear.
The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.
MP-C-15A and MP-C-18A have a high power relay output, which is ideal for switching loads of up to 12 A, such as electrical heating elements.
For applications that require more I/O resources, the SmartX IP Controller – IP-IO modules provide a versatile mix of I/O points for any application. For more information, see the SmartX IP Controller – IP-IO Specification Sheet.
The MP Series controllers support local trends, schedules, and alarms, enabling local operation when the controller is offline or used in standalone applications.
With user-defined fallback values, the IP-IO outputs will be in a predictable state in cases of network disruption.
The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.
All MP-C models can be equipped with the MP-C Display add-on module, which features an LCD display and five keys. With this module, you can manually override analog and digital outputs for testing, commissioning, and maintenance of equipment connected to the outputs. The module's dedicated processing power ensures reliable override for maintenance applications. The override status can be viewed in EcoStruxure Building Operation WorkStation and WebStation, enabling precise monitoring and reliable control.
In WorkStation, you update the firmware of multiple MP Series controllers at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the controllers and sensors. The server can host controllers of different firmware versions.
The MP Series controllers provide an interface designed for the SmartX Sensor family of living space sensors. The SmartX Sensors offer an efficient way to sense the temperature, humidity, CO 2 , and occupancy in a room. The SmartX Sensors are available with different combinations of sensor types and various covers and user interface options, such as touchscreen, setpoint and override buttons, and blank covers.
The sensor bus provides both power and communications for up to four sensors that are daisy-chained using standard Cat 5 (or higher) cables. The maximum number of sensors that can be connected to a controller varies depending on the sensor model and the combination of cover and sensor base type:
Blank covers: Up to four sensors of any combination of sensor base types
3-button and touchscreen covers:
Up to two sensor bases with CO 2 option
Up to four sensor bases without CO 2 option
SmartX LCD temperature sensors: Up to four sensors are supported
The maximum total length of the sensor bus is 61 m (200 ft). For more information, see the SmartX Living Space Sensors Specification Sheet.
The eCommission SmartX Controllers mobile application is designed for local configuration, field deployment, and commissioning of MP Series controllers. The mobile application reduces the commissioning time, allows flexibility in project execution, and minimizes dependencies on network infrastructure.
The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 devices. For more information, see the eCommission SmartX Controllers Specification Sheet.
Using the eCommission SmartX Controllers mobile application, you can connect to one or many SmartX IP controllers. You can connect to a single SmartX IP controller using the eCommission Bluetooth Adapter connected to a SmartX Sensor. Using a wireless access point or a network switch, you can connect to a network of SmartX IP controllers on the local IP network.
With the eCommission SmartX Controllers mobile application, you can easily discover MP Series controllers on the IP network. You can change the configuration of each controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for controllers of the same model.
The eCommission SmartX Controllers mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the controller application directly into the local SmartX IP controller and deploy the controller. The controller application can be created offline using Project Configuration Tool or WorkStation. You can also perform an I/O checkout to verify that the controller's I/O points are configured, wired, and operating correctly.
The power of the SmartX IP controller is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:
WorkStation/WebStation interface
Script and Function Block programming options
Device discovery
Engineering efficiency
WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the MP Series controller and its I/O as well as its attached SmartX Sensors. For more information, see the WorkStation and WebStation specification sheets.
Unique to the industry, the SmartX IP controllers have both Script and Function Block programming options. This flexibility assures that the best programming method can be selected for the application. Existing programs can easily be reused between the EcoStruxure BMS server and the controller.
The enhanced Device Discovery in WorkStation enables you to easily identify MP Series controllers on a BACnet network and to associate the controllers with their parent server.
The engineering and maintenance of MP Series controllers can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete controller application that contains programs and all necessary objects such as trends, alarms, and schedules. The controller application in the Custom Types library is reusable across all controllers of the same model. You can use the controller application as a base for creating new controllers intended for similar applications. You can then edit the controller application, and the changes are automatically replicated to all controllers, while each controller keeps its local values.
WorkStation supports both online and offline engineering of MP Series controllers. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the controllers later.
Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the MP Series controllers, before you deploy your server and controller applications to the servers and controllers on site. For more information, see the Project Configuration Tool specification sheet.
In addition, you can use Automated Engineering Tool to facilitate your engineering process when using MP Series controllers. This tool provides access to a library of standard controller applications that can be quickly configured and customized using the wizards and mass edit functions provided in the tool. You can then load these customized applications into your target server. The tool also enables the quick creation of your own templates based on MP Series controller applications that you have developed. These templates facilitate a standard approach and easy reuse and duplication of common controller applications. For more information, see the Automated Engineering Tool specification sheet.
