Events substitution codes represent the information you want to display when a notification report is triggered. The information is dynamically filled in from the events that are included in the notification report.
Code |
Description |
@(AcknowledgeTime) |
Writes the time and date an alarm was acknowledged. |
@(AlarmState) |
Writes the alarm state. |
@(AlarmText) |
Writes the alarm message that was added to the alarm. |
@(AssignedState) |
Writes the assigned state the alarm had. The possible values are: Unassigned, Assigned, and Accepted. |
@(AssignedToDomain) |
Writes the domain of the user or group that an alarm was assigned to. |
@(AssignedToUniqueUserId) |
Writes the ID of the user or group that an alarm was assigned to. |
@(AssignedToName) |
Writes the name of the user or group that an alarm was assigned to. |
@(BACnetEventType) |
Writes the BACnet alarm that monitored a variable within a BACnet network. |
@(BasicEvaluationState) |
Writes the basic evaluation state of an alarm. The value True indicates that an alarm was triggered. |
@(Category) |
Writes the category name. |
@(Command) |
Writes the executed command. |
@(Comment) |
Writes the comment that was added to an alarm. |
@(ControlSource) |
Writes the initials of the controlling I/NET operator. |
@(ControlDescr) |
Writes the 4 bit I/NET state descriptor. |
@(Count) |
Writes the number of times an alarm has toggled between the alarm and reset state. |
@(Description) |
Writes the description. |
@(DeviceName) |
Writes the name of the I/NET device that generated the event. |
@(DisabledCause) |
Writes the cause for why the alarm was disabled. An alarm can be disabled by user, shunt variable and/or system (it is disabled by system if the alarm was incorrectly configured). |
@(DomainName) |
Writes the domain a user belonged to. |
@(EvaluationState) |
Writes the evaluation state an alarm had. For example, Upper limit alarm is displayed if the monitored value reached the upper alarm limit. |
@(CWSId) |
Writes the ID of the event on the external system. |
@(CWSSourceId) |
Writes the ID of the external object that generated the event. |
@(FireZone) |
Writes the number of the zone from which the alarm originates. Writes 0 if no zone is configured. |
@(FirstName) |
Writes the first name of the individual whose key/card was used at the I/NET door point. |
@(ForcedValue) |
Writes the forced values. |
@(GroupName) |
Writes the name of the cause note or action note group the user edited. |
@(Hidden) |
Writes the visible status an object had. False is displayed when an object was shown. |
@(IndivNdx) |
Writes the individual number of the individual whose key/card was used at the I/NET door point. |
@(InetAdr) |
Writes the system address of the point, or station address of the host or controller that generated the event. |
@(InetEventTypeId) |
Writes the I/NET event type. |
@(LastName) |
Writes the last name of the individual whose key/card was used at the I/NET door point. |
@(LinkName) |
Writes the name assigned to the link of the device from which the event originated. |
@(MessageText) |
Writes the text of an I/NET action or dispatch message, if there is one. |
@(MonitoredVariable) |
Writes the path to the monitored variable. |
@(Note) |
Writes the event notes. |
@(PreviousAlarmState) |
Writes the previous alarm state. |
@(Priority) |
Writes the priority an alarm had. |
@(SigmaEventParams) |
Writes the Sigma event parameter. |
@(SigmaEventType) |
Writes the Sigma event type. |
@(Source) |
Writes the path of the source object. |
@(SourceName) |
Writes the name of the external object that generated the event. |
@(SourceServer) |
Writes the server path of the source object. |
@(TextField) |
Writes the (up to) 4 text characters that represent the text state of a discrete point or the unit description of an analog point. |
@(StationName) |
Writes the name assigned to the controller from which the event originated. |
@(SystemAlarmCategory) |
Writes the category of the fire detection system alarm. |
@(SystemAlarmId) |
Writes the alarm ID generated by the system. |
@(SystemEventId) |
Writes the event ID generated by the system. |
@(TenantNdx) |
Writes the tenant number of the individual whose key/card was used at the I/NET door point. |
@(TimeStamp) |
Writes the time and date when the event was generated. |
@(TriggeredTimestamp) |
Writes the time and date an alarm went from normal state to alarm state. |
@(TYPE) |
Writes the event type. |
@(UniqueAlarmId) |
Writes the unique alarm ID of an alarm. |
@(UniqueUserId) |
Writes the ID of a user. |
@(ItemName) |
Writes the events of which the user has edited checklist, cause note group, or action note group items. |
@(UserName) |
Writes the name of the user that generated the event. |
@(ValueAfter) |
Writes the value of an object after it was changed. |
@(MonitoredValue) |
Writes the value the monitored variable had when the alarm was triggered. |
@(ValueBefore) |
Writes the value of an object before it was changed. |
@(Zone) |
Writes the I/NET security zone number associated with a security event (0-63). |