earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : AS-B
Fonctionnalités : Matériel
Version produit : 3.3, 2022, 2023, 2024
21/07/2021

Triac Outputs

arrow1_rotationOutputs arrow1_rotationSpécifications

The triac outputs can be used in many applications to switch 24 VAC on or off for external loads such as actuators, relays, or indicators. Triacs are silent and do not suffer from relay contact wear.

The outputs can be configured as one of the following types:

  • Digital output

  • Digital pulsed output

  • Tristate output

  • Tristate pulsed output

Outputs

The DO triac outputs are designed to switch 24 VAC. The common terminals COM1 and COM2 can be connected to 24 VAC or to ground. DO5 and DO6 share common terminal COM1. DO7 and DO8 share common terminal COM2. The terminals are opto-isolated from the controller.

 
action_zoom_plus_stroke Triac output internal configuration
Figure : Triac output internal configuration

R V1 and R V2 are varistors (95 V, 2 J) for protection of the triac.

R 1 = 47 ohm

C 1 = 22 nF

Spécifications

Channels, AS-B servers with 24 I/O points
0
Channels, AS-B servers with 36 I/O points
4, DO5 to DO8
Output rating
Max. 0.8 A
Voltage
24 VAC +/-20 %
Commons
COM1 for DO5 and DO6
  
COM2 for DO7 and DO8
The common terminals COM1 and COM2 can be connected to 24 VAC or to ground.
Common voltage, high side output
24 VAC
Common voltage, low side output
0 VAC (ground)
Minimum pulse width
100 ms
  • AS-B Servers
  • AS-B Server Onboard I/O