Product |
Part number |
MP-C-15A
|
SXWMPC15A10001
|
MP-C-18A
|
SXWMPC18A10001
|
MP-C-18B
|
SXWMPC18B10001
|
MP-C-24A
|
SXWMPC24A10001
|
MP-C-36A
|
SXWMPC36A10001
|
MP-C DISPLAY (MP-C override display module) |
SXWMPCDSP10001
|
Spare terminal blocks for all MP-C models (4 x 3-pin, 1 x 4-pin, 7 x 6-pin, 2 x 8-pin terminal blocks) |
SXWMPCCON10001
|
DIN-RAIL-CLIP, DIN-rail end clip package of 25 pieces |
SXWDINEND10001
|
eCommission Bluetooth Adapter
|
SXWBTAECXX10001
|
Product |
Part Number |
MP-C-15A-SMK
|
SXWMPC15A1S001
|
MP-C-18A-SMK
|
SXWMPC18A1S001
|
MP-C-18B-SMK
|
SXWMPC18B1S001
|
MP-C-24A-SMK
|
SXWMPC24A1S001
|
MP-C-36A-SMK
|
SXWMPC36A1S001
|
For more information on part numbers for Network Connectivity Accessories, see section “SmartX IP Controllers – Accessories” in the For more information, see Product Selection Guide - EcoStruxure Building ..
AC input | |||||||||||||
For specifications and information on the restrictions that apply to the Smoke Control (SMK) models, see the EcoStruxure Building Management - Smoke Control System Design Guide, 04-16014-XX-en. | |||||||||||||
Nominal voltage
|
24 VAC
|
||||||||||||
Operating voltage range
|
+/-20 %
|
||||||||||||
Frequency
|
50/60 Hz
|
||||||||||||
Maximum power consumption (MP-C-15A, -18A, -18B)
|
22 VA
|
||||||||||||
Maximum power consumption (MP-C-24A)
|
28 VA
|
||||||||||||
Maximum power consumption (MP-C-36A)
|
33 VA
|
||||||||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||||||||
DC input | |||||||||||||
Nominal voltage
|
24 to 30 VDC
|
||||||||||||
Operating voltage range
|
21 to 33 VDC
|
||||||||||||
Maximum power consumption (MP-C-15A, -18A, -18B)
|
12 W
|
||||||||||||
Maximum power consumption (MP-C-24A)
|
15 W
|
||||||||||||
Maximum power consumption (MP-C-36A)
|
18 W
|
||||||||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||||||||
Environment | |||||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F) at normal operation
a
|
||||||||||||
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
a
|
|||||||||||||
a) MP-C Display has an operating temperature range of -30 to +60 °C (-22 to +140 °F). | |||||||||||||
Ambient temperature, storage
|
-40 to +70 °C (-40 to +158 °F)
|
||||||||||||
Maximum humidity
|
95 % RH non-condensing
|
||||||||||||
Material | |||||||||||||
Plastic flame rating
|
UL94-5V
|
||||||||||||
Ingress protection rating
|
IP 20
|
||||||||||||
Mechanical | |||||||||||||
Dimensions (MP-C-15A, -18A, -18B)
|
153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)
|
||||||||||||
|
|||||||||||||
Dimensions (MP-C-24A, -36A)
