earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos AS-B
Funcionalidades: Hardware
Versión del producto: 2.0, 2.1, 3.0, 3.1, 3.2
20/07/2021

Digital Inputs

arrow1_rotationInputs arrow1_rotationEspecificaciones

The digital inputs can be used for sensing of multiple dry contact digital inputs in applications, such as equipment status monitoring or alarm point monitoring.

As counter inputs, digital inputs are commonly used in energy metering applications.

Inputs

The DI digital inputs are designed to read two different types of inputs:

  • Digital

  • Counter

 
action_zoom_plus_stroke Digital input internal configuration
Figura: Digital input internal configuration

Applied voltages beyond the absolute maximum ratings cause over current in the protection component D Z .

Digital inputs

The external connection of a digital input is shown in the following figure:

 
action_zoom_plus_stroke Digital input external connection
Figura: Digital input external connection

K is the monitored external switch.

V S = 24 V

R PU = 10 kohm

Counter inputs

A counter input uses the same hardware configuration as the digital input that is shown in the figure above.

Especificaciones

Channels, SmartX AS-B servers with 24 I/O points
4, DI1 to DI4
Channels, SmartX AS-B servers with 36 I/O points
0
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Absolute maximum ratings
-0.5 to +24 VDC
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
120 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
  • SmartX AS-B Servers
  • SmartX AS-B Server Onboard I/O