Concept

Concept


Produits : AS-B
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
14/03/2025

AS-B Servers

arrow1_rotationAS-B Server Models arrow1_rotationAS-B Server Onboard I/O arrow1_rotationOutput Override Function arrow1_rotationBuilt-in Power Supply arrow1_rotationMemory arrow1_rotationSupported Building Standards arrow1_rotationAS-B Server Communication Ports arrow1_rotationAS-B Server Screw Terminals arrow1_rotationAS-B Server LEDs arrow1_rotationReset Functions arrow1_rotationDevice Installation arrow1_rotationWiring arrow1_rotationAS-B Server Software arrow1_rotationServer Replacement Using Restore arrow1_rotationSpécifications arrow1_rotationInternal Configuration

An AS-B server is a powerful automation server that features both onboard I/O and built-in power supply. Like the other automation servers, the AS-B server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The automation server controls and supervises equipment, typically HVAC equipment. The AS-B server uses its onboard I/O with connected field devices, such as sensors and actuators, to do that.

The AS-B server is installed on DIN rails in cabinets.

 
action_zoom_plus_stroke  AS-B server
Figure : AS-B server

AS-B Server Models

The AS-B server comes in eight models that offer two different sets of I/O point count and I/O mix.

Model

I/O Points

AS-B-24

24

AS-B-24H

24

AS-B-24-P

24

AS-B-24H-P

24

AS-B-36

36

AS-B-36H

36

AS-B-36-P

36

AS-B-36H-P

36

AS-B servers with “H” in the product name are equipped with a display for output override.

AS-B servers with “P” in the product name are hardware only. An AS-B software package needs to be purchased separately. For more information, see the AS-B Specification Sheet.

AS-B servers with 36 I/O points have the same small footprint as AS-B servers with 24 I/O points.

AS-B Server Onboard I/O

The AS-B server offers a mix of I/O point types that match a wide variety of HVAC applications. Most of the I/O points are universal inputs/outputs, which are highly flexible and can be configured as either inputs or outputs.

Pour plus d'informations, voir AS-B Server Onboard I/O .

Output Override Function

The output override function allows you to manually override outputs. This function can be used for testing, commissioning, and maintenance of equipment.

Pour plus d'informations, voir Output Override Function .

Built-in Power Supply

The device has a built-in power supply designed to accommodate 24 VAC or 24 VDC input power. The main AC/DC input (L/+ and N/-) is galvanically isolated from the electronics. This removes the risk of damage due to earth currents and permits the input power to be wired without concern for AC polarity matching.

Memory

An AS-B server has two types of memory:

  • 256 MB DDR2 SDRAM (for program execution)

  • 4 GB eMMC memory (for storage)

If a power outage occurs, all important variables are automatically saved to the eMMC memory before complete shutdown. When power returns, this data retention function helps ensure that AS-B can continue to run with the correct set of values.

Supported Building Standards

The AS-B server natively communicates with two of the most popular communication protocols:

  • BACnet: The AS-B server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to MP and RP controllers, b3 BACnet devices, and BACnet devices. The AS-B server also supports BACnet/SC applications as a BACnet/SC node, hub, and router. This allows the AS-B server to be in BACnet/SC networks and support applications that connect BACnet/IP or MS/TP networks with BACnet/SC networks.

  • Modbus: The AS-B server natively integrates Modbus RS-485 client and server configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.

AS-B Server Communication Ports

AS-B has the following communication ports:

  • 2 Ethernet 10/100 megabit ports

  • 1 RS-485 port

  • 1 USB host port

  • 1 USB device port

Pour plus d'informations, voir AS-B Server Communication Ports .

AS-B Server Screw Terminals

AS-B servers use pluggable terminal blocks, which are easy to install and remove from the device. The terminal blocks are delivered with the device.

Pour plus d'informations, voir AS-B Server Screw Terminals .

AS-B Server LEDs

There are five LEDs on the front panel of the AS-B server.

Pour plus d'informations, voir AS-B Server LEDs .

Reset Functions

There are four different types of reset for the automation servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the automation server can be reset using the reset button or a command from WorkStation.

Pour plus d'informations, voir Automation Server Reset Functions .

Device Installation

The AS-B servers are designed for installation on DIN rails in a cabinet.

Pour plus d'informations, voir AS-B Server Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Pour plus d'informations, voir Wiring .

AS-B Server Software

Before you engineer an AS-B server, install the AS-B server software on the server using Device Administrator. The software is not pre-loaded on the AS-B servers.

Pour plus d'informations, voir Installing AS-P or AS-B Software .

Server Replacement Using Restore

Backup and Restore helps assure that automation server data can be restored to a replacement automation server in the event of detected failure, or to the same automation server in the event of data loss. As a precaution, you back up your automation servers regularly so that you can use the most current backup to restore the automation server data to a replacement automation server. You also configure the new automation server to match the name and the network settings of the replaced automation server so the system can identify this automation server when online.

Pour plus d'informations, voir Field Server Replacement Using Restore .

Spécifications

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum current
0.5 A rms
Recommended transformer rating
≥15 VA
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
10 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, including terminal blocks
0.504 kg (1.111 lb) a
Weight, excluding terminal blocks
0.420 kg (0.926 lb) a
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45), IEEE 802.3 compliant
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
2-wire port, bias 5.0 VDC
Communications
BACnet
BACnet/IP and MS/TP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BTL B-BC (BACnet Building Controller) a
OPC UA Client
Profile group UACore 1.03
Core Client Facet, Base Client Behaviour Facet a , AddressSpace Lookup Client Facet, Attribute Read Client Facet a , Attribute Write Client Facet a , DataChange Subscriber Client Facet a , Method Client Facet, UA-TCP UA-SC UA Binary, ScurityPolicy-Basic256, ScurityPolicy-Basic256Sha256, User Token - Anonymous Facet, User Token – User Name Password Client Facet, DataAccess Client Facet.
Modbus
Modbus TCP, client and server
  
Modbus RTU and ASCII, RS-485, client and server
MQTT
MQTT over TLS, port configurable, default 8883
  
MQTT over TCP, port configurable, default 1883
  
MQTT over WebSocket Secure (WSS), port configurable, default 443
  
MQTT over WebSocket (WS), port configurable, default 80
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
CPU
Frequency
333 MHz
Type
SPEAr320S, ARM926 core
DDR2 SDRAM
256 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance

Internal Configuration

The AS-B servers internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke  AS-B server internal configuration
Figure : AS-B server internal configuration

The earth ground terminal (

 
action_zoom_plus_stroke
) of the built-in power supply is connected to signal ground, which is the same as the negative output from the power supply. The purpose of this connection is to comply with EMC directives.

  • Hardware Overview
  • AS-B Server Onboard I/O
  • Output Override Function
  • AS-B Server Screw Terminals
  • AS-B Server Communication Ports
  • AS-B Server LEDs
  • Automation Server Reset Functions
  • AS-B Server Device Installation
  • Wiring
  • Installing AS-P or AS-B Software
  • Field Server Replacement Using Restore