|
234 W x 110 H x 64 D mm (9.2 W x 4.3 H x 2.5 D in.)
|
||||||||||||
|
|||||||||||||
Weight, MP-C-15A | |||||||||||||
Including terminal blocks | 0.358 kg (0.789 lb)
|
||||||||||||
Weight, MP-C-18A | |||||||||||||
Including terminal blocks | 0.371 kg (0.818 lb)
|
||||||||||||
Weight, MP-C-18B | |||||||||||||
Including terminal blocks | 0.361 kg (0.796 lb)
|
||||||||||||
Weight, MP-C-24A | |||||||||||||
Including terminal blocks | 0.495 kg (1.091 lb)
|
||||||||||||
Weight, MP-C-36A | |||||||||||||
Including terminal blocks | 0.547 kg (1.206 lb)
|
||||||||||||
Installation
|
DIN rail or other flat surface inside a cabinet
|
||||||||||||
Terminal blocks
|
Removable
|
||||||||||||
Software compatibility | |||||||||||||
EcoStruxure Building Operation software
|
version 2.0 or later
|
||||||||||||
Agency compliances | |||||||||||||
Emission
|
RCM; EN 61000-6-3; EN 50491-5-2; FCC Part 15, Sub-part B, Class B
|
||||||||||||
Immunity
|
EN 61000-6-2; EN 50491-5-3
|
||||||||||||
Safety standards
|
EN 60730-1; EN 60730-2-11; EN 50491-3; UL 916 C-UL US Listed
|
||||||||||||
Smoke control product safety
a, b
|
UL 864
|
||||||||||||
a) Applies to the MP-C SMK models: MP-C-15A-SMK, MP-C-18A-SMK, MP-C-18B-SMK, MP-C-24A-SMK, and MP-C-36A-SMK. | |||||||||||||
b) The MP-C SMK models are shipped with a validated UL 864 software version, which can differ from the latest released software. For more information, see EcoStruxure Building Management - Smoke Control System Design Guide, 04-16014-XX-en. | |||||||||||||
Real-time clock | |||||||||||||
Accuracy, at 25 °C (77 °F)
|
+/-1 minute per month
|
||||||||||||
Backup time, at 25 °C (77 °F)
|
7 days minimum
|
||||||||||||
Communication ports | |||||||||||||
Ethernet
|
Dual 10/100BASE-TX (RJ45)
|
||||||||||||
USB
|
1 USB 2.0 device port (mini-B)
|
||||||||||||
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
|
|||||||||||||
Sensor bus
|
24 VDC, 2 W, RS-485 (RJ45)
|
||||||||||||
Sensor bus protection
|
Transient voltage suppressors on communication and power signals
|
||||||||||||
Communications | |||||||||||||
BACnet
|
BACnet/IP, port configurable, default 47808
|
||||||||||||
BTL B-AAC (BACnet Advanced Application Controller)
a
|
|||||||||||||
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page. | |||||||||||||
CPU | |||||||||||||
Frequency
|
500 MHz
|
||||||||||||
Type
|
ARM Cortex-A7 dual-core
|
||||||||||||
DDR3 SDRAM
|
128 MB
|
||||||||||||
NOR flash memory
|
32 MB
|
||||||||||||
Memory backup
|
128 kB, FRAM, non-volatile
|
||||||||||||
MP-C Display (Optional) | |||||||||||||
Removable
|
No
|
||||||||||||
Dimensions
|
74 W x 46 H x 24 D mm (2.9 W x 1.8 H x 0.9 D in.)
|
||||||||||||
|
|||||||||||||
Display size
|
36 W x 17 H mm (1.4 W x 0.7 H in.)
|
||||||||||||
Display resolution
|
128 x 64 pixels
|
||||||||||||
Display type
|
FSTN monochrome LCD, white color transflective backlight
|
||||||||||||
Power consumption
|
max. 0.15 W (45 mA at 3.3 V)
|
||||||||||||
Ambient temperature, operating
|
-30 to +60 °C (-22 to +140 °F)
|
||||||||||||
Ambient temperature, storage
|
-40 to +70 °C (-40 to +158 °F)
|
||||||||||||
Maximum humidity
|
95 % RH non-condensing
|
||||||||||||
Weight
|
0.035 kg (0.077 lb)
|
||||||||||||
Compliance with standards
|
EN ISO 16484-2
|
||||||||||||
Universal inputs/outputs, Ub and Uc | |||||||||||||
Channels, MP-C-15A
|
8 Ub, Ub1 to Ub8
|
||||||||||||
Channels, MP-C-18A
|
10 Ub, Ub1 to Ub10
|
||||||||||||
Channels, MP-C-18B
|
10 Ub, Ub1 to Ub10
|
||||||||||||
Channels, MP-C-24A
|
16 Ub, Ub1 to Ub16
|
||||||||||||
4 Uc, Uc1 to Uc4
|
|||||||||||||
Channels, MP-C-36A
|
20 Ub, Ub1 to Ub20
|
||||||||||||
8 Uc, Uc1 to Uc8
|
|||||||||||||
Absolute maximum ratings
|
-0.5 to +24 VDC
|
||||||||||||
A/D converter resolution
|
16 bits
|
||||||||||||
Universal input/output protection
|
Transient voltage suppressor on each universal input/output
|
||||||||||||
Digital inputs | |||||||||||||
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
||||||||||||
Minimum pulse width
