0
Concept

Concept


Produits : MP-C, MP-V
Fonctionnalités : Ingénierie, Matériel, Dispositifs SmartX IP Controller
Version produit : 3.3
28/06/2022

MP Controller Reset Modes

You can reset and restart the MP controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

 
action_zoom_plus_stroke Location of the reset button on different MP controller models
Figure : Location of the reset button on different MP controller models

You can use a straightened segment of a paper clip or a similar tool to press the reset button.

Table : Reset Modes

Mode

Description

Warm start

Press and release the reset button in less than 5 seconds.

Performing a power cycle in a BACnet/IP controller is analogous to a hardware warm start.

Cold start

Press and hold the reset button for more than 5 seconds but less than 9 seconds.

Network reset

Press and hold the reset button for 10 to 19 seconds.

Perform a network reset in WorkStation in order to reset the IP address settings to DHCP with a failover to Auto-IP.

Factory reset

Press and hold the reset button for 20 to 29 seconds.

Consult the following Factory Reset subsection for more details.

Erase database

Press and hold the reset button for 30 to 39 seconds.

Cancel reset action

Press and hold the reset button for more than 40 seconds and then release the button.

Performing this action cancels the reset request that would be initiated by any of the shorter button press durations.

Déclaration

If the MP-C is equipped with the MP-C Display add-on module, a count-up timer and progress bar are displayed to assist in reset selection. There is also a reset mode indicator that lets you know which reset occurs if you release at that time.

Factory Reset

In WorkStation, if your BACnet/IP controller device seems completely unresponsive, perform a factory reset to restore the device to a state where it can be successfully commissioned. After you release the reset button, a factory reset may take up to 30 seconds to process. All diagnostic logs and the database are erased during a factory reset. By contrast, controller firmware does not revert and remains at the same active level.

Déclaration

 After a physical reset in a BACnet/IP controller, any controller proxy object in the EcoStruxure BMS database that carries the serial number of that controller may trigger an automatic association. This association occurs between the reset physical controller and the controller proxy object in the EcoStruxure BMS database.

Pour plus d'informations, voir Automatic Association after a Factory Reset in a BACnet/IP Controller .

Retain Levels for Variables

Variables have a configurable retain level, which controls if the value of the variable is retained after a restart of the MP controller. There are three retain levels:

  • No

  • Warm start

  • Cold start

The following table lists what is retained after a warm start or cold start based on the configured retain level.

Table : Retained Variable Values Depending on Restart Mode and Retain Level

Restart mode

Retain level:

No

Retain level:

Warm start

Retain level:

Cold start

Warm start

Default value a  

Values configured by a user or application are lost.

Variable retains last value configured by a user.

Values configured by an application are retained. 

Variable retains last value configured by a user.

Values configured by an application are retained. 

Cold start

Default value a

Values configured by a user or application are lost.

Variable loses last value configured by a user.

Values configured by an application are lost.

Variable retains last value configured by a user.

Values configured by an application are retained. 

a Default value is the value the variable gets when it is created.

Pour plus d'informations, voir Retain Level .

Déclaration

Although variable values in BACnet/IP controllers are retained in accordance with this matrix, automation server retention behaves differently. As a result, variable values retained in the server that are not retained in the controller may be restored to the controller during a download command. Pour plus d'informations, voir Retain Level .

Value Retention on Restarts Using Command Priority Levels

When you configure the restart retain level for an object with command priority levels, it is recommended that you base retention exclusively on either of the following:

  • The value property configured by using the Configure button

     
    action_zoom_plus_stroke
    for that property in the Basic tab of the object.

  • The command priorities configured by the Configure button

     
    action_zoom_plus_stroke
    for the appropriate command priority levels in the Command tab of the object.

Do not configure retention for both the value property on the Basic tab and the command priorities of the object because doing so may result in unexpected behavior following a controller restart. For example, if the value property is configured to retain during a restart, then that value is written to priority 16 following the restart, regardless of the retain level of priority 16.

Pour plus d'informations, voir Binding Value and Priority Properties in a BACnet/IP Controller .

  • MP Controller Models
  • BACnet/IP Device Firmware Management
  • Application Images
  • MP Controller Onboard I/O Module
  • BACnet/IP Controller Communication
  • Association Selection Workflow
  • Configure an Online BACnet/IP Controller Workflow
  • MP Controller Models
  • BACnet/IP Controller Device Memory
  • BACnet/IP Controller Diagnostics
  • Device Discovery for BACnet/IP Devices
  • BACnet/IP Controller Device Management
  • Automatic Association after a Factory Reset in a BACnet/IP Controller
  • Automatic Time Sync for BACnet/IP Controllers
  • BACnet/IP Controller Standard Objects
  • Retain Level
  • Binding Value and Priority Properties in a BACnet/IP Controller