Powering Up MP-C

You perform the following steps to power up an MP-C.

Mehr zeigen
action_close

The MP-C can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

Installation orientation restrictions

The restrictions on installing the device in various orientations differ between the different MP-C controller models ( Für weitere Informationen siehe MP-C Models .). In this regard, the MP-C models can be divided in the following categories:

  • MP-C models without “-M” in the product name:

    MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A

  • MP-C models with “-M” in the product name:

    MP-C-24A-M and MP-C-36A-M

Hinweis

CONTROLLER DAMAGE

Follow the installation orientation restrictions that apply to the specific MP-C controller model.

Failure to follow these instructions can result in equipment damage.

MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the MP-C controller models MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

Installing the MP-C rotated 180 degrees from the horizontal position with device label text up and down (“e” in the figure), face down from a ceiling (“d” in the figure), or face up on a horizontal surface (“f” in the figure) is not supported.

 
action_zoom_plus_stroke Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated in normal conditions, 0 to 50 °C (32 to 122 °F)
Abbildung: Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated in normal conditions, 0 to 50 °C (32 to 122 °F)

When the MP-C is used for rooftop applications, -40 to +60 °C (-40 to +140 °F), the device should be installed horizontally, with the device label text in the upright position reading left to right. See “a” in the following figure. Any other installation orientation (“b”, “c”, “d”, “e”, and “f” in the figure) may exceed the controller's thermal specifications, which can damage the controller.

 
action_zoom_plus_stroke Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated at -40 to +60 °C (-40 to +140 °F)
Abbildung: Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated at -40 to +60 °C (-40 to +140 °F)
MP-C-24A-M and MP-C-36A-M

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the MP-C controller models MP-C-24A-M and MP-C-36A-M can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

  • Face down from a ceiling. See “d” in the following figure.

  • Up and down, which means that the device is rotated 180 degrees from the horizontal position and with the device label text up and down. See “e” in the following figure.

  • Face up on a horizontal surface. See “f” in the following figure.

 
action_zoom_plus_stroke Installation orientations for the MP-C models MP-C-24A-M and MP-C-36A-M (example) operated in normal conditions, 0 to 50 °C (32 to 122 °F)
Abbildung: Installation orientations for the MP-C models MP-C-24A-M and MP-C-36A-M (example) operated in normal conditions, 0 to 50 °C (32 to 122 °F)

Installation on a DIN rail

A DIN rail is a common and convenient technique for installing the MP-C along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the MP-C rail and adjacent rails or other devices.

The MP-C is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke Example of an MP-C controller installed on a horizontal DIN rail
Abbildung: Example of an MP-C controller installed on a horizontal DIN rail
DIN rail end clip

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

Hinweis

EQUIPMENT DAMAGE

Use an end clip (part number SXWDINEND10001) when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
Abbildung: End clip for DIN 35 fixed across the DIN rail

Installation in a cabinet

All MP-C controller models are recommended to be installed in a cabinet, unless local regulations allow an exception.

Hinweis

The device should be installed within an enclosure such as a control cabinet for isolation to exposed live parts.

The MP-C controller can be installed in a standard DIN enclosure/cabinet.

 
action_zoom_plus_stroke MP-C controllers installed on horizontal DIN rails in a cabinet
Abbildung: MP-C controllers installed on horizontal DIN rails in a cabinet

When installing MP-C controllers in a cabinet, it is recommended to provide ample space between the DIN rails and controllers for sufficient ventilation.

Screw terminals

Most of the MP-C controller models have removable screw terminal blocks for the power input and onboard I/O. The screw terminal blocks are easy to install and remove from the device. You can replace the controller in seconds because no terminal wiring is affected. The terminal blocks are installed on the device at delivery. Spare terminal blocks can be ordered separately using the part number SXWMPCCON10001.

For high-power relay outputs, a two-position fixed terminal block is used. The high-power relay output is only available on the MP-C-15A and MP-C-18A models. Für weitere Informationen siehe MP-C Onboard I/O .

The MP-C controller models with “-M” in the product name, MP-C-24A-M and MP-C-36A-M, have fixed screw terminals for the power input and onboard I/O and a removable screw terminal block for connection to the BACnet MS/TP (RS-485) network.

MP-C Display

All MP-C controller models, except MP-C-24A-M and MP-C-36A-M, can be equipped with MP-C Display (part number SXWMPCDSP10001), which is an add-on module that enables manual override control of analog and digital outputs. The module consists of an LCD display and keys. The module is designed for permanent installation.

Hinweis

CONTROLLER DEVICE DAMAGE

Do not try to remove the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

Do not try to remove the MP-C Display module as it may damage the enclosure and the module. Once installed, the MP-C Display module cannot be removed.

 
action_zoom_plus_stroke MP-C Display installed on MP-C
Abbildung: MP-C Display installed on MP-C

Mehr zeigen
action_close

The MP-C has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

The built-in power supply is based on a half-wave rectified, non-isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

To power the controller, you can use a transformer or a DC power supply:

  • Class 2 (EN 60742) transformer supplying a nominal 24 VAC at 50/60 Hz

  • DC power supply supplying a nominal 24 to 30 VDC with the required output power

Für weitere Informationen siehe MP-C Controllers .

A separate, local 24 VAC step-down transformer is recommended to power each MP controller or IP-IO module. The transformer with appropriate VA rating may also be used to power the locally connected I/O devices. The separate transformer helps to avoid problems with ground loops, 24 VAC induced EMI on LAN, low or distorted AC voltage level at the controller, and excess transformer load due to the half-wave power supply, which can result in intermittent equipment detected faults, loss of communications, or equipment damage.

Hinweis

EQUIPMENT DAMAGE

Use a separate, local 24 VAC step-down transformer to power each MP controller or IP-IO module.

Failure to follow these instructions can result in equipment damage.

Hinweis

EQUIPMENT DAMAGE

Do not power the controller or I/O module with a 24 VAC transformer that is used to power devices that contain non-isolated full-wave rectifier power supplies.

Failure to follow these instructions can result in equipment damage.

Hinweis

CONTROLLER DAMAGE

Ensure that the input power polarity is correct and that the voltage level meets the specifications of the controller.

Failure to follow these instructions can result in equipment damage.

Hinweis

EQUIPMENT DAMAGE

Do not connect 230 VAC or 110 VAC to any terminal.

Failure to follow these instructions can result in equipment damage.

Hinweis

EQUIPMENT DAMAGE

Ensure earth ground is properly connected to avoid damage to the device and to ensure proper operation of the device.

Failure to follow these instructions can result in equipment damage.

Hinweis

EQUIPMENT DAMAGE

Use a separate, local 24 VAC step-down transformer to power each MP controller or IP-IO module.

Failure to follow these instructions can result in equipment damage.

To power up MP-C
  1. Check that all wiring is correct.

  2. Ensure that the 24 VAC at 50/60 Hz or 24-30 VDC power is supplied to terminals 1 and 2.

     
    action_zoom_plus_stroke
  3. Ensure that the ground cable is connected to terminal number 3.

  4. After powering up, check that the Status LED changes to a constant green light after about a minute.

  • MP-C Device Installation
  • MP-C Built-in Power Supply
  • Grounding and Power for Systems with MP Controllers
  • MP-C Screw Terminals
  • MP-C-15A Screw Terminals
  • MP-C-18A Screw Terminals
  • MP-C-18B Screw Terminals
  • MP-C-24A Screw Terminals
  • MP-C-36A Screw Terminals
  • MP-C-24A-M Screw Terminals
  • MP-C-36A-M Screw Terminals
  • MP-C Controller LEDs
  • Status LEDs