|
150 ms
|
||||||||||||
Counter inputs | |||||||||||||
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
||||||||||||
Minimum pulse width
|
20 ms
|
||||||||||||
Maximum frequency
|
25 Hz
|
||||||||||||
Supervised inputs | |||||||||||||
5 V circuit, 1 or 2 resistors | |||||||||||||
Monitored switch combinations | Series only, parallel only, and series and parallel
|
||||||||||||
Resistor range
|
1 to 10 kohm
|
||||||||||||
For a 2-resistor configuration, each resistor must have the same value +/- 5 % | |||||||||||||
Voltage inputs | |||||||||||||
Range
|
0 to 10 VDC
|
||||||||||||
Accuracy
|
+/-(7 mV + 0.2 % of reading)
|
||||||||||||
Resolution
|
1.0 mV
|
||||||||||||
Impedance
|
100 kohm
|
||||||||||||
Current inputs | |||||||||||||
Range
|
0 to 20 mA
|
||||||||||||
Accuracy
|
+/-(0.01 mA + 0.4 % of reading)
|
||||||||||||
Resolution
|
1 μA
|
||||||||||||
Impedance
|
47 ohm
|
||||||||||||
Resistive inputs | |||||||||||||
10 ohm to 10 kohm accuracy
|
+/-(7 + 4 x 10
-3
x R) ohm
|
||||||||||||
R = Resistance in ohm | |||||||||||||
10 kohm to 60 kohm accuracy
|
+/-(4 x 10
-3
x R + 7 x 10
-8
x R
2
) ohm
|
||||||||||||
R = Resistance in ohm | |||||||||||||
Temperature inputs (thermistors) | |||||||||||||
Range
|
-50 to +150 °C (-58 to +302 °F)
|
||||||||||||
Supported thermistors | |||||||||||||
Honeywell
|
20 kohm
|
||||||||||||
Type I (Continuum)
|
10 kohm
|
||||||||||||
Type II (I/NET)
|
10 kohm
|
||||||||||||
Type III (Satchwell)
|
10 kohm
|
||||||||||||
Type IV (FD)
|
10 kohm
|
||||||||||||
Type V (FD w/ 11k shunt)
|
Linearized 10 kohm
|
||||||||||||
Satchwell D?T
|
Linearized 10 kohm
|
||||||||||||
Johnson Controls
|
2.2 kohm
|
||||||||||||
Xenta
|
1.8 kohm
|
||||||||||||
Balco
|
1 kohm
|
||||||||||||
Measurement accuracy | |||||||||||||
20 kohm
|
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
|
||||||||||||
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
|
|||||||||||||
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
|
|||||||||||||
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
|
|||||||||||||
10 kohm, 2.2 kohm, and 1.8 kohm
|
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
|
||||||||||||
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
|
|||||||||||||
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
|
|||||||||||||
Linearized 10 kohm
|
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
|
||||||||||||
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
|
|||||||||||||
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
|
|||||||||||||
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
|
|||||||||||||
1 kohm
|
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
|
||||||||||||
RTD temperature inputs | |||||||||||||
Supported RTDs
|
Pt1000
|
||||||||||||
Pt1000 | |||||||||||||
Sensor range
|
-50 to +150 °C (-58 to +302 °F)
|
||||||||||||
|
|||||||||||||
RTD temperature wiring | |||||||||||||
Maximum wire resistance
|
20 ohm/wire (40 ohm total)
|
||||||||||||
Maximum wire capacitance
|
60 nF
|
||||||||||||
The wire resistance and capacitance typically corresponds to a 200 m wire. | |||||||||||||
Voltage outputs | |||||||||||||
Range
|
0 to 10 VDC
|
||||||||||||
Accuracy
|
+/-60 mV
|
||||||||||||
Resolution
|
10 mV
|
||||||||||||
Minimum load resistance
|
5 kohm
|
||||||||||||
Load range
|
-1 to +2 mA
|
||||||||||||
Current outputs (Uc only) | |||||||||||||
Range
|
0 to 20 mA
|
||||||||||||
Accuracy
|
+/-0.2 mA
|
||||||||||||
Resolution
|
21 µA
|
||||||||||||
Load range
|
0 to 650 ohm
|
||||||||||||
Relay outputs, DO | |||||||||||||
Channels, MP-C-15A
|
0
|
||||||||||||
Channels, MP-C-18A
|
3, DO5 to DO7
|
||||||||||||
Channels, MP-C-18B
|
0
|
||||||||||||
Channels, MP-C-24A
|
4, DO1 to DO4
|
||||||||||||
Channels, MP-C-36A
|
8, DO1 to DO8
|
||||||||||||
Contact rating
|
250 VAC/30 VDC, 2 A, Pilot Duty (C300)
|
||||||||||||
Switch type
|
Form A Relay
|
||||||||||||
Single Pole Single Throw
|
|||||||||||||
Normally Open
|
|||||||||||||
Isolation contact to system ground
