Concept

Concept


Produits : AS-B
Fonctionnalités : Matériel
Version produit : 2.0, 2.1, 3.0, 3.1, 3.2
20/07/2021

Digital Inputs

arrow1_rotationInputs arrow1_rotationSpécifications

The digital inputs can be used for sensing of multiple dry contact digital inputs in applications, such as equipment status monitoring or alarm point monitoring.

As counter inputs, digital inputs are commonly used in energy metering applications.

Inputs

The DI digital inputs are designed to read two different types of inputs:

  • Digital

  • Counter

 
action_zoom_plus_stroke Digital input internal configuration
Figure : Digital input internal configuration

Applied voltages beyond the absolute maximum ratings cause over current in the protection component D Z .

Digital inputs

The external connection of a digital input is shown in the following figure:

 
action_zoom_plus_stroke Digital input external connection
Figure : Digital input external connection

K is the monitored external switch.

V S = 24 V

R PU = 10 kohm

Counter inputs

A counter input uses the same hardware configuration as the digital input that is shown in the figure above.

Spécifications

Channels, SmartX AS-B servers with 24 I/O points
4, DI1 to DI4
Channels, SmartX AS-B servers with 36 I/O points
0
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Absolute maximum ratings
-0.5 to +24 VDC
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
120 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz