earth_america
user_standard Accedi
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Modalità

Modalità


Prodotti: MP-C, MP-V, SmartX Sensor
Funzionalità: Hardware
Versione del prodotto: 3.3
26/01/2022

Connecting SpaceLogic Sensor Devices to an MP Controller

You connect SpaceLogic Sensor devices to an MP controller to provide the sensor devices with power and communication from the controller.

Mostra di più
action_close

The MP controller sensor bus allows SpaceLogic Sensor devices to be connected to the controller.

Avviso

LOSS OF COMMUNICATION

  • Ensure that the total length of the sensor bus does not exceed 61 m (200 ft).

  • Use a Cat 5 or higher unshielded twisted pair cable with eight conductors (four twisted pairs), a cross-sectional area of 22 to 26 AWG (0.34 to 0.14 mm 2 ), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

 
action_zoom_plus_stroke Location of the Sensor Bus port on different MP controllers
Figura: Location of the Sensor Bus port on different MP controllers
Avviso

When connecting SpaceLogic Sensor devices to the sensor bus through a daisy-chain configuration, the sensor bus ports on the SpaceLogic Sensor are interchangeable.

Description

Model Number

Power (mW)

Sensor base with temperature sensor

SXWSBTXXXSXX

90

Sensor base with temperature and humidity sensors

SXWSBTHXXSXX

90

Sensor base with temperature and CO 2 sensors

SXWSBTXCXSXX

490

Sensor base with temperature, humidity, and CO 2 sensors

SXWSBTHCXSXX

490

Blank cover

SXWSCBXSELXn a

0

Blank cover with occupancy sensor

SXWSCBPSELXn a

20

3-button cover (buttons for override and setpoint control)

SXWSC3XSELXn a

190

3-button cover (buttons for override and setpoint control) with occupancy sensor

SXWSC3PSELXn a

210

Touchscreen display cover

SXWSCDXSELXn a

190

Touchscreen display cover with occupancy sensor

SXWSCDPSELXn a

210

Touchscreen display cover with light control buttons

SXWSC2XSELXn a

190

Touchscreen display cover with light control buttons and occupancy sensor

SXWSC2PSELXn a

210

Touchscreen display cover with light and blind control buttons

SXWSC4XSELXn a

190

Touchscreen display cover with light and blind control buttons and occupancy sensor

SXWSC4PSELXn a

210

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

SXWSATXXXSLn a

80

Complete non-communicating b SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

SLAnXXX c

SXWSATXXXRXX d

0

SpaceLogic Bluetooth Adapter e

SXWBTAECXX10001

300

  1. The last character (“n”) of this model number indicates the housing: X (Medium matte white), W (Optimum glass white), or B (Optimum glass black).
  2. The SpaceLogic resistive temperature sensor is not designed to be connected to the sensor bus, but instead is connected to I/O points/terminals on the BACnet/IP controller using a two-wire connection.
  3. The fourth character (“n”) of this model number indicates the housing: S (Medium matte white), W (Optimum glass white), or B (Optimum glass black).
  4. The model number SXWSATXXXRXX is replaced by SLASXXX.
  5. Connect the SpaceLogic Bluetooth Adapter to the SpaceLogic Sensor for temporary commissioning and servicing only.

To summarize the power conditions, the sensor bus supports the following key SpaceLogic Sensor combinations:

  • Blank covers: Up to four sensors of any combination of sensor base types

  • 3-button and touchscreen covers:

    • Up to two sensor bases with CO 2 option

    • Up to four sensor bases without CO 2 option

  • SpaceLogic LCD temperature sensors: Up to four sensors are supported

 
action_zoom_plus_stroke Examples with one SpaceLogic Sensor and four SpaceLogic Sensor devices connected to an MP controller in a daisy-chain configuration
Figura: Examples with one SpaceLogic Sensor and four SpaceLogic Sensor devices connected to an MP controller in a daisy-chain configuration

Each SpaceLogic Sensor has two 2-position DIP switches, which are used to give the sensor a unique address on the sensor bus. An incorrectly configured or improper DIP switch can cause two sensors to have the same address on the sensor bus, which means that both sensors will be offline. Per maggior informazioni, consulta SpaceLogic Sensors .

Avviso

LOSS OF COMMUNICATION

Ensure that the address DIP switches on the SpaceLogic Sensor are configured to give the sensor a unique address on the sensor bus.

Failure to follow these instructions can result in loss of communication.

Avviso

SpaceLogic Sensor devices connected to the sensor bus through a daisy-chain configuration can be assigned addresses regardless of the order in which the sensors appear in the daisy chain. For example, sensor number 1 can have the address 6, sensor number 2 can have the address 4, and so on.

Avviso

LOSS OF COMMUNICATION

Locate the sensor bus wiring away from external electromagnetic noise sources such as high voltage cables and Variable Frequency Drives (VFDs) for AC motors.

Failure to follow these instructions can result in loss of communication.

Avviso

EQUIPMENT DAMAGE

Do not connect an Ethernet cable from the controller's Sensor Bus port directly to an external Ethernet switch or router.

Failure to follow these instructions can result in equipment damage.

To connect SpaceLogic Sensor devices to an MP controller
  1. Install the SpaceLogic Sensor and connect a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) to one of the two RJ45 receptacles on the sensor. Use a cable with the wire size (cross-sectional area) 22 to 26 AWG (0.34 to 0.14 mm²).

    Per maggior informazioni, consulta SpaceLogic Sensors - SXWS Sensor Base - Installation Instructions .

    Per maggior informazioni, consulta SpaceLogic Sensors - SXWS LCD Temperature Sensors - Installation Instructions .

  2. Connect the other end of the cable to the Sensor Bus port on the MP controller.

     
    action_zoom_plus_stroke
  3. When an additional SpaceLogic Sensor is needed, install the sensor and connect the other end of the cable to the unused RJ45 receptacle on the previous sensor.

    Avviso

    When connecting SpaceLogic Sensor devices to the MP controller's sensor bus through a daisy-chain configuration, it does not matter if the incoming and outgoing cables are connected to one or the other sensor bus port on the SpaceLogic Sensor.

     
    action_zoom_plus_stroke
  4. Repeat step 3 to install a third and fourth SpaceLogic Sensor, if the power constraints of the sensor bus allow this for the selected combination of cover and sensor base type.

  5. Ensure that the two 2-position address DIP switches on each SpaceLogic Sensor are configured to give the sensor a unique address on the sensor bus.

    Per maggior informazioni, consulta SpaceLogic Sensors - SXWS Sensor Base - Installation Instructions .

    Per maggior informazioni, consulta SpaceLogic Sensors - SXWS LCD Temperature Sensors - Installation Instructions .

    Per maggior informazioni, consulta Configuring a SpaceLogic Sensor .

  • MP-C Controllers
  • MP-V Controllers
  • MP Controller Sensor Bus
  • SpaceLogic Sensor or MP Controller Sensor Bus Is Not Operational
  • Configuring a SpaceLogic Sensor