earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: AS-B
功能: 硬件
产品版本: 1.8, 1.9
2017/3/8

Triac Outputs

arrow1_rotationOutputs arrow1_rotation规格

The triac outputs can be used in many applications to switch 24 VAC on or off for external loads such as actuators, relays, or indicators. Triacs are silent and last longer than relays.

The outputs can be configured as one of the following types:

  • Digital output

  • Digital pulsed output

  • Tristate output

  • Tristate pulsed output

Outputs

The DO triac outputs are designed to switch 24 VAC. The common terminals COM1 and COM2 can be connected to 24 VAC or to ground. DO5 and DO6 share common terminal COM1. DO7 and DO8 share common terminal COM2. The terminals are opto-isolated from the controller.

 
action_zoom_plus_stroke Triac output internal configuration
图: Triac output internal configuration

R V is a varistor for protection of the triac.

R 1 = 47 ohm

C 1 = 22 nF

规格

Channels, AS-B with 24 I/O points
0
Channels, AS-B with 36 I/O points
4, DO5–DO8
Output rating
Max. 0.8 A
Voltage
24 to 30 VAC
Commons
COM1 for DO5 and DO6
  
COM2 for DO7 and DO8
The common terminals COM1 and COM2 can be connected to 24 VAC or to ground.
Common voltage, high side output
0 V
Common voltage, low side output
24 to 30 VAC
Minimum pulse width
100 ms
  • AS-Bs
  • AS-B Onboard I/O