|
3000 VAC
|
||||||||||||
Cycle life (Resistive load)
|
At least 100,000 cycles
|
||||||||||||
Minimum pulse width
|
100 ms
|
||||||||||||
High power relay outputs, DO | |||||||||||||
Channels, MP-C-15A
|
1, DO7
|
||||||||||||
Channels, MP-C-18A
|
1, DO8
|
||||||||||||
Channels, MP-C-18B
|
0
|
||||||||||||
Channels, MP-C-24A
|
0
|
||||||||||||
Channels, MP-C-36A
|
0
|
||||||||||||
Contact rating
|
250 VAC/24 VDC, 12 A, Pilot Duty (B300)
|
||||||||||||
Switch type
|
Form A Relay
|
||||||||||||
Single Pole Single Throw
|
|||||||||||||
Normally Open
|
|||||||||||||
Isolation contact to system ground
|
5000 VAC
|
||||||||||||
Cycle life (Resistive load)
|
At least 100,000 cycles
|
||||||||||||
Minimum pulse width
|
100 ms
|
||||||||||||
Triac outputs, DO | |||||||||||||
Channels, MP-C-15A
|
6, DO1 to DO6
|
||||||||||||
Channels, MP-C-18A
|
4, DO1 to DO4
|
||||||||||||
Channels, MP-C-18B
|
8, DO1 to DO8
|
||||||||||||
Channels, MP-C-24A
|
0
|
||||||||||||
Channels, MP-C-36A
|
0
|
||||||||||||
Output rating (for each triac output)
|
Max. 0.5 A
|
||||||||||||
Voltage
|
24 VAC +/-20 %
|
||||||||||||
Commons
|
COM1 for DO1 and DO2 (on MP-C-15A, -18A, -18B)
|
||||||||||||
COM2 for DO3 and DO4 (on MP-C-15A, -18A, -18B)
|
|||||||||||||
COM3 for DO5 and DO6 (on MP-C-15A, -18B)
|
|||||||||||||
COM4 for DO7 and DO8 (on MP-C-18B only)
|
|||||||||||||
The common terminals can be connected to 24 VAC or to ground. | |||||||||||||
Common voltage, high side output
|
24 VAC
|
||||||||||||
Common voltage, low side output
|
0 VAC (ground)
|
||||||||||||
Minimum pulse width
|
100 ms
|
||||||||||||
Triac output protection
|
MOV and snubber across each triac output
|
||||||||||||
MOV from triac COM to ground
|
Follow proper installation wiring diagrams and instructions, including these instructions:
All MP-C models have several RET terminals for connection of I/O returns, so a common chassis/signal ground rail is optional and may not be needed.
Individual 24 V power sources to the field must be current limited to maximum 4 A for UL compliant installations, and maximum 6 A in other areas.
For more information on wiring, see Hardware Reference Guide.
Product |
Part number |
Sensor base with temperature sensor |
SXWSBTXXXSXX |
Sensor base with temperature and humidity sensors |
SXWSBTHXXSXX |
Sensor base with temperature and CO 2 sensors |
SXWSBTXCXSXX |
Sensor base with temperature, humidity, and CO 2 sensors |
SXWSBTHCXSXX |
Product |
Housing |
Part number |
Blank cover |
Medium matte white |
SXWSCBXSELXX |
Blank cover |
Optimum glass white |
SXWSCBXSELXW |
Blank cover |
Optimum glass black |
SXWSCBXSELXB |
Blank cover with occupancy sensor |
Medium matte white |
SXWSCBPSELXX |
Blank cover with occupancy sensor |
Optimum glass white |
SXWSCBPSELXW |
Blank cover with occupancy sensor |
Optimum glass black |
SXWSCBPSELXB |
3-button cover |
Medium matte white |
SXWSC3XSELXX |
3-button cover |
Optimum glass white |
SXWSC3XSELXW |
3-button cover |
Optimum glass black |
SXWSC3XSELXB |
3-button cover with occupancy sensor |
Medium matte white |
SXWSC3PSELXX |
3-button cover with occupancy sensor |
Optimum glass white |
SXWSC3PSELXW |
3-button cover with occupancy sensor |
Optimum glass black |
SXWSC3PSELXB |
Touchscreen display cover |
Medium matte white |
SXWSCDXSELXX |
Touchscreen display cover with occupancy sensor |
Medium matte white |
SXWSCDPSELXX |
Product |
Housing |
Part number |
Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover |
Medium matte white |
SXWSATXXXSLX |
Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover |
Optimum glass white |
SXWSATXXXSLW |
Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover |
Optimum glass black |
SXWSATXXXSLB |
Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover |
Medium matte white |
SLASXXX |
Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover |
Optimum glass white |
SLAWXXX |
Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover |
Optimum glass black |
SLABXXX |