earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos MP-V
Funcionalidades: Hardware
Versión del producto: 2024, 7.0
07/10/2024

MP-V Controllers

arrow1_rotationMP-V Models arrow1_rotationMP-V Onboard I/O arrow1_rotationMP-V Damper Actuator arrow1_rotationMP-V Air Flow Sensor arrow1_rotationMP-V Built-in Power Supply arrow1_rotationBACnet/IP Device Memory arrow1_rotationBACnet/IP Controller Supported Building Standards arrow1_rotationMP-V Communication Ports arrow1_rotationMP-V Sensor Bus arrow1_rotationMP-V Modbus arrow1_rotationMP-V BACnet MS/TP Support arrow1_rotationMP-V Screw Terminals arrow1_rotationMP-V Controller LEDs arrow1_rotationMP Controller Reset Modes arrow1_rotationMP-V Device Installation arrow1_rotationWiring arrow1_rotationBACnet/IP Device Firmware Management arrow1_rotationEspecificaciones arrow1_rotationInternal Configuration

The MP-V controller is a multi-purpose, fully programmable, IP based field controller dedicated for VAV applications. MP-V integrates a controller, a damper actuator, and an air flow sensor in a single unit for ease of installation. The MP-V can either be used as a standalone BACnet field controller or as part of an EcoStruxure BMS with an automation server or Enterprise Server as the parent server. MP-V can also be reconfigured through the EcoStruxure Building Operation software to use BACnet MS/TP, instead of BACnet/IP.

MP-V allows for flexible control solutions due to the dual Ethernet ports, the interface to SpaceLogic Sensor devices, and the mix of universal inputs, triac outputs, and analog outputs.

When MP-Vs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

 
action_zoom_plus_stroke MP-V
Figura: MP-V

MP-V Models

The MP-V comes in two models with a different I/O point count and different I/O point mix.

Para obtener más información, consulte MP-V Models .

MP-V Onboard I/O

The MP-V models offer a versatile mix of I/O point types that match a wide variety of VAV applications.

Para obtener más información, consulte MP-V Onboard I/O .

MP-V Damper Actuator

The MP-V has an integrated damper actuator, which allows for simplified installation of MP-V directly over the damper shaft.

Para obtener más información, consulte Damper Actuator .

MP-V Air Flow Sensor

The MP-V uses a digital pressure sensor to measure the air velocity pressure signal from the velocity probe in the inlet of the VAV box. The measured value is used by the controller to position the VAV damper actuator for the required air flow.

Para obtener más información, consulte Air Flow Sensor .

MP-V Built-in Power Supply

The MP-V has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz input power.

Para obtener más información, consulte MP-V Built-in Power Supply .

BACnet/IP Device Memory

BACnet/IP devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

Para obtener más información, consulte Memory in RP and MP Controllers and I/O Modules .

BACnet/IP Controller Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the BACnet/IP controller complies with the BACnet open standard, one of the most popular standards for buildings.

Para obtener más información, consulte RP and MP Controller Supported Building Standards .

MP-V Communication Ports

The MP-V provides the following combination of communication ports:

  • Two Ethernet ports

  • Two USB ports

  • One RS-485 port

Para obtener más información, consulte MP-V Communication Ports .

MP-V Sensor Bus

The MP-V sensor bus allows SpaceLogic Sensor devices to be connected to the controller.

Para obtener más información, consulte MP-V Sensor Bus .

MP-V Modbus

The MP controller Modbus RTU (RS-485) subnetwork allows standard Modbus devices to be connected to the controller. An adapter is required for converting the controller RS-485 Com port with RJ45 interface to screw terminals.

Para obtener más información, consulte MP-V Modbus .

MP-V BACnet MS/TP Support

The MP-V controllers can be reconfigured to communicate with the hosting server based on the BACnet MS/TP protocol, instead of the BACnet/IP protocol. An adapter is required for converting the controller RS-485 Com port with RJ45 interface to screw terminals.

Para obtener más información, consulte MP-V BACnet MS/TP Support .

MP-V Screw Terminals

The MP-V is delivered with terminal blocks installed on the device. The MP-V uses pluggable terminal blocks, which are easy to install and remove from the device.

Para obtener más información, consulte MP-V Screw Terminals .

MP-V Controller LEDs

There are five LEDs on the front panel of the MP-V controller.

Para obtener más información, consulte MP-V Controller LEDs .

MP Controller Reset Modes

You can reset and restart the MP controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

Para obtener más información, consulte MP Controller Reset Modes .

MP-V Device Installation

The MP-V incorporates an integral actuator and the device is designed for over-the-shaft damper installation.

Para obtener más información, consulte MP-V Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Para obtener más información, consulte Wiring .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Aviso

SpaceLogic Sensor devices are supported by the BACnet/IP controllers - MP and RP controllers.

Para obtener más información, consulte BACnet/IP Device Firmware Management .

Especificaciones

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum power consumption (MP-V-7A)
21 VA
Maximum power consumption (MP-V-9A)
22 VA
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Plenum rating
UL 2043
Mechanical
Dimensions
161 W x 198 H x 63 D mm (6.3 W x 7.8 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
1.13 kg (2.5 lb)
Installation
Over the damper shaft
Terminal blocks
Removable
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485 port Com A
24 VDC, 2 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 transceiver characteristics
All device models
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
  
BTL B-AAC (BACnet Advanced Application Controller) a
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
Damper actuator
Torque rating
6 Nm (53 lbf.in)
Stroke
0° to 90°, fully adjustable
Timing
Approximately 2 seconds/degree at 60 Hz and 2.4 seconds/degree at 50 Hz
Position indication
Visual indication
Damper position feedback
Yes
Manual override
Push-button clutch release
Damper shaft diameter
12.7 mm (0.5 inch) or 9.5 mm (0.375 inch)
  
Adapter kit AM-135 is required for 9.5 mm (0.375 inch) diameter shafts.
Damper shaft minimum length (from VAV box)
22.2 mm (0.875 inch)
Air flow sensor
Range
0 to 249 Pa (0 to 1 inH 2 O)
Resolution
0.0167 Pa (0.000067 inH 2 O)
Accuracy
±5% of reading (typical) at 25°C (77°F)

Internal Configuration

The MP-V internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke  MP-V internal configuration
Figura: MP-V internal configuration
  • Hardware Overview
  • MP-V Models
  • MP-V Onboard I/O
  • Damper Actuator
  • Air Flow Sensor
  • MP-V Built-in Power Supply
  • Memory in RP and MP Controllers and I/O Modules
  • RP and MP Controller Supported Building Standards
  • MP-V Communication Ports
  • MP-V Sensor Bus
  • MP-V Modbus
  • MP-V BACnet MS/TP Support
  • MP-V Screw Terminals
  • MP-V Controller LEDs
  • MP Controller Reset Modes
  • MP-V Device Installation
  • Wiring
  • BACnet/IP Device Firmware Management