earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: AS-B
功能: 硬件
产品版本: 2.0, 2.1, 3.0, 3.1, 3.2
2022/8/16

SmartX AS-B Servers

arrow1_rotationSmartX AS-B Server Models arrow1_rotationSmartX AS-B Server Onboard I/O arrow1_rotationOutput Override Function arrow1_rotationBuilt-in Power Supply arrow1_rotationMemory arrow1_rotationSupported Building Standards arrow1_rotationSmartX AS-B Server Communication Ports arrow1_rotationSmartX AS-B Server Screw Terminals arrow1_rotationSmartX AS-B Server LEDs arrow1_rotationReset Functions arrow1_rotationDevice Installation arrow1_rotationWiring arrow1_rotationSmartX AS-B Server Software arrow1_rotationSmartX Server Replacement Using Restore arrow1_rotation规格 arrow1_rotationInternal Configuration

A SmartX AS-B server is a powerful SmartX server that features both onboard I/O and built-in power supply. Like the other SmartX servers, the SmartX AS-B server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The SmartX server controls and supervises equipment, typically HVAC equipment. The SmartX AS-B server uses its onboard I/O with connected field devices, such as sensors and actuators, to do that.

The SmartX AS-B server is installed on DIN rails in cabinets.

 
action_zoom_plus_stroke SmartX AS-B server
图: SmartX AS-B server

SmartX AS-B Server Models

The SmartX AS-B server comes in four models with different I/O point count and I/O mix.

Model

I/O Points

AS-B-24

24

AS-B-24H

24

AS-B-36

36

AS-B-36H

36

SmartX AS-B servers with “H” in the product name are equipped with a display for output override.

SmartX AS-B servers with 36 I/O points have the same small footprint as SmartX AS-B servers with 24 I/O points.

SmartX AS-B Server Onboard I/O

The SmartX AS-B server offers a mix of I/O point types that match a wide variety of HVAC applications. Most of the I/O points are universal inputs/outputs, which are highly flexible and can be configured as either inputs or outputs.

有关更多信息,请参阅 SmartX AS-B Server Onboard I/O .

Output Override Function

The output override function allows you to manually override outputs. This function can be used for testing, commissioning, and maintenance of equipment.

有关更多信息,请参阅 Output Override Function .

Built-in Power Supply

The device has a built-in power supply designed to accommodate 24 VAC or 24 VDC input power. The main AC/DC input (L/+ and N/-) is galvanically isolated from the electronics. This removes the risk of damage due to earth currents and permits the input power to be wired without concern for polarity matching.

Memory

A SmartX AS-B server has two types of memory:

  • 256 MB DDR2 SDRAM (for program execution)

  • 4 GB eMMC memory (for storage)

If a power outage occurs, all important variables are automatically saved to the eMMC memory before complete shutdown. When power returns, this data retention function helps ensure that AS-B can continue to run with the correct set of values.

Supported Building Standards

The SmartX AS-B server natively communicates with two of the most popular communication protocols:

  • BACnet: The SmartX AS-B server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to MP Series controllers, b3 BACnet devices, and BACnet devices.

  • Modbus: The SmartX AS-B server natively integrates Modbus RS-485 master and slave configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.

SmartX AS-B Server Communication Ports

A SmartX AS-B server has the following communication ports:

  • 2 Ethernet 10/100 megabit ports

  • 1 RS-485 port

  • 1 USB host port

  • 1 USB device port

有关更多信息,请参阅 SmartX AS-B Server Communication Ports .

SmartX AS-B Server Screw Terminals

SmartX AS-B servers use pluggable terminal blocks, which are easy to install and remove from the device. The terminal blocks are delivered with the device.

有关更多信息,请参阅 SmartX AS-B Server Screw Terminals .

SmartX AS-B Server LEDs

There are five LEDs on the front panel of the SmartX AS-B server.

有关更多信息,请参阅 SmartX AS-B Server LEDs .

Reset Functions

There are four different types of reset for the SmartX servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the SmartX server can be reset using the reset button or a command from WorkStation.

有关更多信息,请参阅 SmartX Server Reset Functions .

Device Installation

The SmartX AS-B servers are designed for installing on DIN rails in a cabinet.

有关更多信息,请参阅 SmartX AS-B Server Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, and SmartX IP Controller devices.

有关更多信息,请参阅 Wiring .

SmartX AS-B Server Software

Before you engineer a SmartX AS-B server, install the SmartX AS-B server software on the server using Device Administrator. The software is not pre-loaded on the SmartX AS-B servers.

有关更多信息,请参阅 Installing SmartX AS-P or SmartX AS-B Software .

SmartX Server Replacement Using Restore

Backup and Restore helps assure that SmartX server data can be restored to a replacement SmartX server in the event of detected failure, or to the same SmartX server in the event of data loss. As a precaution, you back up your SmartX servers regularly so that you can use the most current backup to restore the SmartX server data to a replacement SmartX server. You also configure the new SmartX server to match the name and the network settings of the replaced SmartX server so the system can identify this SmartX server when online.

有关更多信息,请参阅 SmartX Server Replacement Using Restore .

规格

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum current
0.5 A rms
Recommended transformer rating
≥15 VA
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
10 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, including terminal blocks
0.504 kg (1.111 lb) a
Weight, excluding terminal blocks
0.420 kg (0.926 lb) a
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
2-wire port, bias 5.0 VDC
Communications
BACnet
BACnet/IP and MS/TP, port configurable, default 47808
  
BTL B-BC (BACnet Building Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
Modbus
Modbus TCP, client and server
  
Serial, RS-485, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.2, 1.1, and 1.0, port configurable default 443
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
CPU
Frequency
333 MHz
Type
SPEAr320S, ARM926 core
DDR2 SDRAM
256 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance

Internal Configuration

The SmartX AS-B servers internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke SmartX AS-B server internal configuration
图: SmartX AS-B server internal configuration

The earth ground terminal (

 
action_zoom_plus_stroke
) of the built-in power supply is connected to signal ground, which is the same as the negative output from the power supply. The purpose of this connection is to comply with EMC directives.

  • Hardware Overview
  • SmartX AS-B Server Onboard I/O
  • Output Override Function
  • SmartX AS-B Server Screw Terminals
  • SmartX AS-B Server Communication Ports
  • SmartX AS-B Server LEDs
  • SmartX Server Reset Functions
  • SmartX AS-B Server Device Installation
  • Wiring
  • Installing SmartX AS-P or SmartX AS-B Software
  • SmartX Server Replacement Using Restore